10-17-2007, 10:14 AM #1
A/C Condensdate drain gurgling at sink
.........
Similar Threads:Last edited by Clay White; 01-02-2008 at 02:24 PM.
-
10-17-2007, 10:23 AM #2
Re: A/C Condensdate drain gurgling at sink
Clay:
No. In fact, this installation is improper. See IRC P2706.3:
P2706.3 Prohibited waste receptors.
Plumbing fixtures that are used for domestic or culinary purposes shall not be used to receive the discharge of an indirect waste.
Exceptions:
1. A kitchen sink trap is acceptable for use as a receptor for a dishwasher.
2. A laundry tray is acceptable for use as a receptor for a clothes washing machine.
Aaron
-
10-17-2007, 11:32 AM #3
Re: A/C Condensate drain gurgling at sink
Talk about a deep trap seal, look at that one.
Aaron is right on with that reply.
-
10-17-2007, 12:13 PM #4
Re: A/C Condensate drain gurgling at sink
JP:
Every time I write this up I get the same question from the builder: "OK then, where do you want me to put the damned thing." I do bleed a bit about the tounge in an attempt to say what I'm thinking, but what reasonable locations should I suggest to them?
Thanks,
Aaron
-
10-17-2007, 12:35 PM #5
Re: A/C Condensate drain gurgling at sink
[quote=Aaron Miller;21744]I do bleed a bit about the tounge in an attempt to say what I'm thinking, [quote]
Not sure that location would hold much anyway.
but what reasonable locations should I suggest to them?
M1411.3 Condensate disposal.Condensate from all cooling coils or evaporators shall be conveyed from the drain pan outlet to an approved place of disposal. Condensate shall not discharge into a street, alley or other areas where it would cause a nuisance.
-
10-17-2007, 12:51 PM #6
Re: A/C Condensate drain gurgling at sink
Outside?
M1411.3 Condensate disposal.
Condensate from all cooling coils or evaporators shall be conveyed from the drain pan outlet to an approved place of disposal. Condensate shall not discharge into a street, alley or other areas where it would cause a nuisance.
[/quote]
JP:
Now I assume that "approved" means by the AHJ? So then, if he approves termination of the drain lines above the sink traps it is good to go that way?
And, in an area of known expansive soil where depositing this condensate adjacent to the foundation (within 60") would possibly advserly affect foundation performance, then where should it terminate?
Aaron
-
10-17-2007, 01:26 PM #7
Re: A/C Condensate drain gurgling at sink
Nope.
From the IRC. (underlining is mine)
- SECTION R104
- - DUTIES AND POWERS OF THE BUILDING OFFICIAL- - - R104.1 General.The building official is hereby authorized and directed to enforce the provisions of this code. The building official shall have the authority to render interpretations of this code and to adopt policies and procedures in order to clarify the application of its provisions. Such interpretations, policies and procedures shall be in conformance with the intent and purpose of this code. Such policies and procedures shall not have the effect of waiving requirements specifically provided for in this code.
Nope - not when it specifically goes against the stated code, and that would.
And, in an area of known expansive soil where depositing this condensate adjacent to the foundation (within 60") would possibly advserly affect foundation performance, then where should it terminate?
-
10-17-2007, 01:57 PM #8
Re: A/C Condensdate drain gurgling at sink
JP:
OK, that's what I'll tell them then. I'll let you know what they have to say about snaking CPVC out into the yards to fill future mosquito breeding grounds . . . or whatever they come up with.
Thanks,
Aaron
-
10-17-2007, 04:43 PM #9
Re: A/C Condensdate drain gurgling at sink
Aaron, a floor drain with an air gap discharge would be acceptable, as would a dedicated trapped standpipe as long as it has an airgap.
I wish I could post apicture of an approved method, but I have NEVER seen one in person. It would be much easier in the land of basements and floor drains.
-
10-18-2007, 03:18 AM #10
Re: A/C Condensdate drain gurgling at sink
Jim:
Yes, and every time I see these the drain line is lost down in the bottom of the standpipe or they've cut a hole in the floor drain and stuffed the drain line down in there. Besides, how can one practicaly or safely in stall a stand pipe or floor drain in an attic?
Aaron