Help on this older panel
Walked into this older panel....main disconnect 60amps/220v....older service conductors cut off and left to rot at the bottom.....double tapping....GFCI inoperative.....i think there is a fuse on the right upper corner....any other observations would help!
Similar Threads:
-
02-05-2013, 04:36 PM #2
Re: Help on this older panel
The conductors at the bottom have been cut off and the service entrance conductors from the meter are coming into a 2 pole 60 amp breaker at the top right. I could not tell the size of the conductors feeding the 60amp 2 pole breaker. I'm uploading a couple more images to get a better view...
-
02-05-2013, 07:24 PM #3
Re: Help on this older panel
very simple,
save a life
Panel requires replacement!
Period
why screw around with a bastardized piece of crap?
-
02-05-2013, 08:14 PM #4
Re: Help on this older panel
Missing a cable clamp in the bottom. Mr. Sparky didn't have a hex wrench for those cable lugs? Is that a #14 wire on the 20 amp breaker?
There's plenty of fodder there for an electrician. Best fix is a replacement, I agree with Wayne on that one.
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
-
02-05-2013, 08:21 PM #5
Re: Help on this older panel
1200 bucks...replace the panel..and you and your client will be ablle to sleep at night..