Results 1 to 5 of 5
  1. #1
    Join Date
    Dec 2008
    Location
    Erwin, TN
    Posts
    330

    Default Sub-Panel power off main lug on service panel

    Would it be acceptable to jump off the main lug to power a sub-panel that didn't have a main breaker. Main service panel was a GE 200 amp., the sub-panel didnt have a main breaker. TKS

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by Sam Morris; 02-15-2013 at 07:16 PM. Reason: Pic main panel
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: Sub-Panel power off main lug on service panel

    no, double tap not allowed.
    main panel more than likely overloaded
    repairs required


  3. #3
    Darrel Hood's Avatar
    Darrel Hood Guest

    Default Re: Sub-Panel power off main lug on service panel

    Wayne, if the conductor was pig tailed, using proper techniques, to eliminate the double tap, would it be OK?


  4. #4
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Sub-Panel power off main lug on service panel

    Wayne, what are you basing your possibly overloaded comment on? Looks?

    All answers based on unamended National Electrical codes.

  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Sub-Panel power off main lug on service panel

    'Yes', 'no', and 'not like that', along with 'the remote panel bus would need to be rated the same or higher than the rating of the main disconnect'.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •