    Can copper water pipes be bonded and then bonded to HVAC duct.

    Similar Threads:
    OREP Insurance

  2. #2
    Joe Funderburk's Avatar
    Joe Funderburk Guest

    Default Re: Bonding to HVAC duct

    Sounds "unorthodox" -- and stupid -- to me.

    FYI. If the water pipe serves as the only source of ground, I'd write it up since today's code prohibits pipes as the only ground source.


  3. #3
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: Bonding to HVAC duct

    You cannot use a water pipe electrode for an additional bond past the fist 5' of where it enters the structure. At a point past 5' a water pipe is no longer considered an electrode.

    See
    250.104(B) Other Metal Piping. If installed in, or attached to, a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure; the grounded conductor at the service; the grounding electrode conductor, if of sufficient size; or to one or more grounding electrodes used. The bonding conductor(s) or jumper(s) shall be sized in accordance with 250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.
    Informational Note No. 1: Bonding all piping and metal air ducts within the premises will provide additional safety.



  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Bonding to HVAC duct

    Quote Originally Posted by Speedy Petey View Post
    You cannot use a water pipe electrode for an additional bond past the fist 5' of where it enters the structure. At a point past 5' a water pipe is no longer considered an electrode.
    Actually, you can.

    You are not allowed to GROUND the water pipe past 5 feet and then consider it a GROUNDing electrode, but the original post asked about BONDing it, and you can bond it.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Jun 2008
    Location
    Maryland
    Posts
    1,097

    Default Re: Bonding to HVAC duct

    I believe the intent of bonding the duct work is to equalize electrical potential between it and other conductive materials.

    In the case of a lightning strike for instance, if all metal components have equal potential because they're bonded together, the chance of arching which can start fires or perforate CSST is reduced.


  6. #6
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: Bonding to HVAC duct

    Quote Originally Posted by Jerry Peck View Post
    Actually, you can.

    You are not allowed to GROUND the water pipe past 5 feet and then consider it a GROUNDing electrode, but the original post asked about BONDing it, and you can bond it.
    So you think it is OK to bond a water pipe, then down the line, bond from the water pipe to a heating duct? If so then I disagree.
    If it were building steel it would be OK, but not a water pipe.


  7. #7
    Join Date
    Jun 2008
    Location
    Maryland
    Posts
    1,097

    Default Re: Bonding to HVAC duct

    There might be a misunderstanding between grounding and bonding going on here.


  8. #8
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Bonding to HVAC duct

    Quote Originally Posted by Joe Funderburk View Post
    Sounds "unorthodox" -- and stupid -- to me.

    FYI. If the water pipe serves as the only source of ground, I'd write it up since today's code prohibits pipes as the only ground source.
    Not stupid to me, unorthodox for some locals, maybe. At least one of the cities here (Frisco, where I believe the CSST issue was first brought to light) actually requires all the metal in the attic to be bonded together and down to the GEC. So every metal gas pipe, b-vent, pipe, etc. We use flex duct almost exclusively but if it was metal duct, I'm sure they would require that be bonded also. Of course you have to keep in mind we need a little more robust bonding here due to the lack of basements and sticking everything up in the attic. Two water heater vent pipes, two or three furnace vent pipes sticking up in the air two or three stories above the prairie make pretty decent lightening rods whether intended to be so or not.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  9. #9
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Bonding to HVAC duct

    Quote Originally Posted by Jim Luttrall View Post
    Not stupid to me, unorthodox for some locals, maybe. At least one of the cities here (Frisco, where I believe the CSST issue was first brought to light) actually requires all the metal in the attic to be bonded together and down to the GEC. So every metal gas pipe, b-vent, pipe, etc. We use flex duct almost exclusively but if it was metal duct, I'm sure they would require that be bonded also. Of course you have to keep in mind we need a little more robust bonding here due to the lack of basements and sticking everything up in the attic. Two water heater vent pipes, two or three furnace vent pipes sticking up in the air two or three stories above the prairie make pretty decent lightening rods whether intended to be so or not.
    I agree with "not so stupid". We've all been in the older crawlspace where the up grade wiring hangs from water pipes and metal ducts. If the furnace or air-handler has a noise isolation collar then the ducts are not grounded at all. When a wire gets pulled across a sharp corner it can short to the duct and not trip any breaker. When in a crawl like that be sure to at least touch the duct with you hand before squeezing between it and the wet ground. (voltage sniffer is better but do at least the minimum)

    The beatings will continue until morale has improved. mgt.

  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Bonding to HVAC duct

    Quote Originally Posted by John Dirks Jr View Post
    There might be a misunderstanding between grounding and bonding going on here.
    There "IS" a misunderstanding between grounding and bonding going on here, and all we can do it address what is stated, which was "bonding", not "grounding".

    There is nothing which prohibits the metal duct from being bonded to the bonded interior metal water piping system. Note the key word used here is "bonded".

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: Bonding to HVAC duct

    I for one am well aware of the difference between bonding and grounding.
    Quote Originally Posted by Jerry Peck View Post
    There is nothing which prohibits the metal duct from being bonded to the bonded interior metal water piping system. Note the key word used here is "bonded".
    The way this is written says that any metallic piping systems must be bonded back to the service or a service electrode. Info Note #1 says bonding ducts is a good idea also. I read this as saying bonding ducts should be done in the same fashion.
    (B) Other Metal Piping. If installed in, or attached to, a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure; the grounded conductor at the service; the grounding electrode conductor, if of sufficient size; or to one or more grounding electrodes used. The bonding conductor(s) or jumper(s) shall be sized in accordance with 250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible. Informational Note No. 1: Bonding all piping and metal air ducts within the premises will provide additional safety.
    I may be wrong, but I don't feel I am.


  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Bonding to HVAC duct

    Quote Originally Posted by Speedy Petey View Post
    I for one am well aware of the difference between bonding and grounding.
    I was sure of that, but this is what you said and what you said is all I had to go on ...

    Quote Originally Posted by mathew stouffer View Post
    Can copper water pipes be bonded and then bonded to HVAC duct.
    Quote Originally Posted by Speedy Petey View Post
    You cannot use a water pipe electrode for an additional bond past the fist 5' of where it enters the structure. At a point past 5' a water pipe is no longer considered an electrode.
    No mention was made of grounding or using anything as an electrode, so you had ... still have ... me stumped on how you got from "bonding" to "electrode" (which is "grounding").

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  13. #13
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: Bonding to HVAC duct

    Quote Originally Posted by Jerry Peck View Post
    I was sure of that, but this is what you said and what you said is all I had to go on ...





    No mention was made of grounding or using anything as an electrode, so you had ... still have ... me stumped on how you got from "bonding" to "electrode" (which is "grounding").
    Well, I tried to clarify in post #12. If that is not clear enough I am not sure what to write.
    Sorry.