Results 1 to 22 of 22
Thread: Maximum drain slope
-
01-29-2009, 04:08 AM #1
Maximum drain slope
I've been told that once the slope on a drain pipe exceeds 1/2" per foot it should be sloped at 45 degrees or greater to ensure correct scouring of solids, however I can't find the code requirement mandating this. Is it a code requirement, or just good practice?
Similar Threads:
-
01-29-2009, 04:27 AM #2
Re: Maximum drain slope
"There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
www.ArnoldHomeInspections.com
-
01-29-2009, 06:48 AM #3
Re: Maximum drain slope
Wow... I've been around here long enough to have forgotten that I posted in that thread!
Rereading it, however, I 'm not convinced the question really got answered...
-
01-29-2009, 09:50 AM #4
Re: Maximum drain slope
Drainage fittings are required to be designed to maintain 1/4" per foot slope.
Drainage piping is required to have a minimum slope of 1/4" per foot for sizes 2-1/2" and smaller, and, a minimum slope of 1/8" per foot for sizes 3" and larger.
Table P3005.4.2 shows three slopes: 1/8" per foot, 1/4" per foot, and 1/2" per foot for calculating number of fixture units allowed.
The maximum slope of horizontal branch piping is 1/2" per foot.
- From the 2006 IRC.
- - P3110.3 Slope and size of horizontal branch.The maximum slope of the vent section of the horizontal branch drain shall be one unit vertical in 12 units horizontal (8-percent slope). The entire length of the vent section of the horizontal branch drain shall be sized for the total drainage discharge to the branch in accordance with Table P3005.4.1.
The maximum slope of a horizontal combination waster and vent pipe is 1/2" per foot.
- P3111.2.1 Slope.The horizontal combination waste and vent pipe shall have a maximum slope of 1/2 unit vertical in 12 units horizontal (4-percent slope). The minimum slope shall be in accordance with Section P3005.3.
Yes, it has to do with the water speed. Too much slope and the water speed will outrun the waste it is carrying with it, leaving the waste behind to clog the line up.
If you need to exceed 1/2" per foot slope, then either use a 45 degree slope or a tie into a vertical drop.
The above information is from what I have learned over the years and from very knowledgeable plumber (the ones who teach the courses for apprenticeship programs).
Back up and supporting documents in writing? only what I've posted above.
-
01-29-2009, 01:34 PM #5
Re: Maximum drain slope
I was talking about this with my plumber a few weeks ago when we were laying out my waste and vent lines. The fittings are designed to fit tight at 1/4" / foot, which is why if you start getting too crazy on your slopes, you have a much higher change of a leak at the fitting. I didn't ask him about the solids being left behind, but it makes sense at some level. He was quite picky about making sure things were either plumb or sloped properly at the 1/4" / foot designation.
Jim Robinson
New Mexico, USA
-
01-29-2009, 07:41 PM #6
Re: Maximum drain slope
-
01-29-2009, 07:50 PM #7
Re: Maximum drain slope
-
01-30-2009, 10:38 PM #8
Re: Maximum drain slope
Jerry Peck has the answer "nailed". Great reply
-
02-18-2013, 02:34 PM #9
-
02-18-2013, 05:03 PM #10
Re: Maximum drain slope
I posted both sections, one is incorrect (as you pointed out) and one is correct (as you did not point out).
Yes, "one unit vertical in 12 units horizontal" = 1" per foot.
And, yes, "1/2 unit vertical in 12 units horizontal" = 1/2" per foot.
I apparently got the fingers typing and made a typo - oops - thanks for catching it.
-
02-20-2013, 08:34 AM #11
Re: Maximum drain slope
-
02-20-2013, 06:48 PM #12
Re: Maximum drain slope
The mis-type (typo) is where I said that 1" in 12" was 1/2" per foot, as brought up by Dennis in this post of his:
I included both sentences from my post to show the typo and where it was - that the typo was in the 1" in 12" was 1/2" per foot (1" in 12" is 1" per foot), not in the 1/2" in 12" was 1/2" per foot.
-
02-20-2013, 08:42 PM #13
Re: Maximum drain slope
I don't think you actually did make a typo...there are two allowable maximums depending on the purpose of the pipe. Horizontal branch piping can be up to 1:12 when it is a vent section, but cannot be more than 1/2:12 when its a combination waste and vent pipe.
Not sure what one might gain by going that little bit steeper because, as you pointed out, the fittings aren't really designed for that.
-
02-20-2013, 09:33 PM #14
Re: Maximum drain slope
I did make the typo, where I typed this:
"one unit vertical in 12 units horizontal" is 1" per foot, not 1/2" per foot as I typed in the quote above.The maximum slope of horizontal branch piping is 1/2" per foot.
- From the 2006 IRC.
- - P3110.3 Slope and size of horizontal branch.The maximum slope of the vent section of the horizontal branch drain shall be one unit vertical in 12 units horizontal (8-percent slope). The entire length of the vent section of the horizontal branch drain shall be sized for the total drainage discharge to the branch in accordance with Table P3005.4.1.
-
02-22-2013, 12:14 PM #15
Re: Maximum drain slope
I think the reasons for the max slope, stated in the 2005 thread (referred to by Michael) are valid but isn't it also because if the slope is too great, the water will flow so fast that it will drain any p-trap along it's path?
Checkpoint Home Inspections
www.checkpointinspections.ca
-
04-10-2013, 11:58 AM #16
Re: Maximum drain slope
-
02-23-2019, 12:37 PM #17
Re: Maximum drain slope
Maybe a few years late, BUT the code section referred to above applies to circuit vents only. I have read about the "liquid out runs the solids" for years but have NEVER seen any real studies that confirm that theory. Nor have I seen a maximum slope listed for a regular drain or sewer line in an adopted code book. I have also discussed this with "very knowledgeable plumber (sic)" (ones that have worked in the field for decades, including me (licensed plumber for over 40 years)) with the same conclusion.
-
02-23-2019, 05:41 PM #18
Re: Maximum drain slope
Only the last two above are related to vent piping, the others, as stated above, are from chapter 30, drainage piping. I gave the slope for BOTH drainage piping (Chapter 30) and vents (Chapter 31) with the original code sections
From the 2018 IRC P3005.3 Horizontal drainage piping slope - same "1/4 unit vertical in 12 units horizontal (2-percent slope) for 2 1/2 inch (64 mm) diameter and less, and not less than 1/8 unit vertical in 12 units horizontal (1-percent slope) for diameters of 3 inches (76 mm) or more."
Maybe it is different in CA codes, but that is why I said it was from the IRC - so the code reference can be looked up and verified.
ybe it is different in CA, but that is why I said it was from the IRC, the original post had quotes from the 2006 IRC.
-
02-24-2019, 12:31 PM #19
Re: Maximum drain slope
Something else I've not yet seen addressed is in conjunction with the trend towards low flow fixtures, a worthy water conservation measure. This occurs to me as I do some inspection for a green program that awards points for low flow fixtures. I support the overall goal, but as one who inspects under houses a lot, it leads me to wonder about the following.
1. Will this leave solids in drain lines due to lower volume flow?
2. With (1) considered, is it perhaps time to reconsider slope requirements in conjunction with a building specific (fixture flow rates considered/included) design?
Are there any plumbing designers in this group? Or former plumbers with thoughts?
Tim Kaiser, Nitty Gritty Inspections, LLC
Home and small commercial inspections for Central Oregon
http://nittygrittyinspections.com/index.html
-
03-04-2019, 04:16 AM #20
-
03-13-2019, 05:42 PM #21
-
03-13-2019, 06:18 PM #22
Re: Maximum drain slope



Reply With Quote



Bookmarks