Results 1 to 3 of 3

Thread: Split bus ?

  1. #1
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Split bus ?

    I know there should be no more than 6 breakers to shut off everything.
    On a panel with a single main, no problem, but how do you tell how many ( and which) breakers on a split bus panel are the controlling breakers? For that matter how do you determine it is a split bus and not just breakers on a panel without a main?

    Similar Threads:
    Inspection Referral
    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Split bus ?

    On a split bus panel you will find the upper bus section and the lower bus section are separate in the middle - like someone cut a section out.

    You will find that one 'main' in the top 6 feeds the lower bus section - the panelboard section.

    This is done a couple of ways, each of which has conductors coming off a breaker in the top section, then ... a) feed terminals on the lower bus, b) are welded to the lower bus.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Richard Rushing's Avatar
    Richard Rushing Guest

    Default Re: Split bus ?

    Note the upper section and the lower section of breakers. The upper section are all seperate circuits with the exception bottom 60 amo breaker on the left hand side (of the upper section). This breaker kills power to all of the lower section (15 and 20 amp breakers) and is also know as a 'lights main'.

    See photo below of this mighty fine FPE stay-Lok

    rr

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images