Results 1 to 30 of 30
  1. #1
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default cement board tile backer over drywall?

    Inspected a "rehab" today where there were access panels to two tile showers and a tub/shower. I hoped to find cement board as the backer for the tiles, but saw drywall instead.
    My question is: is it common to install the cement board over drywall, so that you would only see the drywall when viewing from the other side of the wall?
    In the photo you can see the rubber liner for the shower, and the drywall inside of it, which doesn't make much sense to me, even if there is cement board on the other side of the drywall.

    tile backer.jpg

    Similar Threads:
    Member Benefits1
    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  2. #2
    Join Date
    Dec 2008
    Location
    Maryland
    Posts
    2,809

    Default Re: cement board tile backer over drywall?

    Green Board with tile, but not just reg drywall. Though it is done in rehabs as a cheaper material. Will last for a while so long as no moisture gets to the drywall. A tile and run job. Or a drive by tiling....


  3. #3
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by Garry Sorrells View Post
    Green Board with tile, but not just reg drywall. Though it is done in rehabs as a cheaper material. Will last for a while so long as no moisture gets to the drywall. A tile and run job. Or a drive by tiling....
    Thanks Garry.
    What I'm trying to figure out is - Do I assume there is no cement board between the tile and the drywall that I can see, or is it common to put the cement board over drywall?

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  4. #4
    Join Date
    Jul 2008
    Location
    Chicago
    Posts
    263

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by John Arnold View Post
    Thanks Garry.
    What I'm trying to figure out is - Do I assume there is no cement board between the tile and the drywall that I can see, or is it common to put the cement board over drywall?
    It's not common. I'd assume no cementitious substrate and would say so. This is an old reference.

    ANSI A108, A118, & A136 1999 American National Standard for Installation of Ceramic Tile AN-2.4.1 Some backing materials are subject to deterioration when subjected to moisture. When a tile installation is subjected to frequent wetting, backing materials of concrete, portland cement mortar, cementitious backer units, or masonry are recommended.

    Garry is right. It is a drive-by tile job.

    Mike Lamb
    Inspection Connection, Inc.
    http://www.inspection2020.com/

  5. #5
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by Mike Lamb View Post
    It's not common. I'd assume no cementitious substrate and would say so. This is an old reference.

    ANSI A108, A118, & A136 1999 American National Standard for Installation of Ceramic Tile AN-2.4.1 Some backing materials are subject to deterioration when subjected to moisture. When a tile installation is subjected to frequent wetting, backing materials of concrete, portland cement mortar, cementitious backer units, or masonry are recommended.

    Garry is right. It is a drive-by tile job.
    Mike, Thanks. The more I look at install instructions for tile showers, the more I agree that there's probably no cement board there. I'm sure it's a complete coincidence that no permits were obtained for this "rehab"...

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by Garry Sorrells View Post
    Green Board with tile, ...
    Nope, green board is not for use behind tile in wet or damp areas such as showers or around tubs with showers; green board is for use behind tile in dry areas such as wall areas outside the shower area.

    ... but not just reg drywall.
    I agree on that part - no drywall behind the cement board as then the cement board will simply be attached to, or through, a sponge and will not stay in place, this will cause all kinds of problems you would not even want to consider.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: cement board tile backer over drywall?

    Kerdi is designed to be installed directly onto gypsum board. I've done three showers with it so far, and it seems like a good product. They love it over at John Bridge, so I thought I'd try it out. I think it is approved in PA, but it depends on what codes are in use.

    Schluter-KERDI - Schluter-Systems

    It's not necessary to use the rubber liner with it, but it probably wouldn't hurt anything to use a conventional base with the Kerdi system.

    Jim Robinson
    New Mexico, USA

  8. #8
    Join Date
    Mar 2007
    Location
    Orlando, FL
    Posts
    1,594

    Default Re: cement board tile backer over drywall?

    You can always pop the trim ring from the shower valve to see the cross-section of the wall.

    Did they use a bull-nose or mud cap on the edges?


  9. #9
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by Dom D'Agostino View Post
    You can always pop the trim ring from the shower valve to see the cross-section of the wall.

    Did they use a bull-nose or mud cap on the edges?
    The top edge was finished with grout, if that's what you mean by mud cap.

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  10. #10
    Join Date
    Feb 2008
    Location
    New York
    Posts
    868

    Default Re: cement board tile backer over drywall?

    Mold loves cellulose and is colorblind.

    Steven Turetsky, UID #16000002314
    homeinspectionsnewyork.com
    eifsinspectionsnewyork.com

  11. #11
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by Jim Robinson View Post
    Kerdi is designed to be installed directly onto gypsum board.
    It is?

    While I did not click through and read each of the available information links, I clicked on and looked as several of then, and not even a single one mentioned anything about installing on gypsum board.

    Then, of course, there is the gypsum board manufacturer's who stated NOT to use gypsum board in those areas ...

    - - - Updated - - -

    Quote Originally Posted by Steven Turetsky View Post
    Mold loves cellulose and is colorblind.
    Steven,

    I like that! Very good and simple way to put it. Cool.

    Green ... board (MR board)

    Blue ... board (plasterboard)

    Gray ... board (regular drywall)

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  12. #12
    Join Date
    Apr 2011
    Location
    Bozeman, Montana
    Posts
    94

    Default Re: cement board tile backer over drywall?

    Click on Jim's KERDI link. Then check out the installation manual, page 5.... Just because you can doesn't always meen you should.


  13. #13
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by Mark Hagenlock View Post
    Click on Jim's KERDI link. Then check out the installation manual, page 5.... Just because you can doesn't always meen you should.
    Quote Originally Posted by Jerry Peck View Post
    While I did not click through and read each of the available information links, I clicked on and looked as several of then, and not even a single one mentioned anything about installing on gypsum board.

    Then, of course, there is the gypsum board manufacturer's who stated NOT to use gypsum board in those areas ...
    Mark,

    Yep, it is there ... as I said, I did not check all links ... but don't forget the last part of my post too ... "Then, of course, there is the gypsum board manufacturer's who stated NOT to use gypsum board in those areas ..." the manufacturers of the gypsum board would also need to give their thumbs up for their gypsum board to be used that way.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  14. #14
    Join Date
    Feb 2008
    Location
    New York
    Posts
    868

    Default Re: cement board tile backer over drywall?

    Thanks Jerry. Paper is paper and that is what the mold likes.

    In my bathroom every wall and ceiling is cement board, every joint is sealed with fiberglass mesh and thinset AND everything is coated with a moisture barrier. And while I may have overdone it (that is my way), I am happy I did it that way.

    Steven Turetsky, UID #16000002314
    homeinspectionsnewyork.com
    eifsinspectionsnewyork.com

  15. #15
    Tabb Jensen's Avatar
    Tabb Jensen Guest

    Default Re: cement board tile backer over drywall?

    Yes - you should have backer. But, Tile has been placed on drywall in bathrooms for a long time. It needs care to survive. It needs to be sealed, then resealed as needed, usually every 1-3 years. Water intrusion will destroy it.


  16. #16
    Bruce Lightfoot's Avatar
    Bruce Lightfoot Guest

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by Tabb Jensen View Post
    Yes - you should have backer. But, Tile has been placed on drywall in bathrooms for a long time. It needs care to survive. It needs to be sealed, then resealed as needed, usually every 1-3 years. Water intrusion will destroy it.
    I'm not an HI, just a nosy neighbor on this occasion. I recently saw a situation where a tub spout had been hit hard and popped off a couple of tiles. Backer was 1970's era drywall, a nice bright black where it had not just fallen away, and some surface rotting of the 2x's as well. The handyman's fix was a wrench to re-bend the pipe (leaving a kink in the copper) and a bit of silicone to hold the broken tiles in place. He said he would recommend they install a tub liner when the bottom of the cast iron tub rusted through in a couple of years. Glad I was not the owner!


  17. #17
    Join Date
    Aug 2010
    Location
    BC Canada
    Posts
    368

    Default Re: cement board tile backer over drywall?

    I do not think any builder would put cement board on dry wall at shower closure.


  18. #18
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by Peter Louis View Post
    I do not think any builder would put cement board on dry wall at shower closure.
    I can't imagine why one would even consider doing that??

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  19. #19
    Join Date
    Mar 2010
    Location
    conyers, ga
    Posts
    97

    Default Re: cement board tile backer over drywall?

    Did not see or overlooked in the thread, was this a tiled shower or full fiberglass enclosed, etc ?
    If full fiberglass, or if using panels not as bad but if tiled and not using other membrane then would be bad.
    I still see many continue to use drywall with showers even when using tile, Using Kerdi may be different, just the way many did many years ago and their practice never changed or the way they taught their son taking over the business, etc. Always the way they have done it for forty years and do not want to change.


  20. #20
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by Mike Clarke View Post
    Did not see or overlooked in the thread, was this a tiled shower or full fiberglass enclosed, etc ?...
    Tile.

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  21. #21
    Join Date
    Mar 2007
    Location
    Spring City/Surrounding Philadelphia area
    Posts
    3,509

    Default Re: cement board tile backer over drywall?

    I tell people it doesn't matter if greenboard or straight-up drywall was installed. They will both become damaged, moldy, and spongy if they get wet over and over. I think the only thing you could do John is a look around a cutout/penetration for the tub/shower fixture pipes and see if there is any cement board there. Other than that, I think it's just a guess.

    "It takes a big man to cry. It takes an even bigger man to laugh at that man". - Jack Handey

  22. #22
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by Nick Ostrowski View Post
    I tell people it doesn't matter if greenboard or straight-up drywall was installed. They will both become damaged, moldy, and spongy if they get wet over and over. I think the only thing you could do ...
    ... is change that into a positive and explain to the buyers that ... ... the get to remodel and re-tile the shower every 5-10 years or so, no hard decisions to make as to 'should we or shouldn't we'; that will become 'we need to because the tile is coming loose'.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  23. #23
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by Jerry Peck View Post
    I can't imagine why one would even consider doing that??
    I can, circumstance when specifically required.When a bath/shower is installed upon a common separation wall, such as in a multi-family occupancy, or more often in a row-type townhome which has utilized the specifically prescribed alternative to a masonry "fire wall", i.e. the now prescribed separation and formerly identified UL assemblies for one-hour separations, especially for those "party walls".When the code prescribes a covering to same "or equallivent" to gypsum wall board (equal such as plaster, etc.) the fibercement board is not equallivent in ALL the characteristics necessary when "fire testing" performance of the party wall/firewall one-hour/two-hour fire resistive assembly requiring two-each 5/8" gypsum wall board independantly taped and mudded, staggered on each side of the studding of the wall assembly. I know of NO such vintage or current assembly which allows for the replacement of required gyp board with durarock or similar as a tested (by fire) assembly modification/substitution esp. not repairing a vintage (no longer current code compliant such as insultion or studding) assembly. When Those two 5/8" gypsum board, staggered on studs, independantly taped & mudded on each side of the stud wall is specified - you may not replace one layer (or both) with durarock or similar, unless the entire modification is approved as a part of a listed/tested approved assembly (the entirety of the specification and build of the entire separation wall).To maintain the specification of the (dated edition) of the former assembly - apply to and upon but not a replacement TESTED to the ASSEMBLY which was specified and approved at original construction.

    Last edited by H.G. Watson, Sr.; 04-24-2013 at 09:42 AM.

  24. #24
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by H.G. Watson, Sr. View Post
    I can, circumstance when specifically required.When a bath/shower is installed upon a common separation wall, such as in a multi-family occupancy, or more often in a row-type townhome which has utilized the specifically prescribed alternative to a masonry "fire wall", i.e. the now prescribed separation and formerly identified UL assemblies for one-hour separations, especially for those "party walls".When the code prescribes a covering to same "or equallivent" to gypsum wall board (equal such as plaster, etc.) the fibercement board is not equallivent in ALL the characteristics necessary when "fire testing" performance of the party wall/firewall one-hour/two-hour fire resistive assembly requiring two-each 5/8" gypsum wall board independantly taped and mudded, staggered on each side of the studding of the wall assembly. I know of NO such vintage or current assembly which allows for the replacement of required gyp board with durarock or similar as a tested (by fire) assembly modification/substitution esp. not repairing a vintage (no longer current code compliant such as insultion or studding) assembly. When Those two 5/8" gypsum board, staggered on studs, independantly taped & mudded on each side of the stud wall is specified - you may not replace one layer (or both) with durarock or similar, unless the entire modification is approved as a part of a listed/tested approved assembly (the entirety of the specification and build of the entire separation wall).To maintain the specification of the (dated edition) of the former assembly - apply to and upon but not a replacement TESTED to the ASSEMBLY which was specified and approved at original construction.
    Nonetheless ... one does NOT want tile applied to the gypsum board used for the resistive barrier.

    Therefore my statement/question stands - I cannot imagine why one would put cement-board on drywall ... the moisture will go through the cement-board and ruin the drywall ... I hope *you* would not want the gypsum board installed on a fire-resistive wall ruined by moisture from a shower - repairing that fire-resistive wall will be quite a task to do properly, and permits and inspections will be required, although whomever does the work will think permits and inspections are not required.

    Yes, bathtub shower areas and shower stalls are frequently located next to fire-resistive walls because that reduces the plumbing cost, but it does not take much to offset that cost and relocated those tub and shower areas so they are not up against the fire-resistive walls.

    Just poor planning on the architects part in my opinion. The thing that happens most of the time is that they forget to run the type x drywall down beyond the tub, leaving the under-tub area open to the inside of the fire-resistive wall.

    If the tub and shower areas are to be against that fire-resistive wall, install the type x drywall as required, install furring strips, then install the cement-board, making sure to properly fire-block as needed. Problem solved - except that they now lost 3/4" of space in the condos/apartments along each side of that wall.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  25. #25
    don agel's Avatar
    don agel Guest

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by Peter Louis View Post
    I do not think any builder would put cement board on dry wall at shower closure.
    Believe it nor not caught 3 times in Raeford NC, and once in Wilmington NC this year alone. There are some builders who use sub-par sub contractors and in small townships the building inspection departments may be inadequate to non-existent. Raeford NC falls in Hoke County. That entire area has two building inspectors for the entire department who happen to ride together in the same vehicle. Can't imagine why I cringe every time I get a new construction in that county.

    - - - Updated - - -

    Quote Originally Posted by Jerry Peck View Post
    If the tub and shower areas are to be against that fire-resistive wall, install the type x drywall as required, install furring strips, then install the cement-board, making sure to properly fire-block as needed. Problem solved - except that they now lost 3/4" of space in the condos/apartments along each side of that wall.
    Too easy!


  26. #26
    Join Date
    Mar 2012
    Location
    Lansdale, PA
    Posts
    876

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by Jim Robinson View Post
    Kerdi is designed to be installed directly onto gypsum board. I've done three showers with it so far, and it seems like a good product. They love it over at John Bridge, so I thought I'd try it out. I think it is approved in PA, but it depends on what codes are in use.

    Schluter-KERDI - Schluter-Systems

    It's not necessary to use the rubber liner with it, but it probably wouldn't hurt anything to use a conventional base with the Kerdi system.
    Note the hijack the thread, but...I planning a master bathroom renovation and just read about Kerdi last night (at John Bridge). It does sound like a good product. Did you use it with a mortar bed for the floor?


  27. #27
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: cement board tile backer over drywall?

    Yes. I followed the instructions from the John Bridge web site and the Kerdi instructions. I set the drain height first, then I constructed the sloped floor with the mortar mix. The Kerdi material is applied to the mortar floor and to the drain edges. It's been working great for 5 years or so now.

    Jim Robinson
    New Mexico, USA

  28. #28
    Join Date
    Mar 2012
    Location
    Lansdale, PA
    Posts
    876

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by Jim Robinson View Post
    Yes. I followed the instructions from the John Bridge web site and the Kerdi instructions. I set the drain height first, then I constructed the sloped floor with the mortar mix. The Kerdi material is applied to the mortar floor and to the drain edges. It's been working great for 5 years or so now.
    Thanks for the reply. I am debating between a mortar bed and the prefab bed they make.


  29. #29

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by Mark Reinmiller View Post
    Thanks for the reply. I am debating between a mortar bed and the prefab bed they make.
    I know it has been stated but in the interest of brevity...the pan material and the drywall are both not installed according to the manufacturers standards and specifications!

    Jeff Zehnder - Home Inspector, Raleigh, NC
    http://www.jjeffzehnder.com/
    http://carolinahomeinspections.com/

  30. #30
    Join Date
    Mar 2012
    Location
    Lansdale, PA
    Posts
    876

    Default Re: cement board tile backer over drywall?

    Quote Originally Posted by Jeff Zehnder View Post
    I know it has been stated but in the interest of brevity...the pan material and the drywall are both not installed according to the manufacturers standards and specifications!
    I'm not sure if you are responding to my questions, but I do not see any reason why a mortar pan or drywall backing do not meet the manufacturer's requirements. You can question whether you think the products are adequate for water resistance, but they are approved for that installation.