04-15-2013, 07:53 AM #1
PVC to Cast Iron Waste Pipe
-
04-15-2013, 03:42 PM #2
Re: PVC to Cast Iron Waste Pipe
Looks like it is mortared into the old cleanout connection. Connection is designed to fail over time. Yes you could install a neoprene hub but a new cleanout needs to be added at the PVC pipe for servicing.
-
04-15-2013, 04:15 PM #3
Re: PVC to Cast Iron Waste Pipe
Thanks. You are right. That's a clean-out access.
-
04-15-2013, 06:36 PM #4
Re: PVC to Cast Iron Waste Pipe
And a sanitary tee is required there for the PVC. A clean-out access *is not* suitable for that use.
Obviously ... it "can" be done because you took a photo of it having been done, however, it is "not allowed" to be done - big different in those two words 'can' and 'allowed'.
-
04-16-2013, 04:21 AM #5
Re: PVC to Cast Iron Waste Pipe
TITLE 77: PUBLIC HEALTH
CHAPTER I: DEPARTMENT OF PUBLIC HEALTH
SUBCHAPTER r: WATER AND SEWAGE
PART 890 ILLINOIS PLUMBING CODE
SECTION 890.420 PIPE CLEANOUTS
Section 890.420 Pipe Cleanouts
....
....
....
h) Cleanout Plugs. A cleanout shall not have a plumbing fixture installed in it or be used as a floor drain.
TITLE 77: PUBLIC HEALTH
CHAPTER I: DEPARTMENT OF PUBLIC HEALTH
SUBCHAPTER r: WATER AND SEWAGE
PART 890 ILLINOIS PLUMBING CODE
SECTION 890.320 TYPES OF JOINTS
Section 890.320 Types of Joints
....
...
..
i) Cement Mortar Joints. Except for repairs, cement mortar joints are prohibited.
Section 890.330 Special Joints
....
...
..
g) Plastic Pipe to Non-Plastic Pipe Joints. Joints between plastic pipe and non-plastic pipe shall be made only by one of the following methods:
....
2) Non-pressure piping - Drain Waste Vent (DWV)
A) Caulked lead joints with caulked adaptors.
B) No-hub soil pipe shielded couplings with approved adaptor having a raised bead.
C) Compression type joints for hub and spigot cast iron pipe.
D) Threaded adaptors.
- - - Updated - - -
The part about cement mortar joints has to do with clay sewer repairs. In the past clay sewers were all installed using oakum and cement.