04-30-2013, 04:05 PM #1
Brain overloaded
I am at a loss at how to describe what this heating duct does in the attic, Damper opened when heat is on and pours hot air into the attic. Condensation was noted at air handler and zone damper controls.
Little help please, thanks
Similar Threads:
-
04-30-2013, 06:31 PM #2
Re: Brain overloaded
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
05-01-2013, 04:01 AM #3
Re: Brain overloaded
I'd also include a mention about wasted heat, increased heating costs, the potential for infiltration of airborne attic insulation dust and debris and rodents into the ducts and air handler.
"It takes a big man to cry. It takes an even bigger man to laugh at that man". - Jack Handey
-
05-01-2013, 04:28 AM #4
Re: Brain overloaded
This is done at every air handler, 4 of them, 2 in the attic and 2 in the crawl space.
-
05-01-2013, 05:39 AM #5
Re: Brain overloaded
- Some bizarre attempt at turning the attic into 'conditioned' space in order to avoid having to meet requirements for an unconditioned space?
- Unfinished line that got forgotten about
- some weird heat purge set-up that doesn't make sense
-
05-01-2013, 07:01 AM #6
Re: Brain overloaded
The furnace appears to be a universal flow. Is this a cooling only unit? I don't see a flu pipe. I don't actually see the supply trunk run. The flex duct running on top of the unit is either laying down or is attached to some type of register. A flex duct run should be no more than 10'. I don't see a return air duct. The opened end duct that you are concerned about is too close to the cabinet take off to be a supply ( where is the rest of the supply duct) and the air flow that you are experiencing could be system back pressure . The damper, does it modulate or does it go open and shut? It looks like it is controlled by grey temp. switch? At any rate nothing should be vented into the attic space and should be vented directly out side. Each space that is supplied by the AHU should have its own return back to the unit. See if you can obtain the installation manual from the owner. Call a licensed HVAC contractor and request duct static pressure check for proper air flow requirements for rated efficiency.
-
05-01-2013, 07:17 AM #7
Re: Brain overloaded
You guys! That duct keeps the tech warm and toasty when he works on the unit.
If you choose not to decide, you still have made a choice.
-
05-02-2013, 06:37 PM #8
Re: Brain overloaded
From what I see in the picture you have an air handler with a hot water coil. The grey temp switch appears to be an aqua-stat attached to one of the hot water pipes for the coil. This controls a relay in the air handler to turn the blower on when hot water is present.
Regarding the damper, that is called a dump damper. It is used to maintain the proper static in a forced air zoning system. The purpose is to relieve pressure when some of the zone dampers are closed to keep proper air flow moving through the system. This is one method of maintaining proper static. Another method is to put in a bypass damper connecting the supply into the return.
Both ways of maintaining proper static have drawbacks. As demonstrated in this picture, the dump damper "dumps" conditioned air into unconditioned spaces (like a basement). With a bypass damper, you're short cycling the air back into the air handler and run the risk of overheating the heat exchanger or freezing the A/C coils.
-
05-02-2013, 06:56 PM #9
Re: Brain overloaded
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
05-03-2013, 04:42 AM #10
Re: Brain overloaded
It's hydro air and it is a dump damper, I think this house was spec'd out by the owner who oversized everything thinking it would be better.
Now we have huge ammounts of hot or cold air being dumped into the attic and crawl spaces.
Wood floors at 1st level are cupped in areas and attic shows moisture evidence.
I whacked it! I just wasn't able to pull the wording out of my cluttered brain at time of post.
Thanks for all the comments.
now stop bickering, the report is probably already in the trash
-
05-03-2013, 05:20 AM #11
-
05-03-2013, 06:15 AM #12
-
05-03-2013, 06:30 AM #13
-
05-03-2013, 07:22 AM #14
Re: Brain overloaded
Last edited by Billy Stephens; 05-03-2013 at 04:24 PM.
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
05-03-2013, 07:23 AM #15
Re: Brain overloaded
I agree with the dump damper. I'm assuming it is a zoned system since there appears to be a zone controlled above the system. however, a dump damper should not sent heat or ac to an unconditioned space. Likely to have problems with condensation or ice damming. A bypass damper would be better, but zoned systems can be a hassle to get right.
-
05-03-2013, 05:19 PM #16
Re: Brain overloaded
Is the flex duct to the left that is pointing down into the plywood going thru the plywood decking? It looks as if that may have cut off the open valve and is just sitting on the plywood.
-
05-03-2013, 05:56 PM #17
-
05-03-2013, 07:07 PM #18
Re: Brain overloaded
Billy,
Those things you drew a rounded corner rectangle around look like exhaust fans for bathrooms with remote mounted fans.
-
05-04-2013, 05:28 PM #19
Re: Brain overloaded
I saw this on a house I did Friday. It was also a zoned system. Let me see if I understand this, I hope some HVAC guy will set me straight. The furnace is designed to heat or cool the whole house, when only one zone calls for heat or cooling you have the same amount of air that used to go to whole house now going to half the house. To make up for this and not have too much air going through ducts you dump some of it. The one I saw dumped to exterior. This seems like a real waste of energy. I think someone said you can also dump this back into the return air (bypass damper), is this less wasteful?
-
05-10-2013, 07:59 PM #20
Re: Brain overloaded
I agree mostly Tom. The dump should be going back to the return. If it's going outside there is a major problem in many ways. That air has to be made up somewhere on the return side of the fan or it won't provide the proper flow across the coil. The energy issue is a whole nasty cow in that case.
Relieving or dumping to the return is not overly energy efficient but it offers the luxury of better zone control. I actually like it on small residential systems.
I wonder if the attic or crawl space in the OP's post were meant to be return plenums.