06-26-2013, 06:00 PM #1
bare bulbs in closets - important reminder
As many probably do I call out bare bulb fixtures in closets. I'd say about 1/2 the time I do that and the listing agent is nearby they go into some routine about how ... "that's just overboard, that doesn't really happen, the inspector is just being picky or trying to find things to write up", etc.
You know the routine.
On today's inspection I checked the bedroom closet and looky what I found.
The buyer was horrified. The listing agent was actually really nice and left the Seller a letter explaining the issue.
I thought some of you might want these two pics to use as examples. I don't actually know if they can be downloaded from IN or not. If not send me a PM and I'll email them to you.
I'm going to print out a few copies and keep them in my kit.
Similar Threads:
-
06-26-2013, 06:22 PM #2
Re: bare bulbs in closets - important reminder
Markus,
Excellent photos of what can happen.
To download the photos from IN, click on the thumbnail, after it opens through the magic of Brian's software, click the photo and it will (at least they do on my Google Chrome) open in a new tab, now right click over the photo and select 'save image as' or whatever wording it says indicating that you can save it.
-
06-26-2013, 06:23 PM #3
Re: bare bulbs in closets - important reminder
Yes people knock into them with boxes and I also ask them to not use metal pull chains on them which might conduct electricity if threaded side is live and exposed by busted porcelain.
Article 410 Luminaries (Lighting Fixture), Lampholders, and Lamps
Article 410.8 (B) Luminaries (Fixture) Types Permitted. Listed. The following types of light fixtures shall be permitted to be installed in a closet. Closets (Clothes and storage) eight (square feet (0.74 m²) or larger one of the following type of light fixtures shall be installed:
1. A recessed incandescent fixture with a completely enclosed lamp operated by a wall switch.
2. A surface mounted or recessed fluorescent fixture with a completely enclosed tube(s) operated by a wall switch.
410.8 (C) Luminaries (Fixture) Types Not Permitted. The following fixtures are not permitted:
1. Surface mounted incandescent fixture with enclosed, partially enclosed or open bulbs.
2. Pendant Style
3. Lampholders
Exception:
Walk-in closets of larger area where no storage exists within forty (40) inches (1016 mm) in any direction of a vertical line extending from the floor to ceiling, away from the wall, incandescent fixtures with totally enclosed bulb(s) may be used. Said light fixtures shall be operated by a wall switch.
-
06-26-2013, 07:35 PM #4
Re: bare bulbs in closets - important reminder
Thanks, Marcus. Here's one from my library.
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
-
06-27-2013, 03:26 AM #5
Re: bare bulbs in closets - important reminder
Its not only closet lights. Pot lights above shelving or even interior doors under pot lights can be of concern.
Good find Markus.
-
08-13-2013, 09:22 AM #6
-
08-13-2013, 09:25 AM #7
Re: bare bulbs in closets - important reminder
my boilerplate Bare bulb fixtures are present in the home.We recommend globed fixture installation for safety.
There are dangers associated with light fixture bulbs that are not covered with a globe in an area like a closet. These bare light bulbs often get very hot and can become an ignition source to start a fire in your home. These light bulbs are usually found in attics, closets and crawl spaces. The worst case scenario usually is a closet light. This will either be a plastic or porcelain light fixture, with or without a pull chain.
The danger starts when this hot bulb is either placed too close to combustible materials and they touch or nearly touch the light bulb, or something in the closet falls off of a shelf and right into contact with the bulb.
By installing a light fixture that has a glass globe, the combustible materials will not be able to come into contact with the light bulb, thus nearly eliminating the chance of a fixture starting a fire. Be sure to leave ample room around light fixtures when storing thing s in a closet. This will lessen the dangers of a fire and bring you peace of mind.
-
08-13-2013, 10:35 AM #8
Re: bare bulbs in closets - important reminder
WOW! Thank You
-
08-13-2013, 02:34 PM #9
Re: bare bulbs in closets - important reminder
Here's an example from today's condo inspection. This was inside the utility closet.
Welmoed Sisson
Inspections by Bob, LLC, Boyds, MD
"Given sufficient thrust, pigs fly just fine."
-
08-13-2013, 05:19 PM #10
-
08-13-2013, 06:03 PM #11
-
08-13-2013, 06:58 PM #12
Re: bare bulbs in closets - important reminder
Wire Insulation Identification and Application Guide
MAKE WATTS TYPE of BULB TEMP (°F) @ 12" TEMP (°F) of Lamp Fixture 2 min 5 min 10 min 2 min 5 min 10min ZooMed 150 Infra-red Spot 149 159 171 77 80 82 ZooMed 160 MV Flood 'Powersun' 96 106 115 85 95 102 Westron 160 MV Flood 'MegaRay SB' 98 112 128 74 77 84 ESU 150 Incandescent 'Nocturnal BL' 143 164 165 100 118 118 ESU 150 Incandescent 'Brightlight' 191 209 218 75 77 79 ZooMed 150 Flood 'Basking Lamp' 181 186 195 105 114 123 ZooMed 100 MV Flood 'Powersun' 118 131 136 98 116 118 T Rex 100 MV Spot 'Active UV Heat' 93 114 136 84 102 113 ESU 100 Incandescent 'Nightlight' 134 150 152 78 80 83 ESU 100 Incandescent 'Brightlight' 165 188 194 77 79 81 ACE 100 Halogen Flood 205 226 226 77 82 86 ZooMed 100 Ceramic Heat Emitter 101 127 140 75 99 104 GE 100 Halogen Spot Lamp 158 257 271 75 82 87 GE 100 Halogen Flood Lamp 128 178 187 74 86 88 GE 75 Incandescent Spot 'Black Light' 92 101 103 89 96 97 GE 60 Incandescent 'Black Light' 102 109 112 93 94 105 GE 60 Incandescent Clear Glass 169 176 178 75 81 86 Westron 60 Inline MV Flood Lamp 95 97 103 90 93 98 Westron 60 Inline MV Spot Lamp 130 146 150 Westron 60 Heat Emitter 98 112 130 77 79 80 GE 50 Halogen Spot Lamp 185 193 196 76 85 88 GE 50 Halogen Flood Lamp 123 138 141 74 78 81
Last edited by Billy Stephens; 08-13-2013 at 07:05 PM. Reason: Temp. Chart
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
08-14-2013, 04:24 AM #13
Re: bare bulbs in closets - important reminder
Welmoed
Wise to have mentioned the concern.
As you can see by the chart, there is no indication of a bulb touching the wiring only from 12 inches away.
-
08-14-2013, 05:58 AM #14
Re: bare bulbs in closets - important reminder
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
08-16-2013, 04:31 AM #15
Re: bare bulbs in closets - important reminder
Yes 'fixture' temperature, not the light bulb temperature.
Check via Google what the temp of the exterior bulb can reach.
http://www.tcforensic.com.au/docs/uts/essay1.pdf
Globe of a bulb can reach 300-400 Celcius.
-
08-16-2013, 07:41 AM #16
Re: bare bulbs in closets - important reminder
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
08-17-2013, 04:47 AM #17
Re: bare bulbs in closets - important reminder
For your further edification.
The surface of a 75 watt incandescent bulb reaches about 125 C, whereas the surface of a halogen lamp ranges from 250 to 600 C.
-
08-17-2013, 05:47 AM #18
-
08-17-2013, 07:58 AM #19
Re: bare bulbs in closets - important reminder
Thats okay I knew you couldn't defend your proposition.
So I did a reading using an iR thermometer on an bare 50-100-150 (wattage) tri-light bulb.
After the bulb had been on for 5 minutes the surface temp taken at the top of the bulb was
302 f. and when switched up to 100 watts the temp measured at the top of the bulb was 420 f.
Of course at 150 watts the temp went to 560 f.
You should care your negligent advice could find an inspector in trouble. Then you say you don't care.. real professional of ya. Like they say, you can't fix stupidity.
-
08-17-2013, 08:29 AM #20
Re: bare bulbs in closets - important reminder
Ray, Ray, Ray,
My post have been on a wire touching the fixture and bottom of a bulb in a Supply Closet.
*not a cloths closet with a foam pillow stuffed around it.
** find something else to Fret About ( have you had your Meds Checked as of late? )
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
08-17-2013, 11:27 AM #21
Re: bare bulbs in closets - important reminder
If you can't support your claims claiming you were only speaking about the bulb touching the wire; is nonsense. Then to ad disclaim to your theory you post a chart which doesn't even relate to the issue. And if you cared to enlighten yourself you will see the temp of a bulb from an authoritative article, and by fact actual measurement of a 50 watt bulb can exceed the rating of the pvc sleeve as indicated on the link to the wire chart you provided.
If you have comprehension problems please don't repeatedly try to indicate who may be off their meds..
http://www.reptileuvinfo.com/html/wa...eat-output.htm
-
08-17-2013, 11:54 AM #22
Re: bare bulbs in closets - important reminder
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
08-17-2013, 02:46 PM #23
Re: bare bulbs in closets - important reminder
This is from the 2008 NEC.
- 410.16 Luminaires in Clothes Closets.
- - (A) Luminaire Types Permitted. Listed luminaires of the following types shall be permitted to be installed in a closet:
- - - (1) A surface-mounted or recessed incandescent luminaire with a completely enclosed lamp
- - - (2) A surface-mounted or recessed fluorescent luminaire
- - - (3) Surface-mounted fluorescent or LED luminaires identified as suitable for installation within the storage area
- - (B) Luminaire Types Not Permitted. Incandescent luminaires with open or partially enclosed lamps and pendant luminaires or lampholders shall not be permitted.
- - (C) Location. The minimum clearance between luminaires installed in clothes closets and the nearest point of a storage space shall be as follows:
- - - (1) 300 mm (12 in.) for surface-mounted incandescent or LED luminaires with a completely enclosed light source installed on the wall above the door or on the ceiling
- - - (2) 150 mm (6 in.) for surface-mounted fluorescent luminaires installed on the wall above the door or on the ceiling
- - - (3) 150 mm (6 in.) for recessed incandescent or LED luminaires with a completely enclosed light source installed in the wall or the ceiling
- - - (4) 150 mm (6 in.) for recessed fluorescent luminaires installed in the wall or the ceiling
- - - (5) Surface-mounted fluorescent or LED luminaires shall be permitted to be installed within the storage space where identified for this use.
http://ask-the-electrician.com/electrical/electrical-code/lighting-code.html
-
08-17-2013, 04:31 PM #24
Re: bare bulbs in closets - important reminder
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
08-17-2013, 05:20 PM #25
Re: bare bulbs in closets - important reminder
The bulb is still in contact with the wiring. Common sense prevails whether there is a code provision or not. The code whether it states clothes closet is moot given what is evident in the photo.
More importantly how would our colleagues write it up? My bet is they would put it in the report, again based solely on the photo.
-
08-17-2013, 05:34 PM #26
Re: bare bulbs in closets - important reminder
Last edited by Billy Stephens; 08-17-2013 at 05:46 PM. Reason: again added
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
08-17-2013, 07:26 PM #27
Re: bare bulbs in closets - important reminder
“Talk sense to a fool and he calls you foolish.”Euripides
―
-
08-17-2013, 07:51 PM #28
Re: bare bulbs in closets - important reminder
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
08-17-2013, 08:24 PM #29
Re: bare bulbs in closets - important reminder
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.