Results 1 to 3 of 3
Thread: Sub-panels
-
08-17-2013, 05:40 PM #1
-
08-17-2013, 06:35 PM #2
Re: Sub-panels
A demand load calculation is the only way to know if the service is sized correctly. The fact that the panels are rated for 200 amps has no bearing on the actual load.
All answers based on unamended National Electrical codes.
-
08-17-2013, 07:18 PM #3
Re: Sub-panels
Tell them they have a 100 amp panel and an 80 amp panel. They might believe you or they might not.

Then like Jim says, the 40 breakers in each may be excessive but that would be determined by an electrician doing load measurements.
Last edited by John Kogel; 08-17-2013 at 07:31 PM.
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca



Reply With Quote
Bookmarks