Results 1 to 10 of 10
Thread: gas meter tap off
-
08-20-2013, 04:24 AM #1
-
08-20-2013, 05:30 AM #2
Re: gas meter tap off
Yes, the valve and tap location is wrong. But, the copper line is/was allowed in many areas.
-
08-20-2013, 05:37 AM #3
-
08-20-2013, 06:06 AM #4
Re: gas meter tap off
Last edited by Scott Patterson; 08-20-2013 at 06:11 AM.
-
08-20-2013, 06:51 AM #5
Re: gas meter tap off
Looks as if they drilled & tapped the street ell. I have not seen a ell drilled & tapped from the factory, could be an issue but it is on the low pressure side of the regulator. NG companies in my area won't allow copper tube. Like Scott I don't think the valve is approved for this service & location.
Black pipe looks as if it isn't sleeved, I don't see a ground clamp & wire, maybe it's just outside frame?
-
08-20-2013, 08:00 AM #6
Re: gas meter tap off
thanks everyone...sounds like a bad tap-off like I thought.
no ground clamp here at the meter, only on the water pipe at a hose bib.
-
08-20-2013, 08:08 AM #7
Re: gas meter tap off
All the above. The big nut on the right side of the meter is the "point of delivery" where the federal CFR ends and your local gas codes pick up.
I'm not aware of any such fitting approved by the gas codes as it would tend to weaken the ell, which is part of a swing joint.
Not aware of that valve being a listed gas cock approved
Cannot use compression joints on "gas piping". They are allowed within the appliance since the appliance listing picks them up. Must be downstream of gas combination valve such as a safety pilot.
Copper tubing is allowed if the local supplier confirms less than 0.3 grains H2S per 100 cu. ft.
If aluminum tubing not allowed except inside appliance cabinet as part of listed appliance.
Sleeve and paint pipe entering bldg.
Improper bend radius on tubing off that compression fitting. It will leak or break easily
electrical bonding
How far above grade is the vent on the MP regulator coming into the meter or is there one? How is meter supported/ braced?
Keep the fire in the fireplace.
-
08-20-2013, 08:53 AM #8
Re: gas meter tap off
Bob, you mention electical bonding on the gas meter....if one installed on the water pipe, we still need one on the gas meter?
-
08-22-2013, 11:34 AM #9
Re: gas meter tap off
The gas piping above ground at the meter may be bonded there or inside the building IF it is likely to become energized. Some AHJs want to see a bonding wire from the downstream piping just out of the meter to the EGC regardless of risk, some allow it inside and some don't care.
Gas piping cannot be used as an intentional electrical conductor but must be bonded if there's a chance of this happening.
2009 IRC E3609.7 and G2410.1 and G2411.1
CSST has its own special bonding requirements regardless of likelihood getting energized.
HTH
Keep the fire in the fireplace.
-
08-24-2013, 09:03 AM #10
Re: gas meter tap off
DavidSmith,
Bonding of the gas might not have been required at time of original construction. I typically recommend upgrading the bonding to include hot, cold and gas piping. Areas with lightening strikes often require bonding of all metal, such as gutters/downspouts, ducting, etc. When bonding upgrades have been made, they are often between hot, cold and gas at the water heater.
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/



Reply With Quote

Bookmarks