Results 196 to 260 of 266
08-13-2013, 01:56 PM #196
08-13-2013, 02:04 PM #197
Re: Determining the amperage mat a main disconnect fuse block
08-13-2013, 02:12 PM #198
That math was posted 200 posts ago and you said it was wrong, now you say it was right. Robert and I both said that two 60 amp 120 circuits had the same capacity of one 240 volt. Amazing.
Someone asks a question analogous to how much water can two pipes supply to a house and some want to know how the water gets to the treatment plant.
08-13-2013, 02:19 PM #199
08-13-2013, 02:27 PM #200
08-13-2013, 03:27 PM #201
08-13-2013, 04:12 PM #202
Really Jim
I see your basic knowledge of plumbing is as weak as your knowledge of electricity. For electricity to do work it must return to its source immediately. Water can do work, e.g. turn a water wheel, and dump into the sea, not to return to the headwaters of the river for thousands of years.
08-13-2013, 04:54 PM #203
Still confused by a 120 circuit I see.
08-13-2013, 10:11 PM #204
I believe you have it. A total of a 120 amp load at 120 volts is achievable if you are drawing 60 amps per leg. Leg (A) has a 60 amp load and leg (B) has a 60 amp load. Vern continues to ask where we can actually measure 120 amps. The answer is you can't. There isn't anyplace in the panel you can place an amp meter to measure 120 amps. Even though 120 amps can't be measured, It can be calculated by adding the total ampacity of each leg together. 60 amps + 60 amps. If 60 amps total was all there was available as Vern keeps insisting, you would not have enough current to run a toaster, electric stove, coffee pot, microwave oven, nesco roaster, TV, lights, and furnace all at the same time like we do come thanks giving.
08-14-2013, 05:18 AM #205
Its the same 60 amps. If 120 was available you would be able to measure it because electricity is a science. See my other posts for the correct math and theory...
Or read Vern's post here..he's the only other one that understands the math and theory so far..
Of course, the other issue here is the one of "self appointed experts" and who should you believe.
Jim, Robert, Jerry Peck, and HG all answer questions and promote them selves as "experts". The difference comes when someone disagrees with them. They then spin the question, redirect the issue, try to send you off to check with "someone that knows", accuse you of costing some innocent group money, say you can't even answer simple questions and are spreading misinformation. And call you a TROLL. And often they resort to insults and directly questioning whether you know anything about the subject. ..and add to that--They have checked with their buddy's and they agree with them.
This sure sounds a lot like BULLYING to me!
Thanks for the good example of BULLYING!
08-14-2013, 06:35 AM #206
YES, a 120 amp balanced load would trip a 60 amp OCPD. Anything that exceeds the 60 amps should trip it. And if 120 amps actually existed anywhere in this circuit you could calculate it and measure it in a lab. The dark theory Jim and Robert presented does not exist in this world...
08-14-2013, 07:12 AM #207
Your math shows the same thing that others posted 200 posts ago, but you say yours is correct and theirs is wrong?
Lets try this; Step 1: Install three fully loaded 20 amp breakers all on Leg A. How much load is on the incoming leg? How much load is on Leg B? Do the circuits function properly?
Step 2: install three more fully loaded 20 amp breakers all on Leg B. How much load was just added to the panel? How much load is on Leg A? Has this changed since the addition of the three new circuits? How much load is now on Leg B? What is the TOTAL load that both Leg A and B are supplying? Do all six circuits function properly without opening the fuse or breaker? Turn off all the breakers on Leg A. Has the load on Leg B changed?
As far as the bullying comment, I don't remember anyone besides you and Vern using words like simpleton or advising a career change.
Actually it would not. There would be 60 amps on each leg which is not over the trip limit of the breaker or fuse. In fact, your math even show the 7200 watts on each leg. Care to reconsider your answer?
08-14-2013, 07:17 AM #208
Here's the correct math for your example----------AGAIN
Jim--your are still missing the fact that A phase and B phase are 180 degrees out of phase which makes one + and one - in respect on one another at any give time. And you can't take the total wattage at the 240 volts and divide it by 120 and have anything meaningful. The correct problem equivalent of 240 is the (2 X 120).. not a single 120. This leads to a mathematical error and an incorrect assumption..
The 2- 60 amp loads on A and B phases are added using vector addition and since they are 180 degrees out of phase it is as easy as sliding your finger up and down a number line ( much like in 5th grade).
08-14-2013, 07:21 AM #209
08-14-2013, 08:13 AM #210
Here is one example.
And you continue to miss that someone could add a 60 amp load to one leg or both legs and the panel will still function. This is the same premise from over 200 posts ago. This can be measured.
08-14-2013, 08:16 AM #211
There you go--using a half-truth to make yourself look good. Again you are using oranges to prove and apple theory.
Thanks for agreeing with me again.. Lets see that's 6 times now.... I have not missed that point---again you spin it and half-truth it to seem like you are right. And you are not!
08-14-2013, 09:33 AM #212
So 60 amps on two legs does not equal 120 amps of capacity? You can run two 60 amp 120 volt loads from one panel but the panel will not support 120 amps of load? Interesting.
I will bow out and leave you and Vern to your confusion. As Robert said many posts ago, it didn't matter how many times and different ways that this would work there is no light at the end of the tunnel.
Sorry that you never took the challenge to post this topic on an electrical forum.
08-14-2013, 09:44 AM #213
After 45 years of teaching and doing the math and science of electricity ( a degree in Communication Electronics and Science and a life long practicing master electrician) I would have to say I have probably taught some of them about the NEC or the science of electricity. Really Jim--it is simple enough that someone with a 5th grade education could grasp. I have said "I could teach anyone to be an electrician" but I am wrong because there are at least 3 of you wouldn't make it....
08-14-2013, 09:54 PM #214
Hello, all, I am new here. I would like to respond to the discussion about electrical cabinet capacity. I have been in the multifamily industry for nearly 40 years, and have a lot of experience with electrical circuits. This topic is a difficult one to grasp at times. The ampacity of the cabinet in question (or any cabinet, for that matter) is the rated ampacity for the main disconnect. In this case the disconnect is rated at 60 amps. This means that this cabinet has an ampacity of 60 amps. The "legs" (more correctly, "poles") are not additive. If one would employ a clamp-style ammeter, clamp around both poles (service drop conductors), one would see a reading on the ammeter of zero amps if both poles were utilizing 60 amps of current simultaneously. If one pole is using more current (for example, a 120 volt lighting circuit is being utilized in addition to a 240 volt HVAC system), the ammeter would display the current difference ONLY. I wrestled with this concept until I performed the action I described by clamping my digital ammeter around the main conductors in a service panel just to see the outcome. VOILA! My Four Rules for Living: #1- Don't panic (thanks Mr. Adams); #2 - Pay attention; #3 - Learn something every day; #4 - When all else fails, read the directions.
08-16-2013, 08:43 AM #215
Hi Joe, Welcome to this forum. You will find lots of useful information here. I look forward to seeing you post more often. I might add that all threads are not like this one. Another qualified electrical guy like yourself is needed. You just have to be willing to sort out the BS and Bullying from the real information.
08-16-2013, 10:37 AM #216
If you insert one double pole 60 amp breaker and put a 60 amp load on it, you've maxed out the available amount of current on both legs and any more breakers whether it be single or double pole will blow a fuse. The amperage available, determined by the amperage of the fuses, is based on 240 volts, not 120 volts. If you exceed 60 amps at 120 volts on either leg, you will blow a fuse, If you exceed 60 amps at 240 volts, you will blow fuses. this is why its a 60 amp panel.[/QUOTE]
I wanted to quote this and clear it up - The difference between a double (or three breaker) and fuse cartridges is that the breaker [more than one pole] is tied to the other so if one leg exceeds the rating all poles trip - this is done to keep the load somewhat balanced between the hot legs.
You can draw 60 amps (using this example) off of each leg - so to make this more of a mess let's talk about industrial loads "Three Phase Power" In this situation you have three hot legs and each leg is 120 degree out of phase with each other, Sometimes you have a neutral and sometimes you do not. However Now you have three fuses rated at 60 amps (remember amps are amps no matter what the voltage is they are still amps) the rating of the service would be 60 amps because that is the most you can draw through a hot leg.
The return get's a little confusing in 120 v circuits when we start looking at the load of the neutral because the neutral is often tied to the ground and in a home the neutral coming off the street is earth grounded at the transformer with a grounding rod , just like in a house (often tied to a water pipe) so if you could isolate the neutral and the ground and actually measure it where you are drawing your power - you would actually have two current reading (I know what the code says about grounds not being load carrying conductors) and these two readings (done at the same time with two meters) would add up to 120 amps - if you were to draw 60 amps from each leg.
On a side note I have found this thread to be most amusing and really , stop pulling my leg.
08-16-2013, 11:09 AM #217
08-16-2013, 11:56 AM #218
08-16-2013, 12:02 PM #219
Hey Dwight, Use this diagram to show us what you are thinking..
08-16-2013, 12:12 PM #220
08-16-2013, 01:38 PM #221
Why don't you share some more of your knowledge? I would have thought with all that experience you would know how to use a clamp on ampmeter.
I know the reading will be useless, even on a single pole circuit.
08-16-2013, 02:01 PM #222
You really do need to give it up.
Putting a clamp-on ammeter around the hot and neutral of a single pole? circuit will tell you if there are neutral to neutral faults in the circuit. If it reads anything except 0 amps the neutral current is going somewhere else. This creates, rather than cancels electric fields..
08-16-2013, 02:21 PM #223
I will add that a small portion of the population is physically sensitive to stray electric fields. They make them physically ill. They solve it by having all the neutral to neutral faults corrected and installing a special isolation transformer (scared yet?) to supply their residences. Not to mention stray electric fields have a direct interference to sensitive electronic equipment..
08-16-2013, 02:58 PM #224
That method would not tell you the load on the panel which was the subject under discussion. We were not looking for neutral to neutral faults.
08-16-2013, 04:20 PM #225
08-16-2013, 05:12 PM #226
Of course, Mr.Port, I am well-versed in the use of clamp ammeters, having owned both analogue and digital flavors (one of the first on the market, the A.W. Sperry Digisnap 1000, ca. 1982). I used them mostly to test the three-pole 300 amp contactors on the electric water heaters at the multifamily communities where I supervised the HVAC/plumbing crews. My present digital ammeter is bluetooth-enabled so that the meter can drop data into my laptop regarding voltage/current/temperature over time. I also use it to test start and run capacitors in HVAC systems. My intent was to illustrate that a simultaneous 60 amp load ON BOTH POLES OF THE SERVICE DROP does not constitute a 120 amp panel. The question has been answered many times here. The cabinet is a 60 amp panel. By the bye, the reading on a single-pole circuit would be 60 amps if there is a 60 amp load; your logic is erroneous, as one would be using the meter correcly, having clamped only one conductor, as is required for ampacity measurement.
08-16-2013, 06:52 PM #227
I read it as you were testing the load by clamping both conductors, not one. Sorry for the confusion.
08-16-2013, 09:21 PM #228
Well here we are at over 250 posts and Judge Judy is about to reign down her wrath
. Before I am sent off to the hall I would like to apologize for loosing my cool to all of my friends on IN, including and most importantly to Jim and Robert.
I truly was just trying to help people understand what was happening inside the 3-wire circuit. It does not really matter if you understand it fully to be able to size breakers and wiring, using ohms law formulas. Knowing the maximum current that can be on each leg, you will come up with the correct answers, and the maximum current will be the breaker size.
Where the most problems came from in this thread was from the terms used. Jim and Robert used the term "amp load" throughout the discussion. Amp load is typically reserved for electric motor and battery loads. In this discussion the term "amp load" was used synonymously with "watts or power". The original question was directed at "current" which is only one part of the formula to find power.
The 3-wire circuit, as in all circuits, is a continuous loop. A good analogy of the loop would be that of the lazy river that is found in many amusement parks. All of the water leaves the pump and sends inner tubers down the river, some of the tubers may take a short-cut back to the pump station, because there is a traffic jamb on the return leg (less load or more resistance), but they are using just some of the same current that is taking the rest of the tubers the long way around. When the traffic (load) is the same on both legs of the river, no tubes take the short-cut (neutral) but return to the pump via the main return leg. We can get the current to do more work "power" by adding more tubers (loads) but it requires more current. The total current is still in a loop so whether we split it at the short-cut or not is irrelevant. The total current leaving the pump must equal the current returning to the pump.
I hope this has helped someone, and will now go take my beating for prolonging this thread
08-18-2013, 10:23 AM #229
08-18-2013, 12:15 PM #230
You know Rick, I too noticed the same thing , no name call, no back stabbing , no cheap shots below the belt
There is something just Un American about the whole thing - it disgusts me
Actually , I am really proud to see people acting in a professional way trying to help someone understand a difficult concept.
09-04-2013, 09:36 AM #231
I may not have seen the answer I was looking for in the volume of posts written here, but the size of an electric service is determined by the lowest rating of the following three things: rating of the service conductors, manufacturer's rating of the equipment, and the rating of the over current device(s).
The size of the over current device is determined by the maximum size of load per hot leg. All other things equal, a 60 AMP fuse would limit a service size to a "60 AMP service". Two hot legs with 60 AMP fuses do not make a 120 AMP service any more than 3 of them make a 180 AMP service. Service size refers to the maximum size of an individual connected load. On a 60 AMP single phase service you can hook up a 240 volt 60 AMP load or two 120 volt 60 AMP loads. You can't hook up a single 120 volt 120 AMP load - ergo you have a 60 AMP service.
The maximum capacity of the service will be determined by the total wattage allowed by the voltage and overload size.
09-04-2013, 05:52 PM #232
As I know the correct answer for the previous thread, let me ask a question. How can a MWBC using # 12 wire for all of the conductors be allowed to be supplied by 20 amp breakers if the potential current on the grounded conductor is 40 amps? Is such an installation cited as non- compliant?
09-04-2013, 06:32 PM #233
09-04-2013, 06:37 PM #234
09-04-2013, 07:26 PM #235
A properly wired MWBC will have the two hots on opposite legs of the panel. The neutral will carry the difference, not the sum of the hots.
09-04-2013, 07:41 PM #236
09-05-2013, 06:31 AM #237
09-05-2013, 07:42 AM #238
09-05-2013, 07:55 AM #239
09-05-2013, 08:06 AM #240
09-05-2013, 09:02 AM #241
Why does he say this over and over again in regards to the orginal post??
U.S. Illiteracy Statistics Data Percent of U.S. adults who can’t read 14 % Number of U.S. adults who can’t read 32 Million Percent of U.S. adults who read below a 5th grade level 21 % Percent of prison inmates who can’t read 63 % Percent of high school graduates who can’t read 19 %
09-05-2013, 09:24 AM #242
09-05-2013, 02:36 PM #243
09-05-2013, 04:03 PM #244
Nice Try.
John Kogel
Member
Join DateFeb 2009LocationSouthern Vancouver IslandPosts3,603
Re: Square D panel
It appears to be a split bus panel with the 50 amp breaker protecting the lower half. But this reply will bump your thread ahead of that other one which has bored most of us for 3 weeks, so hopefully you will get your answer today.
09-05-2013, 05:43 PM #245
09-05-2013, 05:59 PM #246
You keeping saying the same thing trying to make it true, when it isn't. You can't dispute the math and science not matter how many times you say it. Vern as well as myself can prove our position, you can only state yours. You have a growing following though---3 or 4 now..
09-05-2013, 06:23 PM #247
Others have also explained numerous times the error of your understanding of the issue. It is such a shame that someone of your professed experience cannot grasp this simple concept.
09-06-2013, 04:56 AM #248
09-06-2013, 05:50 AM #249
Re: Determining the amperage at a main disconnect fuse block
Just so it is clear. The answer is a 60 amp service. The two legs are not added to give the capacity of the service. And when installed according to the NEC there will not be more then 60 amps present at any point in the circuit.
I see Jim has started with his bullying tactics. That's a real shame that you cannot rise above your mistake and your ego.
Jim, you have agreed with me 7 times now but insist your statement is true. What's up with that?
09-06-2013, 07:46 PM #250
Roland, obviously I do not agree with you since I have said from somewhere on page 1 that the panel has a capacity of 120 amps at 120 or 60 amps at 240. I simply corrected your statement about the capacity per leg. You keep saying the limit is 60 amps regardless of voltage. It seems from the post from Robert concerning generator capacities that the engineers for those companies too agree with me. There never was an issue with the correct size of the service.
I again will invite your to post the same question as asked by the OP on an electrical forum and post a link to it. Since you have refused multiple times I will assume you do not want to submit yourself to ridicule and further embarassment.
Speaking the truth and refusing to waver is not a matter of ego. Simply because you do not like the answer does not make it wrong.
And once again you accuse me of being the bully when the true issue is your inability to understand a simple issue. I never posted literacy figures trying to infer anyone's lack of knowledge.
09-07-2013, 05:54 AM #251
I see you don't understand how a 240/120 volt generator is wired. I can certainly understand why you are confused about the connection of a single phase transformer. Again apples and oranges--will it never end? Or do you like fruit salad?
I still don't understand why you keep agreeing with me in between your insults?
The 60 amps you speak of is not +60 and +60 . You get your answer only with a math error. If one truly understands the math and the concept it develops what is known as adaptive reasoning. That is where you take what you know is correct problem solving and apply it to more complex problems and still come up with the correct answer.
Just a funny note though: I just watched a video of a teacher explaining to a PTA group why 3 X 4 = 11 is a correct answer under the new common core math model the President is driving. No wonder our economy and everything else is slipping into the dark pit...It was funny. I see you have already taken that course.
09-07-2013, 04:49 PM #252
You say I am wrong but you say I keep agreeing with you?
Ironic that you say this since you clearly cannot get the correct answer from this:Just a funny note though: I just watched a video of a teacher explaining to a PTA group why 3 X 4 = 11 is a correct answer under the new common core math model the President is driving. No wonder our economy and everything else is slipping into the dark pit...It was funny. I see you have already taken that course.
You have stated numerous times that 60 + 60 = 60. I doubt that even a first grader would agree.The 60 amps you speak of is not +60 and +60 . You get your answer only with a math error. If one truly understands the math and the concept it develops what is known as adaptive reasoning. That is where you take what you know is correct problem solving and apply it to more complex problems and still come up with the correct answer.
Perhaps you can explain the generator ratings posted by Robert above and tell us why the voltage ratings change the ampacities? Surely not all the engineers are wrong.
09-07-2013, 04:57 PM #253
09-07-2013, 10:00 PM #254
You would be surprised at the PM's in my message box!
Or better still, we could tell G.E. and all the rest of the panel manufactures that they have been under selling there product as they only have a code for one current ratting per panel.
I have edited my analogy from post 251 to try and make it as clear as I can.
The 3-wire circuit, as in all circuits, is a continuous loop. A good analogy of the loop would be that of the lazy river that is found in many amusement parks. All of the water leaves the pump and sends inner tubers down the river, some of the tubers may take a short-cut back to the pump station, because there is a traffic jamb on the return leg (less load or more resistance), but they are using just some of the same current that is taking the rest of the tubers the long way around. When the traffic (load) is the same on both legs of the river, no tubes take the short-cut (neutral) but return to the pump via the main return leg. The same current that took the tubers down one leg will take them up the other. The total current is still in a loop so whether we split it at the short-cut or not is irrelevant. The total current leaving the pump must equal the current returning to the pump. We can measure the current on the down leg (A) and again on the up leg (B). As a matter of fact we could measure current at several more locations but it is all the same, or portion of the same, current that left the pump. The number of measurements taken are not additive.
As I said before in 251, we can use the current in each of the legs to calculate power using 120 volts and come up with the correct answer. But if you do not understand the "lazy river" then you do not understand the circuit.
I hope we can all agree and put this one to bed.
09-08-2013, 07:19 AM #255
I have posted this information before. Did you forget or just not read it? I am sorry you don't understand the generator wiring and make ignorant statements such as you did. Every major published textbook on AC/DC theory, electrical engineer, physicist and math professional as well as 100's of years of science are on my side and would agree with the math as I have stated it. I don't need any more on my team...
09-08-2013, 10:16 AM #256
You cannot add the rms AC Amperage limitation capacity of the two fused conductors and claim that the amperage capacity has doubled!
Each of these two "hot" conductors are SINGULARLY FUSED each in-line or series at the origination of the 3-wire (with or without ground) occupancy "mains" power feeder.
The rate (speed, accelaration, change of direction) of electron transfer as RMS'd does not increase. The ONLY thing that can increase (or decrease) is the RMS Voltage at max (amperage) capacity. The legs are not going to magically increase (for very long before the fuse opens - and for that matter the companion fuse) the number of electrons passed in a single second (60 cycles) or a tenth of a second (six cycles) to RMS 120 amps as long as functioning fuses and correctly rated (temp, voltage, type, etc.) are in place singularly in series with nothing but simple resistance loads and no induct. generator or other load-side.
There is NO WAY a simple properly wired/configured 120/240 Volts RMS AC split (center-tapped) single phase 3-wire FEEDER with fused on both hots with 60 amp fuses can be in any way confused to have a 120 Amp RMS capacity. (without some transformtation, inversion, generation, induction, introduction of of, etc. load side of same!)
120/240 = 1/2 = 180/360. 120 Vrms AC - ( - 120 Vrms AC) = 120 Vrms AC + 120 Vrms AC = 2(120 Vrms AC)V(A) = VA = V x A(V rms AC) x (A rms AC) = VA{120/240 V rms AC (that's a fraction - which is the product of 240V rms AC center tapped) V rms AC} x (60 A rms AC) = the Volt-Amps rms AC available (not really, there are a host of more complicated mathmetical functions to consider).
For both legs (2): (at the voltage side of the compound equasion) multiplies same (front end) by 2 (in the form of 2/1 actually). That function occurs to the modification of the Voltage factor BEFORE multiplying the voltage factor by the Amperage factor to determine approximate VA rms.
You can remember the "order" of the equasion by remembering (1) it is the voltage factor which has changed in your application and (2) the Intensity (amperage) for each conductor remains LIMITED by the FUSE present (in-line, in-series) in each conductor AHEAD of the Load. Finally, there is a reason we refer to the product as Volt-Amps, not Amp-Volts.
Remember, each conductor is FUSED at 60 amps, Line-side of the FEEDER. There is no CB.
Little of this five-page discussion has been on-topic of the OP.
The capacity is current-limited to 60 amps rms regardless of the voltage (as long as the fuse is capable of functioning properly in the presence of what ever voltage the conductors/feeder circuit is exposed to). Generally that would be approx 50 - 600 Vrms AC for the type of fuse commonly employed for a strictly residential occupancy, strictly single-phase; however we do not know the age, vintage, nor the SERVICE arrangement for the OP's TWO-HUNDRED-UNIT Apartment Building and Unknown building requirements as well as unknown other (mixed) occupancies.
{2 ( 120/240 V ) } x (60 A) = VA That's the same whether there are all 120V loads, all 120/240 loads, all 240V loads, or a mix of loads; its STILL JUST 60 A.
Finally when you "minus a minus" the "minuses" cancel out, the result is a function of positive values.
AC both voltage and Intensity are alternating. acceleration and deceleration in AC sinusodal.
Intentionally avoided peak and peak-to-peak as this would only further distract and confuse the majority (as well as a host of other issues), K.I.S.S. and kept it at elementary (4th-grade) mathmatics and 5th-grade Physics.
The limited capacity of the OP's question is sixty (60) amps based ONLY on the OP's information (limited) regrding the presence of the fuses. Whether or not the fuses are correctly determined, the unknown ambient conditions of the "room" hosting the fuses, the resistance, if the conductors run nything other than perfectly straight, the temperture rating and condition of the conductors (and insulation), ratings and conditions of contacts, and a host of other considertions, we cannot say.P.S. the likelyhood of the OP's 200-apartment-building's singular apartment's feeder supply being 120/240 VAC single-phase is SLIM.
Last edited by H.G. Watson, Sr.; 09-08-2013 at 10:47 AM. Reason: lost every dang paragraph. hopefully inserted enough carriage returns to make it readable. that auto save feature of the forum glitches!
09-08-2013, 01:14 PM #257
Nice Mr. Watson!! I was about to float Jim's rubber duckies down Vern's lazy river.
09-08-2013, 01:45 PM #258
I see Watson can't add 7200 + 7200 and come up with 14400 either.
09-08-2013, 01:50 PM #259
09-08-2013, 02:15 PM #260
I will leave you to wallow in your confusion. Professionals that work in the trade every day along with engineers for the generator companies have explained ad infinitum why you are wrong. Please stay away from the edges of the earth. I wouldn't want you to fall off.