Results 1 to 22 of 22
  1. #1
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default neutral terminal

    What are the odds that this terminal is rated for two wires? This place was huge, and was wired very pro, but this showed up in one of the 7 panels. It feeds from one panel to the next one beside it. I searched on the web but can't find any single hole lugs that size rated for two wires.


    d

    Crawl Space Creeper
    Jim Robinson
    New Mexico, USA

  2. #2
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: neutral terminal

    I can't see the photo.

    All answers based on unamended National Electrical codes.

  3. #3
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: neutral terminal

    Quote Originally Posted by Jim Port View Post
    I can't see the photo.
    Thanks. Not sure what happened there.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Jim Robinson
    New Mexico, USA

  4. #4
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: neutral terminal

    I agree with you Jim, one only. This could be confirmed by checking the label in the panel that should show the number and acceptable size range.

    All answers based on unamended National Electrical codes.

  5. #5
    Join Date
    Mar 2013
    Location
    Md and or PA
    Posts
    137

    Default Re: neutral terminal

    Looking at the photo I think it is a tough call to make one way or the other. They do make lugs that are designed for two conductors that look just like that one. The actual lug is marked for the number of conductors and the size , but it it tough to see as it is normally stamped on the part that bolts to the panel. That lug looks deeper than most. The lugs that look like that one and are designed for two conductors will normally have an elongated opening for the two conductors thus making them deeper than the standard. That's just my 2 cents worth


  6. #6
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: neutral terminal

    I've spent about 30 minutes on Thomas and Bett's web site, and I can't find one lug that is rated for two conductors that doesn't have two separate holes for the wires. My report isn't due until Monday. I have a call in to my old boss who has been a commercial electrician forever, so I'll see what he says.

    Jim Robinson
    New Mexico, USA

  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: neutral terminal

    Quote Originally Posted by Jim Robinson View Post
    I've spent about 30 minutes on Thomas and Bett's web site, and I can't find one lug that is rated for two conductors that doesn't have two separate holes for the wires. My report isn't due until Monday. I have a call in to my old boss who has been a commercial electrician forever, so I'll see what he says.
    Do you have a photo showing that terminal lug from a different angle? It is quite possible, due to the apparent height of the lug (or is that an optical illusion?), that the terminal lug is rated for two conductors.

    I've seen some which had (as best I can think of describing them): two 'half holes' in the terminal, one above the other, and the terminal lugs were identified as being rated to 2 conductors along with the size of the conductors allowed in the terminal.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: neutral terminal

    That's the only photo I have. It was in a tough spot to get the photo. Any recollections of what brand had one with the two wires allowed? I have looked and looked, and I can't find one. That's a 2/0 and #2 wire I think. I have to look back in my notes.

    Jim Robinson
    New Mexico, USA

  9. #9
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: neutral terminal

    It is round, not oval of figure eight shaped.

    Jim Robinson
    New Mexico, USA

  10. #10
    Join Date
    Mar 2013
    Location
    Md and or PA
    Posts
    137

    Default Re: neutral terminal

    It would also help if you had posted the manufacture and model of Panel that it is in.From what you said in your original post I am curious if it a factory designed feed thru panel?


  11. #11
    Join Date
    Dec 2007
    Location
    Chico,Ca
    Posts
    454

    Default Re: neutral terminal

    The panel looks like a SQ D NQOD, do you have a catalog number of the panelboard interior? It may help in deciding if it is OK , if info is avail. online or in a SQ D catalog.


  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: neutral terminal

    Quote Originally Posted by Jim Robinson View Post
    It is round, not oval of figure eight shaped.
    Then, most likely, it is only rated for one conductor.

    It is a good practice to take a photo of the panel label, especially if you have any questions about it, but taking a photo of the label anyway (questions or no questions) will make it easier to answer questions which may come up later.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  13. #13
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: neutral terminal

    I don't see anything in 408.41 (2011 NEC) that restricts the application of the rule of one grounded conductor per terminal to branch circuits in a panel regardless of the listing of the lug. This application would require a lug with 2 separate connections (2 holes, 2 setscrews)

    408.41 Grounded Conductor Terminations. Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.

    Exception: Grounded conductors of circuits with parallel conductors shall be permitted to terminate in a single terminal if the terminal is identified for connection of more than one conductor.

    Occam's eraser: The philosophical principle that even the simplest solution is bound to have something wrong with it.

  14. #14
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: neutral terminal

    I should have written down or photographed the data sticker, but I didn't. Good call on the NQOD, I do think that is what the panel is, circa 1998. The only spot where I can see that two wires are allowed are when there is a pass through lug installed. That is not the case here.

    I found a PDF for a similar, if not the same, panel. Page 11 shows the pass through lugs, which don't look like this one.

    http://static.schneider-electric.us/...1630CT0701.pdf

    I'm confident enough to cut that part loose. Now if I could just verify my boiler pump wiring once and for all.

    Jim Robinson
    New Mexico, USA

  15. #15
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: neutral terminal

    highlighting with bold and underlining are mine:
    Quote Originally Posted by Bill Kriegh View Post
    I don't see anything in 408.41 (2011 NEC) that restricts the application of the rule of one grounded conductor per terminal to branch circuits in a panel regardless of the listing of the lug. This application would require a lug with 2 separate connections (2 holes, 2 setscrews)

    408.41 Grounded Conductor Terminations. Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.

    Exception: Grounded conductors of circuits with parallel conductors shall be permitted to terminate in a single terminal if the terminal is identified for connection of more than one conductor.
    Could thye be parallel conductors? They look to be the same size.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  16. #16
    Join Date
    Mar 2012
    Location
    Northern Indiana
    Posts
    98

    Default Re: neutral terminal

    Does't anyone else think that that lug is NOT original to that equipment?


  17. #17
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: neutral terminal

    It does look strange with the mounting bolt appearing to be under the neutral bar. It does look taller than the normal factory lug.

    All answers based on unamended National Electrical codes.

  18. #18
    Join Date
    Dec 2007
    Location
    Chico,Ca
    Posts
    454

    Default Re: neutral terminal

    Quote Originally Posted by Jim Port View Post
    It does look strange with the mounting bolt appearing to be under the neutral bar. It does look taller than the normal factory lug.

    I just pulled a lug off a scrap SQ D interior, and the angle of the photo just makes it look strange, wanted to look at the data on the lug & it was a "standard" single conductor lug made by Ilsco w/ a range of 6 AWG to 300 MCM.

    Reason it's scrap is the deadfront is missing.


  19. #19
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: neutral terminal

    Not parallel conductors, just tapping over to the next sub panel beside this one. I also think the lug was added to the panel. I'm on safe ground here. If that lug is rated for two conductors of that size, I can't find it in any electrical supply catalog.

    Jim Robinson
    New Mexico, USA

  20. #20
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: neutral terminal

    Quote Originally Posted by Jim Robinson View Post
    Not parallel conductors, just tapping over to the next sub panel beside this one.
    Then the exception to allow two grounded (neutral) conductors in one terminal which is identified for two conductors does not apply - meaning it is not allowed (even if the terminal had been designed and listed for two conductors).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  21. #21
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: neutral terminal

    Quote Originally Posted by Jim Robinson View Post
    What are the odds that this terminal is rated for two wires? This place was huge, and was wired very pro, but this showed up in one of the 7 panels. It feeds from one panel to the next one beside it. I searched on the web but can't find any single hole lugs that size rated for two wires.


    Seven panels.
    Have you considered the possibility that these are serivice conductors and the adjacent panel is not being fed, but supplied as additional service equipment? Where is the bond to the local grounding system taking place (outside - meter can ? or inside)? What sort of raceway between these adjacent panels and how are they bonded? I don't recall you're having said in the discussion that the hot conductors from one panel to the next one beside it" were actually OC protected in the first, just that this panel suposedly "feeds", and I am suspicious of that conclusion without more information and guess that there just may be more than one MCB service panel constituting the "service". Are there multiple metered occupancies present?

    If there is an engraved "2" on the lug this would be definitive, as would a notation on the wiring diagram/label for the panel. From the the shadowed poorly lit and staged vantage point of the photo and presuming the same type the grounded (service?) conductors appear to be the same size.


  22. #22
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: neutral terminal

    Quote Originally Posted by H.G. Watson, Sr. View Post


    Seven panels.
    Have you considered the possibility that these are serivice conductors and the adjacent panel is not being fed, but supplied as additional service equipment? Where is the bond to the local grounding system taking place (outside - meter can ? or inside)? What sort of raceway between these adjacent panels and how are they bonded? I don't recall you're having said in the discussion that the hot conductors from one panel to the next one beside it" were actually OC protected in the first, just that this panel suposedly "feeds", and I am suspicious of that conclusion without more information and guess that there just may be more than one MCB service panel constituting the "service". Are there multiple metered occupancies present?

    If there is an engraved "2" on the lug this would be definitive, as would a notation on the wiring diagram/label for the panel. From the the shadowed poorly lit and staged vantage point of the photo and presuming the same type the grounded (service?) conductors appear to be the same size.
    Thanks for joining in a week after the last post and bringing all sorts of extraneous questions to the table. The question certainly seemed easy enough to understand and answer for all the other contributors without all the sidetrack.

    All answers based on unamended National Electrical codes.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •