You mention a beam, but don't mention the size, just the size of the joists above. If the beam is compromised, replace the beam with a comparable member. If replacement is not practical, a repair should be designed by a licensed structural engineer.
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
12-09-2013, 02:13 PM #3
Re: How to Repair a Notched Beam
Gunnar is correct, the beam size is what needs to be known as the beam is allowed to be notched, and is allowed to be notched up to the 1/3 point, and is allowed to be notched up to 1/3 the actual depth of the beam, meaning that ... it is possible ... that the notch may be allowed (depending on the size of the beam).
-
12-09-2013, 03:35 PM #4
Re: How to Repair a Notched Beam
-
12-09-2013, 05:06 PM #5
Re: How to Repair a Notched Beam
Yep, my apologies, "and is allowed to be notched up to 1/3 the actual depth of the beam" should have been:
"and is allowed to be notched up to 1/6 the actual depth of the beam"
Got carried away typing 1/3 ... 1/3 ... 1/3 ... me bad, need to be more careful next time - thank you Raymond.
I should have said that the notch could be 1/3 the depth for the max length of the notch, but the notch is only allowed to be 1/6 of the depth of the beam.
-
12-10-2013, 03:52 AM #6
Re: How to Repair a Notched Beam
You are welcome Jerry, we are all here to help one another. I am just glad you did not hit the 6 key 3 times - 666. In which case you could have said the 'devil made me do it!'

-
12-10-2013, 08:40 AM #7
Re: How to Repair a Notched Beam
Around here you are not allowed to touch any beam without structural analysis.
Just to muddy the waters a bit, but...
https://engineering.purdue.edu/~jliu...tching_IBC.pdf
In just reading the one page it seems these rules apply even (using sawn lumber) if there is a point load? Or, is there another page that addresses that issue and this page applies only to uniformly loaded beams?
Seems odd that if someone spec'd a beam size (sawn lumber) to carry a load, and you meet the code requirements for notching all is well. I think the designer might have some say depending how the beam is loaded and where the notch is located.
-
12-10-2013, 04:20 PM #8
Re: How to Repair a Notched Beam
-
12-19-2013, 06:14 PM #9
Re: How to Repair a Notched Beam
-
12-20-2013, 07:55 AM #10
Re: How to Repair a Notched Beam
Where a beam is split or is found notched, anything that is obvious improvement should be considered, for prompt action. Here is what I have done:
Energy Conservation How To: Strong Attic Floors
-
12-20-2013, 09:04 AM #11
Re: How to Repair a Notched Beam
Last edited by Garry Sorrells; 12-20-2013 at 10:15 AM. Reason: aded pict
-
12-20-2013, 11:05 AM #12
Re: How to Repair a Notched Beam
Here's an option (assuming that the notch is not within the allowed limits): Metwood Joist Reinforcers | Floor Joist Repair | Metwood Store
-
12-21-2013, 02:41 AM #13
Re: How to Repair a Notched Beam
I'm very curious--Is it now common practice for home inspectors to recommend how to make structural repairs? Seems like it could make for some potential problems, if/when the buyer proceeds to do "what the inspector told me to do," and the structure suffers a significant failure. Even if the failure occurs elsewhere (and unrelated to the repaired member), we all know the lawyers will name the home inspector who proposed specific repair methods (and his/her liability carrier) as defendants in the lawsuit.
It's been a few years since I've been out of the inspection business--Have most SOPs since changed to allow inspectors to make structural repair recommendations?
-
12-22-2013, 08:19 AM #14
Re: How to Repair a Notched Beam
Bridgeman,
It boils own to the inspector being considered competent by license or experience to offer direction on how to affect a repair. If you have standing to design and perform the repair then you have a standing to offer the recommendation for the repair.
-
12-22-2013, 11:33 AM #15
Re: How to Repair a Notched Beam
-
12-23-2013, 10:18 AM #16
-
12-23-2013, 03:50 PM #17
Re: How to Repair a Notched Beam
Last edited by Jerry Peck; 12-23-2013 at 03:55 PM. Reason: added second part of post about trying to register as a student
-
12-24-2013, 06:21 AM #18
Re: How to Repair a Notched Beam
-
12-24-2013, 04:00 PM #19
Re: How to Repair a Notched Beam
Kevin,
That is the same link from last night - it starts off with "I am a..." and then gives an option to select "Non-Member (applying for membership)" or "InterNACHI Member (renewing membership)".
I am neither.
That is the problem. Maybe Nick can put up a "Guest" link? I promise to be a nice and tidy guest - I'll even vacuum my room and make the bed with clean linens when I leave.
-