    Just this week I received notice from an insurance company's legal firm that they are seeking a $103,000 reimbursement check from me for fire damage sustained from a lightning strike on a home I inspected 3 years ago.

    The lightning strike happened a year and half ago. The legal team went after the Ward company claiming defective csst. The Ward legal people pointed the finger at me because I failed to follow TREC sop "The inspector shall report as deficient appliances and metal pipes that are not bonded or grounded.' The one time I failed to mention this deficiency, is the one time lightning strikes that particular house. What are the odds.

    In the five years that I've been inspecting, only one time did I see the bonding cables on all metal piping and appliances in the attic.

    My insurance company is handling this. I'll keep you guys posted.

    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: I just got sued: Lightning strike and CSST

    Thanks for sharing

    I have a saying about how insurance companies make money:
    #1 By finding ways to raise your rates
    #2 Finding ways to deny a claim
    and #3 (This applies to you) By finding someone else to pay the claim.

    Keep us posted

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  3. #3
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: I just got sued: Lightning strike and CSST

    It's called Subrogation and has become more and more common in the world. I did not know that TX had CSST in their standards three years ago..... The problem with reporting on bonding is that the majority of the time you really can't verify the bond is or is nor present. Time for us all if you don't already have it, to add canned boilerplate verbiage about CSST, bonding, etc.... CYA!

    Glad you have E&O to help defer the legal cost.

    Last edited by Scott Patterson; 09-22-2013 at 06:21 AM.
    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  4. #4
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: I just got sued: Lightning strike and CSST

    I don't see a lot of CSST in the City but run into some of it in the burbs. Did a house out in the burbs about 6 months or so ago that had lots of CSST. Overall bad install. Having read some of the grounding, lightning strike issues, I did some research and included 3 or 4 PDF's about CSST issues with my report. I wrote up the CSST as hazardous due to the install methods.
    Buyer gave seller report, Seller said I was full of ----; then buyer sent seller the pdf's I had sent them, seller shut up and worked out a deal.
    On NC around here I often find a ground wire run to the gas meter. Unfortunately the wire is always just hanging in the air, not actually attached. I always write it up and developers instead of buying a bracket and having one of their grunts install it prefer to argue about whose responsibility it is to attach the wire.
    Sometimes it all just seems so stupid and useless to talk about it when fixing the problem would take less time.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  5. #5
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: I just got sued: Lightning strike and CSST

    Quote Originally Posted by Markus Keller View Post
    I did some research and included 3 or 4 PDF's about CSST issues with my report.
    Maecus,

    Could you post these PDFs or their links please?

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  6. #6
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: I just got sued: Lightning strike and CSST

    Hi Gunnar, the attached files are the PDF's I gave the client with their report.
    Hope they are helpful
    MarkusCSST_Product_Liability_Suit.pdfGastite_01.pdf

    The following is the title of another PDF I sent them but it doesn't seem to want to upload. I think its too big: Validation of Installation Methods for CSST Gas Piping to Mitigate Lightning Related Damage; put out byThe Fire Protection Research Foundation
    Y
    ou can probably find it and download

    When I do run into CSST I also send the client the 'Gastite design and installation guide PDF'. I've had too many DIY husbands comment about how easy it will be to add/modify gas piping for the barbeque grill etc. 'oh with this yellow stuff I can run more gas pipe pretty easy'.
    I have the 08 install manual, which I should probably find the new version. The interesting thing about it is that Page 2 talks about lightning safety. Not page 4, 27 or 99; The very next page after the cover page.
    Sorry I don't know whats going on with these font sizes, I didn't do it on purpose.



    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  7. #7
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: I just got sued: Lightning strike and CSST

    my boilerplate According to some authorities, CSST may be particularly susceptible to damage from lightning strikes. During electrical storms, the metallic systems and the building itself can become highly energized. Metal siding, gas piping, water piping, electrical wiring, communication and entertainment cables may be affected. Arcing from one metallic path or conductor to another can take place, resulting in physical damage. (Arcing is electrical energy jumping through air from one conductor to another or from a conductor to ground, typically accompanied by considerable heat, light and sound. Arcing occurs only where there is a significant difference in potential energy between two materials.)

    This is especially dangerous with CSST because of the gas inside. There are several cases of CSST leaks related to electrical storms. At least one class action lawsuit has been brought against manufacturers as a result of this. See Csstsettlement.com.


    In response to this issue, installation manuals now have a special electrical bonding and grounding procedure for their CSST systems that may help prevent electricity from jumping (arcing) between metallic systems. Some jurisdictions require the CSST be kept away from other metallic systems such as metal ducts, vents and other pipes to reduce the chance of arcing.

    Special bonding requirements for CSST (not copper tubing) typically include the following:


    • The tubing itself should be electrically continuous and should be directly bonded to a reliable ground-fault current path.
    • There should be a minimum 6 AWG (American Wire Gauge) bonding jumper connected to the electrical service grounding system for the building.
    • The bond connection to the gas tubing should be accessible and just downstream of the meter, near the service entrance into the house.
    • The bond connection should be upstream of any CSST. Listed bonding/grounding clamps (UL 467) should be used, and connections should be made to a brass fitting, steel manifold or unpainted black iron pipe, not to the CSST itself.


    - - - Updated - - -

    Also CSST(corrugated stainless steel tubing), is being used as a gas supply line in this home.
    We recommend installation of Excess Flow Valves in the event of a gas line breach that would shut down the gas flow.
    Please click on link for more information on excess flow valves.
    http://www.tracpipe.com/CSST_Gas_Pipe_Products/AutoTrip_EFV_Automatic_Gas_Shut_Off_Valve/


  8. #8
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: I just got sued: Lightning strike and CSST

    I almost never actually see a ground of any kind to the csst. The ground wire talked about wrapped around the gas pipe coming out of the ground??? Not a ground!

    On older homes I always state that a ground rod should be incorporated to the grounding system as know one ever knows if PEX or PVC was added to the plumbing lines which will cancel a good ground anyway with the water lines. As far as CSST I always state that I have no idea how well the csst is grounded as I cannot see the full length of all pipe and they should have the system checked. If I just flat out do not see a ground I recommend the same thing.

    A few years ago I got a call to cancell an inspection. The reason? The home was hit by lightening and they confirmed there was not a solid ground for the the homes electric system. The home burnt to the ground.

    I never shy away at making the call to have the grounding system for any system in the home confirmed.

    Sorry to hear about getting sued.

    What if they did not have a home inspection? Would they have gone after the plumber? Electrician? You are not the one that did not ground the system! Hell. In most cases you would have never seen the ground or how good it was.


  9. #9
    Join Date
    Mar 2012
    Location
    Lansdale, PA
    Posts
    876

    Default Re: I just got sued: Lightning strike and CSST

    Quote Originally Posted by Ted Menelly View Post
    I almost never actually see a ground of any kind to the csst. The ground wire talked about wrapped around the gas pipe coming out of the ground??? Not a ground!

    On older homes I always state that a ground rod should be incorporated to the grounding system as know one ever knows if PEX or PVC was added to the plumbing lines which will cancel a good ground anyway with the water lines. As far as CSST I always state that I have no idea how well the csst is grounded as I cannot see the full length of all pipe and they should have the system checked. If I just flat out do not see a ground I recommend the same thing.

    A few years ago I got a call to cancell an inspection. The reason? The home was hit by lightening and they confirmed there was not a solid ground for the the homes electric system. The home burnt to the ground.

    I never shy away at making the call to have the grounding system for any system in the home confirmed.

    Sorry to hear about getting sued.

    What if they did not have a home inspection? Would they have gone after the plumber? Electrician? You are not the one that did not ground the system! Hell. In most cases you would have never seen the ground or how good it was.
    There are now clear requirements on how CSST should be grounded. The grounding should be as close as possible to where the gas piping enters the house (that is my wording, not an exact quote). I suggest that instead of telling your clients you have not idea how it is grounded you should learn how it should be grounded.


  10. #10
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: I just got sued: Lightning strike and CSST

    Quote Originally Posted by Mark Reinmiller View Post
    There are now clear requirements on how CSST should be grounded. The grounding should be as close as possible to where the gas piping enters the house (that is my wording, not an exact quote). I suggest that instead of telling your clients you have not idea how it is grounded you should learn how it should be grounded.
    And I think you should think before giving uneeded advise like "you should learn how it should be grounded". I just happen to know how it is suppose to be grounded. Do you? I did not say I did not know how it is suppose to be grounded. I said I said I have no idea if it is or if its a good ground. Of course unless I can see that it appears to be a good ground.


  11. #11
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: I just got sued: Lightning strike and CSST

    Quote Originally Posted by Markus Keller View Post
    On NC around here I often find a ground wire run to the gas meter. Unfortunately the wire is always just hanging in the air, not actually attached. I always write it up and developers instead of buying a bracket and having one of their grunts install it prefer to argue about whose responsibility it is to attach the wire.
    Sometimes it all just seems so stupid and useless to talk about it when fixing the problem would take less time.
    That wire is used to trace the underground pipe by the utility if they have to. It isn't meant to have any other purpose or ground anything.

    If you choose not to decide, you still have made a choice.

  12. #12
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: I just got sued: Lightning strike and CSST

    I'll be a little picky here. Piping is not grounded. Piping is bonded to a ground. Subtle difference and in the grand scheme of life, won't change anyone's life.

    As for being sued, we are in a business where we are expected to be perfect at every inspection. That's a high hurdle to get over every day of every week of every year. Finding bonding can be difficult. I think having a boiler plate disclosure is appropriate and might even mitigate or derail a suit...... occasionally.

    If you choose not to decide, you still have made a choice.

  13. #13
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: I just got sued: Lightning strike and CSST

    Quote Originally Posted by Lon Henderson View Post
    I'll be a little picky here. Piping is not grounded. Piping is bonded to a ground. Subtle difference and in the grand scheme of life, won't change anyone's life.

    As for being sued, we are in a business where we are expected to be perfect at every inspection. That's a high hurdle to get over every day of every week of every year. Finding bonding can be difficult. I think having a boiler plate disclosure is appropriate and might even mitigate or derail a suit...... occasionally.
    Yes, bonding. Yes trace wire wrapped around the pipe in the ground.

    Thank ya. Thank ya very much.


  14. #14
    Join Date
    Mar 2007
    Location
    Alton Bay NH
    Posts
    49

    Default Re: I just got sued: Lightning strike and CSST

    Here's a good link about CSST bonding. I see it a lot in my area and only once did I find the bonding wire and that was because is was a gas company install.


    CSST Safety Solution


  15. #15
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: I just got sued: Lightning strike and CSST

    http://www.grefesidney.com/documents...A531161169.pdf


    1. CSST gas line is extremely thin, with walls typically around 0.008" in thickness. Blackiron gas pipe is typically 0.12" in thickness. Put another way, the walls of black iron pipe are 15times thicker than the walls of CSST tubing. When this is considered, perhaps it is notsurprising that the amount of electrical energy needed to defeat traditional black iron pipe isabout 15 times more than the energy needed to defeat the much thinner walls of CSST tubing.


      When electrical energy from lightning is conducted through CSST tubing, electricalarcing can be created between the CSST and any grounded metallic object, as the lightningenergy seeks a ground source. This arcing can instantaneously burn a small hole, ranging fromthe size of a pin-head to a pencil eraser, right through the very thin wall of the CSST. The arcingevent can easily ignite the escaping gas being carried by the CSST, which can then serve as ablow-torch with an endless gas fuel source more than sufficient to ignite nearly any type ofstructure.


      Lightning strikes the United States more than 25 million times each year and accordingto Underwriters Laboratories (UL), lightning accounts for more than $1 billion in annualstructural damage. A single bolt of lightning can carry over 100 million volts of electricity, andin reality, there are no construction methods or safety measures that can completely protect a



    structure from a direct lightning strike. CSST gas pipe, however, is susceptible to damage fromnon-direct lightning strikes as well, even strikes which may be recorded a significant distanceaway from the structure. “Lightning does not have to strike a building directly in order for theCSST to be affected,” explains Guy Maxwell, president of the Lightning Safety Alliance. “Thereports of CSST related fires that I have seen have involved strikes that were near the structure.”


    CSST was originally developed in the late 1980s, but most CSST product has beeninstalled since 2003. Any building that has had natural gas piping work done since 1990 couldhave CSST installed. According to the National Fire Protection Association (NFPA), no tests onthe effects of lightning on CSST were conducted prior to its approval for use. One CSSTmanufacturer has acknowledged that the installation of a lightning protection system addressesthe lightning hazard associated with CSST, yet homes with CSST are rarely equipped withlightning protection systems.


  16. #16
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: I just got sued: Lightning strike and CSST

    To add fuel to this fire( little pun...).... Let's not forget about the CSST that is covered with the black plastic sheathing. It is designed to not be bonded unless the AHJ just wants it done.....

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  17. #17
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: I just got sued: Lightning strike and CSST

    Scott

    Never seen black sheathing, only yellow, at least up here.


  18. #18
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: I just got sued: Lightning strike and CSST

    Quote Originally Posted by Scott Patterson View Post
    To add fuel to this fire( little pun...).... Let's not forget about the CSST that is covered with the black plastic sheathing. It is designed to not be bonded unless the AHJ just wants it done.....
    Its erroneous statements like that (Red colored, bolded & underlined statement by SP, above) that gets HI's & HO's in trouble.

    It (only the latest generation black-jacketed SS Tube, the earlier black counterstrike omegaflex still requires special) is still required to be bonded, the manufacturer instructions just don't require ADDITIONAL bonding steps to counteract the inherent deficiency in thin-walled yellow-jacketed SS tube and the earlier version(s) of black jacketed counterstrike, IF the black jacket is intact and the product is overall installed properly, the tubing system IS bonded as per NFPA 70 (national electric code unammended) and NFPA 54 (national fuel gas code unammended) AND a lightning arrestor system is properly designed and installed.

    Lets get it right.

    For RW, supplying the CSA info at the end of the following snippets quoted from the link provided at the end.

    There are no additional bonding requirements for TracPipe® CounterStrike® imposed by the manufacturer's installation instructions. With TracPipe® CounterStrike®'s improved properties, TracPipe® CounterStrike® is to be bonded in accordance with current requirements of the National Electrical Code (NFPA 70), and the National Fuel Gas Code (NFPA 54), and with any local requirements that may be in excess of the national codes. This may result in the avoidance of additional bonding costs which are required for conventional CSST.
    TracPipe® CounterStrike® is listed by CSA to ANSI LC 1. TracPipe® CounterStrike® meets building code requirements (ASTM E84) with respect to flame spread and smoke density...
    Link:

    Corrugated Stainless Steel Tubing - Lightning Protected Gas Pipe


  19. #19
    Frank Adame's Avatar
    Frank Adame Guest

    Default Re: I just got sued: Lightning strike and CSST

    My E&O underwriters just informed me they will no longer insure me. Surprised?


  20. #20
    Join Date
    Dec 2008
    Location
    Maryland
    Posts
    2,809

    Default Re: I just got sued: Lightning strike and CSST

    , but expected. The worst thing that an agent can have is a claim paid out.


  21. #21
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: I just got sued: Lightning strike and CSST

    Quote Originally Posted by Frank Adame View Post
    My E&O underwriters just informed me they will no longer insure me. Surprised?
    Thanks for the update

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  22. #22
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: I just got sued: Lightning strike and CSST

    Please update us on if you have any problems getting re-insured.

    A friend of mine just wrapped up a lawsuit where his insurance settled for a few bucks over his deductible and immediately jacked his rate up. BUT, the amazing thing is that the mediator asked the insurance attorney why he was settling when the plaintiff didn't have any case at all.

    It was cheaper for the company than any further litigation and winning didn't matter to them. Only what it cost them was what mattered. To hell with what it cost the inspector. Of course, the inspector could have continued the fight on his own but that would have been even more costly, even if he won.

    If you choose not to decide, you still have made a choice.

  23. #23
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: I just got sued: Lightning strike and CSST

    Quote Originally Posted by Frank Adame View Post
    My E&O underwriters just informed me they will no longer insure me. Surprised?
    Who did you have your E&O with? Always good to know who should be avoided!

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  24. #24
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: I just got sued: Lightning strike and CSST

    Don't forget to sue the agent to share in the damages you paid (get half your money back).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  25. #25
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: I just got sued: Lightning strike and CSST

    Dumb question and I do know the answer but if someone did not bond some piping or any type of bond or ground fir the systems in the home why would they not go after just the installer of that gas pipe or the installer of the system. Why would they keep going in circles to get a home inspector.

    Example

    Someone does some bad wiring in a home and a section that started a fire happened to have the insulation pushed back away from it but was done by someone else hooking some other circuit into the line after the home inspection....they are going after a home inspector?

    Example (three years is a long time)

    He did not mention it. Does that mean there was never a bond. If never a bond go after the installer. If there was a bond and it was a poor bond or someone changed something and removed the bond???? I guess that is the inspectors fault as well? Obviously if the original installer never bonded it and should have why is the inspector singled out. Mentioned it or not there was never a bond...go after the installer. yeah yeah, he did not go by SOPs! There was still never a bond.

    Just freaking criminal.


  26. #26
    Join Date
    Mar 2012
    Location
    Lansdale, PA
    Posts
    876

    Default Re: I just got sued: Lightning strike and CSST

    Quote Originally Posted by Ted Menelly View Post
    Dumb question and I do know the answer but if someone did not bond some piping or any type of bond or ground fir the systems in the home why would they not go after just the installer of that gas pipe or the installer of the system. Why would they keep going in circles to get a home inspector.

    Example

    Someone does some bad wiring in a home and a section that started a fire happened to have the insulation pushed back away from it but was done by someone else hooking some other circuit into the line after the home inspection....they are going after a home inspector?

    Example (three years is a long time)

    He did not mention it. Does that mean there was never a bond. If never a bond go after the installer. If there was a bond and it was a poor bond or someone changed something and removed the bond???? I guess that is the inspectors fault as well? Obviously if the original installer never bonded it and should have why is the inspector singled out. Mentioned it or not there was never a bond...go after the installer. yeah yeah, he did not go by SOPs! There was still never a bond.

    Just freaking criminal.
    Typical practice for attorneys is to sue everybody who was in any way involved. Most cases settle without going to court. Each company or insurance company often figures it is cheaper or there is less risk to settling than fighting. It is not fair, but attorneys make the laws.


  27. #27
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: I just got sued: Lightning strike and CSST

    Keep in mind that the date of the installation and the bonding requirements at that time take precedence ... while not forgetting what has been learned about the necessity for bonding since that time.

    Regardless of bonding the CSST, the CSST can be damaged by a lightning strike, not sure that the additional bonding would prevent that damage - that is up to people much smarter than me (much higher pay grade too ).

    The CSST *is* bonded - the CSST is bonded through the electrical/gas equipment it is connected to.

    The key is the "additional" bond required *by current manufacturer's installation instructions" - keep in mind that we are referring to the regular 'yellow' outer jacketed CSST, not the newer 'strike resistant' CSST with the newer outer jacket which is supposed to help dissipate the energy from the strike.

    The reason they go after the home inspector is that they go after "everyone" - like throwing spaghetti against the wall and seeing what sticks. Using that California case, the home inspector may be able to bring the real estate agent and the seller in to get part of their money back, even bringing in the builder, the contractor who installed it, etc. ... again, the practice of 'shotgunning' everyone to see what sticks to whom.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  28. #28
    Join Date
    Oct 2011
    Location
    smyrna ga
    Posts
    21

    Cool Re: I just got sued: Lightning strike and CSST

    [QUOTE=Frank Adame;I received notice from an insurance company's legal firm that they are seeking a $103,000 reimbursement check from me for fire damage sustained from a lightning strike on a home I inspected 3 years ago.

    Here is a case that might ease your mind. CCST not necessarily lightning p-roof even if grounded.

    [url=http://www.structuretech1.com/2010/11/alert-jury-rules-that-csst-is-a-defective-product-in-landmark-case/]ALERT: Jury Rules That CSST Is A Defective Product In Landmark Case | Structure Tech Home Inspections[/url]

    Tks for post. gonna check my rentals for grounded meter - CSST or not.


  29. #29
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: I just got sued: Lightning strike and CSST

    [QUOTE=james hiatt;235604]
    Quote Originally Posted by Frank Adame;I received notice from an insurance company's legal firm that they are seeking a $103,000 reimbursement check from me for fire damage sustained from a lightning strike on a home I inspected 3 years ago.

    Here is a case that might ease your mind. CCST not necessarily lightning p-roof even if grounded.

    [url=http://www.structuretech1.com/2010/11/alert-jury-rules-that-csst-is-a-defective-product-in-landmark-case/
    ALERT: Jury Rules That CSST Is A Defective Product In Landmark Case | Structure Tech Home Inspections[/url]

    Tks for post. gonna check my rentals for grounded meter - CSST or not.
    That makes a lot of sense to me as well

    Dale Griffis
    January 4, 2012, 10:42 pm
    Actually, the biggest problem with standard CSST is the bond. I’ll explain. All gas piping must be bonded with a dedicated copper ground to the ground buss in the electrical panel box. The problem arises when the communications guys cross the CSST with their low voltage wiring. When the lightning strikes, it actually strikes the communication lines ( which aren’t bonded ) and arcs to the thin CSST, sometimes in several places, which subsequently burns small holes in the CSST and ignites the gas that is now escaping at the same time. I have installed miles of Stainless gas lines and have done my fair share of repairing after the fires. Every time without exception it has been the communication lines that caused the problem. I find CSST to be a good product, there just needs to be care exercised when installing low voltage near it.


  30. #30
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: I just got sued: Lightning strike and CSST

    Quote Originally Posted by Ted Menelly View Post
    All gas piping must be bonded with a dedicated copper ground to the ground buss in the electrical panel box.
    While that is what the article said, the installation instructions which I recall having seen all specify for the bond to be 'in accordance with NEC/NFPA 70', and that states: (bold and underlining are mine)
    - (B) Other Metal Piping. Where installed in or attached to a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with 250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.

    Note that it is not to "electrical panel box", it is to the service equipment or grounding electrode system.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  31. #31
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: I just got sued: Lightning strike and CSST

    Quote Originally Posted by Ted Menelly View Post
    Dumb question and I do know the answer but if someone did not bond some piping or any type of bond or ground fir the systems in the home why would they not go after just the installer of that gas pipe or the installer of the system. Why would they keep going in circles to get a home inspector.

    Example

    Someone does some bad wiring in a home and a section that started a fire happened to have the insulation pushed back away from it but was done by someone else hooking some other circuit into the line after the home inspection....they are going after a home inspector?

    Example (three years is a long time)

    He did not mention it. Does that mean there was never a bond. If never a bond go after the installer. If there was a bond and it was a poor bond or someone changed something and removed the bond???? I guess that is the inspectors fault as well? Obviously if the original installer never bonded it and should have why is the inspector singled out. Mentioned it or not there was never a bond...go after the installer. yeah yeah, he did not go by SOPs! There was still never a bond.

    Just freaking criminal.
    The reason the insurance company comes after the inspector is because in Texas we have insurance which paints a big target on our back. Good luck finding the installer or even the builder. We have become the low hanging fruit on the subrogation (sp?) plan of insurance companies.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  32. #32
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: I just got sued: Lightning strike and CSST

    Quote Originally Posted by Jerry Peck View Post
    While that is what the article said, the installation instructions which I recall having seen all specify for the bond to be 'in accordance with NEC/NFPA 70', and that states: (bold and underlining are mine)
    - (B) Other Metal Piping. Where installed in or attached to a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with 250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.

    Note that it is not to "electrical panel box", it is to the service equipment or grounding electrode system.
    I was speaking of the low voltage wires or any wires for that matter that are lying across the CSST. But thanks for the other info anyway.


  33. #33
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: I just got sued: Lightning strike and CSST

    Quote Originally Posted by Ted Menelly View Post
    I was speaking of the low voltage wires or any wires for that matter that are lying across the CSST. But thanks for the other info anyway.
    Yes, it is a good idea to keep all conductors away from CSST, however, if there is a lightning strike not having any conductors near the CSST is not going to protect the CSST as the lightning strike will go everywhere and hit anything it can trying to find a path to ground. Do you remember those photos I posted years ago of a lightning strike which splintered a truss and exploded NM cable on it way to ground?

    - - - Updated - - -

    Quote Originally Posted by Ted Menelly View Post
    I was speaking of the low voltage wires or any wires for that matter that are lying across the CSST. But thanks for the other info anyway.
    Yes, it is a good idea to keep all conductors away from CSST, however, if there is a lightning strike not having any conductors near the CSST is not going to protect the CSST as the lightning strike will go everywhere and hit anything it can trying to find a path to ground. Do you remember those photos I posted years ago of a lightning strike which splintered a truss and exploded NM cable on it way to ground?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  34. #34
    Join Date
    Jun 2008
    Location
    Maryland
    Posts
    1,097

    Default Re: I just got sued: Lightning strike and CSST

    Here's my boiler on CSST bonding.

    This house has CSST gas piping. All CSST gas piping manufacturers require that their product be bonded to the house electrical grounding system. The bonding is intended to prevent damage to the CSST that could happen from lightning strikes. Of all the visible portions of CSST in this house, I did not see any of it bonded. Have a qualified electrician bond this CSST to meet the installation requirements of its manufacturer. The following link is to a document with the manufacturers bonding instructions.

    I then leave in the applicable link depending what brand is present, and cut out the other two.


    http://www.wardflex.com/images/Techn...tin_WF2008.pdf

    http://www.ci.faribault.mn.us/assets...ipebonding.pdf

    http://www.gastite.com/include/langu.../TB2010-01.pdf


  35. #35
    Join Date
    Aug 2008
    Location
    Atlanta, GA
    Posts
    163

    Default Re: I just got sued: Lightning strike and CSST

    Quote Originally Posted by John Dirks Jr View Post
    Here's my boiler on CSST bonding.

    This house has CSST gas piping. All CSST gas piping manufacturers require that their product be bonded to the house electrical grounding system. The bonding is intended to prevent damage to the CSST that could happen from lightning strikes. Of all the visible portions of CSST in this house, I did not see any of it bonded. Have a qualified electrician bond this CSST to meet the installation requirements of its manufacturer. The following link is to a document with the manufacturers bonding instructions.

    I then leave in the applicable link depending what brand is present, and cut out the other two.


    http://www.wardflex.com/images/Techn...tin_WF2008.pdf

    http://www.ci.faribault.mn.us/assets...ipebonding.pdf

    http://www.gastite.com/include/langu.../TB2010-01.pdf
    Excellent John!

    Just out of curiosity, do you include the comment in the Electrical portion of your report or the Gas Piping / Plumbing section of your report?

    - - - Updated - - -

    Quote Originally Posted by John Dirks Jr View Post
    Here's my boiler on CSST bonding.

    This house has CSST gas piping. All CSST gas piping manufacturers require that their product be bonded to the house electrical grounding system. The bonding is intended to prevent damage to the CSST that could happen from lightning strikes. Of all the visible portions of CSST in this house, I did not see any of it bonded. Have a qualified electrician bond this CSST to meet the installation requirements of its manufacturer. The following link is to a document with the manufacturers bonding instructions.

    I then leave in the applicable link depending what brand is present, and cut out the other two.


    http://www.wardflex.com/images/Techn...tin_WF2008.pdf

    http://www.ci.faribault.mn.us/assets...ipebonding.pdf

    http://www.gastite.com/include/langu.../TB2010-01.pdf
    Excellent John!

    Just out of curiosity, do you include the comment in the Electrical portion of your report or the Gas Piping / Plumbing section of your report?


  36. #36
    Join Date
    Jun 2008
    Location
    Maryland
    Posts
    1,097

    Default Re: I just got sued: Lightning strike and CSST

    Hank,

    I put the comments about bonding CSST into the electrical section of the report.

    Other types of CSST problems like lack of proper protection (strike plates) and incorrect routing or supporting go into the plumbing section of the report.


  37. #37
    Join Date
    Mar 2007
    Location
    S.W. Missouri
    Posts
    75

    Default Re: I just got sued: Lightning strike and CSST

    Alpha Home Inspections
    417- 334-7047


  38. #38
    Join Date
    Apr 2014
    Location
    FL, TX
    Posts
    146

    Default Re: I just got sued: Lightning strike and CSST

    [QUOTE= My insurance company is handling this. I'll keep you guys posted.[/QUOTE]


    Never let your insurance company handle something like this all by itself. Hire your own attorney at least to review the facts and give an opinion regarding culpability in writing and to your insurance. Also that atty should review any information available from existing cases regarding percentage liability….. The insurance will tell you that IF they are to insure you that they MUST handle your defense etc. However your atty can let them know that if they ignore YOUR legal rights (and his legal opinions) that they legally will not be able to use the settlement against you in future rates or to terminate your insurance. In other words you can make it very hard for the ins to play games with you instead of the plaintiff.

    Remember, you did not obtain the permit, do the work and illegaly install the system and you did not cause the lightening strike. Therefore your culpability is severely reduced. Now, if the bonded ground was visible and had been damaged (broken by a weed wacker lets say) and you missed it then you have much more liability.

    The issue is that Insurance companies are NOT THERE FOR YOUR BENEFIT, they are there to minimize thier own losses and make money. Thier interests are NOT your interests and never will be.

    Spend the few hundred and do some research on your own as well to assure that COURT CASES that exist uphold the suit against you or not and to what percentage of total liability. Remember YOU are the one being sued, not your insurance! You have rights of defense. The ins company will try and tell you that if thier attys dont handle it then you are not insured. I doubt that will hold up in a court in any state. The action is against you. They must look after YOUR interests in the actions as well as limiting liability.


  39. #39
    Join Date
    Jun 2008
    Location
    Delmar NY
    Posts
    157

    Default Re: I just got sued: Lightning strike and CSST

    Quote Originally Posted by Scott Patterson View Post
    To add fuel to this fire( little pun...).... Let's not forget about the CSST that is covered with the black plastic sheathing. It is designed to not be bonded unless the AHJ just wants it done.....
    In NY (at least in my area) it is still required to be bonded (additional bonding), just like the yellow jacketed csst.

    - - - Updated - - -

    Quote Originally Posted by Scott Patterson View Post
    To add fuel to this fire( little pun...).... Let's not forget about the CSST that is covered with the black plastic sheathing. It is designed to not be bonded unless the AHJ just wants it done.....
    In NY (at least in my area) it is still required to be bonded (additional bonding), just like the yellow jacketed csst.


  40. #40
    Frank Adame's Avatar
    Frank Adame Guest

    Default Re: I just got sued: Lightning strike and CSST

    Two weeks ago I talked to the head building official for Wichita Kansas. He said additional csst bonding is not required there because the metallic tubing material is a better bonding conductor than a #6 bonding wire. I'm not making this up!


  41. #41
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: I just got sued: Lightning strike and CSST

    Quote Originally Posted by Frank Adame View Post
    Two weeks ago I talked to the head building official for Wichita Kansas. He said additional csst bonding is not required there because the metallic tubing material is a better bonding conductor than a #6 bonding wire. I'm not making this up!
    CSST is just an accident waiting to happen! Bonded or not the thin wall CSST is just no match for a lighting strike, it's going to punch a hole in it. With Lubbock TX outlawing its use, my bet is that this will expand through other TX towns and parts of the country. You just can't beat "black" pipe for gas distribution in a home.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  42. #42
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: I just got sued: Lightning strike and CSST

    you should all be recommending Excess flow valve installation even where the system is bonded.
    Code is minimum, we are trying to save lives.


  43. #43
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: I just got sued: Lightning strike and CSST

    Quote Originally Posted by wayne soper View Post
    you should all be recommending Excess flow valve installation even where the system is bonded.
    Code is minimum, we are trying to save lives.
    CSST is a good example of what I frequently say: Code is the most unsafe, the least safe, one is legally allowed to do.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  44. #44
    Join Date
    Dec 2012
    Location
    Texas
    Posts
    4

    Default Re: I just got sued: Lightning strike and CSST

    Sept 2015......any update on this case?

    Thanks

    John B.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •