Results 1 to 13 of 13
-
03-02-2014, 02:47 PM #1
Revisiting horizontal fill on guard rails - testing by the "4/50 guideline."
Looked at another million+$ house yesterday as a "new house inspection," the entire structure has been passed by the AHJ as acceptable to code. As usual these days, all decks, stairs, balconies, etc. used horizontal cable infill. While at it I set up the recommended test (see photo). I am using a 4 inch rigid plastic ball and applying a force to it with the tape and scale. (The scale measures to 75lbs. force (note "lbs. force", not "pressure", maximum and gives a good reading at 50lbs, near mid-range) Obviously no AHJ checked this. The cables were 1/8 inch on 3.5 inch centers and the ball fell through the cables with no force at all. I guess most jurisdictions now are just ignoring this as not worth the fight. I am not sure what to tell owners and buyers in these situations, I don't want to get in the habit of poking local code enforcement agencies in the eye with a sharp stick. Something about hibernating bears?
Last edited by Allen Ingling; 03-02-2014 at 03:00 PM. Reason: clarify test procedure
-
03-02-2014, 08:37 PM #2
Re: Revisiting horizontal fill on guard rails - testing by the "4/50 guideline."
Allen, I think you should just tell them what you found and what the rule is. They can decide for themselves along with their realtor if they want to take it up with the builder.
The builder will most likely do nothing about it, but that is not your fight.
There is no denying the information in your report, tho.
They are pretty ugly railings, IMO.
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
-
03-03-2014, 06:55 AM #3
Re: Revisiting horizontal fill on guard rails - testing by the "4/50 guideline."
Agree with John.
But out of curiosity, how many of you guys do this "test" as Allen does?
If you choose not to decide, you still have made a choice.
-
03-03-2014, 07:08 AM #4
Re: Revisiting horizontal fill on guard rails - testing by the "4/50 guideline."
Horizontal cables like that also act like a ladder allowing adults and children to climb it. That is worse than the spacing issue, IMVHO.
The 4" sphere is used by many inspectors(not me) but I have never seen anyone using a force gauge.
Last edited by Scott Patterson; 03-03-2014 at 07:14 AM.
-
03-03-2014, 09:09 AM #5
Re: Revisiting horizontal fill on guard rails - testing by the "4/50 guideline."
Jim,
You keep saying that.
How many code change proposals have you submitted?
The code is a consensus MINIMUM level of safety. The code is not and does not attempt to address things to a higher standard. I am glad that YOU like higher standards, just as I do. ... However, you seem to fail to recognize that the code is a MINIMUM standard.
-
03-03-2014, 09:54 AM #6
Re: Revisiting horizontal fill on guard rails - testing by the "4/50 guideline."
It wasn't prohibited for many years in the various code agencies which produced the various codes.
When the ICC was formed, the various code agencies combined the various codes into the ICC codes by consensus. In doing so some things in the individual codes were dropped.
I agree that - in my opinion - horizontal infill should be prohibited, but it is not.
-
03-03-2014, 10:19 AM #7
Re: Revisiting horizontal fill on guard rails - testing by the "4/50 guideline."
-
03-03-2014, 06:12 PM #8
Re: Revisiting horizontal fill on guard rails - testing by the "4/50 guideline."
-
03-04-2014, 01:12 AM #9
Re: Revisiting horizontal fill on guard rails - testing by the "4/50 guideline."
-
03-06-2014, 01:09 PM #10
Re: Revisiting horizontal fill on guard rails - testing by the "4/50 guideline."
Obviously no one is concerned (except some of us) about the ladder effect. But the spacing I believe is a much greater choking risk for toddlers and younger who are not big enough to try climbing it but will definitely try to stick their little (4", pinheads?) heads through it. That is what the four inch spacing on any sort of guard is about anyway. I have yet to see one of these close up that I think would not be a choking risk way beyond the "ladder risk."
- - - Updated - - -
Steven: You must be one big guy! My fist is only about three inches wide (and lacks a built in force gauge).
-
03-06-2014, 01:26 PM #11
Revisiting horizontal fill on guard rails - testing by the "4/50 guideline."
I'm not a big guy either and I use my first too. It's just shy 4", if I can move my fist side to side much at all in the opening, I measure the opening.
While my fist does not have a force gage either, if I can put my fingers in the opening and spread the infill apart, be it cable or 1/2" square tube over spanned for its strength, and I know that I do not have even 20 pounds of force in spreading my fingers - probably not even 5 or 10 pounds of force, I know that the infill will not meet the requirements of 50 pounds/sq ft.
-
03-06-2014, 01:45 PM #12
Re: Revisiting horizontal fill on guard rails - testing by the "4/50 guideline."
John: You ain't seen ugly until you look at this! These cables are on 4" centers. In places the ball goes through without touching. You would think that this was someone's mountain hideaway but it is actually my alma mater's demo house. I am embarrassed to say where it is. "Demo" in this case should mean demolition, not demonstration. I particularly like the added "spacers."
-
03-07-2014, 06:45 AM #13
Re: Revisiting horizontal fill on guard rails - testing by the "4/50 guideline."
Bookmarks