    I'd like your thoughts on why this efflorescence is occurring.

    New home with no weepholes over and under the windows.

    I've already got some info from the Brick Industry Associaton but wanted to run it past others.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral
    Erby Crofutt, Georgetown, KY - Read my Blog here: Erby the Central Kentucky Home Inspector B4 U Close Home Inspections www.b4uclose.com www.kentuckyradon.com
    Find on Facebook at: https://www.facebook.com/B4UCloseInspections

  2. #2
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: Effloresence on brick veneer

    My first thought is that the windows are allowing water to seep in the wall. Any moisture on the interior drywall?

    Any idea of what type of vapor barrier was used?

    Look under the front porch, it has some efflorescence as well. Maybe the wrong type of mortar mix.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  3. #3
    Join Date
    Mar 2007
    Location
    Lake Barrington, IL
    Posts
    1,367

    Default Re: Effloresence on brick veneer

    With new construction efflorescence is quite common. But after the first year its occurrence should stop - if water is not getting in the brick. Certainly the windows are suspect but I also see efflorescence under the front porch. Was/is there a way to get to the framing in the basement under the windows to see if there is elevated moisture?

    I often find poorly pitched sills at windows, lack of caulking and sometimes just lousy windows.

    Eric Barker, ACI
    Lake Barrington, IL

  4. #4
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Effloresence on brick veneer

    New brick, dark color and it will be more pronounced when it gets wet.
    In short, It happens.
    Jim

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  5. #5
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: Effloresence on brick veneer

    Erby, I would be suspicious about how they flashed under the brick sill on those windows. Hard to tell at this stage without cutting so the comment would be that if the efflo continues to occur there may be a flashing problem.
    It is a slim chance that a bad mix was made just under three window areas and the porch, and the porch is covered with concrete so water draining off the top would be carrying minerals with it also.
    A thermography inspection after a rain storm would give some info also.


  6. #6
    Richard Rushing's Avatar
    Richard Rushing Guest

    Default Re: Effloresence on brick veneer

    I agree with Wayne and Scott-- I would be suspicious of the window flashings.

    By the way... that middle dormer would make some kid an excellent skateboard ramp to land on the sidewalk!!

    RR


  7. #7
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Effloresence on brick veneer

    I agree that the flashing detail on the window might be a problem, but the moisture does not have to get behind the brick to cause the problem. Brick and mortar are very porous and will absorb water through the surface and then leave deposits as the water evaporates.
    Any window with or without flashing will increase the amount of water on the brick below since the glass does not absorb any water but just sheds the water it receives to the brick below.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  8. #8
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: Effloresence on brick veneer

    The flashing would be suspect for sure. But if you look at the brick above the top windows toward the rake of the roof, the effloursence is present there also and in other various areas.

    I'm leaning maybe towards a bad batch of mortar.

    Last edited by Rick Hurst; 04-17-2007 at 03:35 PM.

  9. #9
    David Banks's Avatar
    David Banks Guest

    Default Re: Effloresence on brick veneer

    And under the front porch.


  10. #10
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Effloresence on brick veneer

    Certain colors of brick are subject to efflorescence. Mortar would not bleed into the brick in my experience. It is just the salts and minerals being washed out of the brick due to moisture.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  11. #11
    Join Date
    Mar 2007
    Location
    Fuquay Varina, NC
    Posts
    1,074

    Post Re: Effloresence on brick veneer

    In our area the only place the windows have to be flashed is above them. There not required at the row lock/ soldier course under them. BIA recommends it but it's not enforced here. Even the row lock under the window only has to be pitched 4 degrees. Only one builder I know installs them at 15 degrees. I bet the brick row under the windows are about level which will collect and absorb water and cause the efflorescence.

    So it may be a combination of above and bad mortar mix.

    Mike Schulz License 393
    Affordable Home Inspections
    www.houseinspections.com

  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Effloresence on brick veneer

    Add me to those who suspect the through-wall flashing below the window was either not installed, or not installed "properly".

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  13. #13
    Join Date
    Mar 2007
    Location
    Georgetown, KY
    Posts
    538

    Default Re: Effloresence on brick veneer

    Thank y'all for your thoughts & sharing. Though I didn't have time, until now, to get back on here and review them, I do appreciate the sharing.

    Report Comment:
    =============================
    (1) Weep holes are usually installed over and under doors and windows along with the base of the walls to allow water to get out of the wall. Proper weep holes are not present in the brick veneer. Flashing is supposed to be installed behind the brick to direct water to the weep holes. I can't tell if flashing has been installed in the required areas behind the brick veneer.

    Even though some local jurisdictions require it, I seldom see proper weep holes in brick veneer in recent construction in this area. For more information on brick systems on the internet see: http://www.bia.org/html/frmset_thnt.htm Look at Technical Note #7 for weephole information.

    Also see attachment "Weep Holes In Brick Veneer". Click the link on page three of the report.


    (2) Water does get behind brick veneer. It needs a way out so it doesn't sit in the wall rotting the structural wood until it evaporates.
    Weep holes are openings in the brick mortar that provide drainage for water that has penetrated into the space between the brick and the wall sheathing. When installed, these are combined with flashing (a piece of sheet metal or other similar water resistant material) between the sheathing and bricks which lead the collected moisture out the weep holes.

    There is no way to see into this space behind the brick without removing brick or opening the interior wall. Making a determination about moisture issues inside the wall is beyond the scope of this inspection.

    The Brick Industry Association (the people who make the brick and design installation requirements for it) recommend "weep holes should be located above all doors and windows, below all window sills, and above the ground at the base of the wall."

    Generally accepted nationwide building practices also call for proper weep holes in brick construction. However, local generally accepted building practices usually lag behind nationally accepted practices and may not require weep holes.
    Walls may be retrofitted with weep holes but without flashing to direct the water to the weep holes, retrofitting may be useless.

    You may also want to review the following resources about the need for flashing and weep holes in brick walls.
    a. The Brick Industry Association web site at www.bia.org.
    b. An article on The Journal of Light Construction web site www.jlconline.com.
    The article is: Keeping water out of brick veneer, by Jerry Carrier. Great
    explanations, great pictures. Costs $5 to download if you're not a member.
    c. The Building Science Corporation web site at
    www.buildingscience.com/resources/walls/solar_driven_moisture_brick.htm
    d. Construction books at your local library.

    I recommend three courses of action:
    1. Review the above resources to educate yourself about the need for brick
    weep holes and flashing.
    2. Consult the local building inspectors office for local requirements.
    3. Contact some knowledgeable qualified brick or masonry contractors to
    determine repair methods, estimate costs, and perform the necessary repairs.

    ==================================

    Again, thanks for sharing.

    Erby Crofutt, Georgetown, KY - Read my Blog here: Erby the Central Kentucky Home Inspector B4 U Close Home Inspections www.b4uclose.com www.kentuckyradon.com
    Find on Facebook at: https://www.facebook.com/B4UCloseInspections

  14. #14
    Join Date
    Mar 2007
    Location
    Fuquay Varina, NC
    Posts
    1,074

    Default Re: Effloresence on brick veneer

    Don't forget this.

    R703.7. See Section R703.8 for additional requirements.
    R703.7.6 Weepholes. Weepholes shall be provided in the outside wythe of masonry walls at a maximum spacing of 33 inches (838 mm) on center. Weepholes shall not be less than 3/16 inch (4.8mm) in diameter.Weepholes shall be lo-cated immediately above the flashing.
    R703.8 Flashing. Approved corrosion-resistive flashing shall be provided in the exterior wall envelope in such a manner as to prevent entry of water into the wall cavity or penetration of water to the building structural framing components. The flashing shall extend to the surface of the exterior wall finish and shall be installed to prevent water from reentering the ex-
    terior wall envelope. Approved corrosion-resistant flashings shall be installed at all of the following locations:

    1. At top of all exterior window and door openings in such
    a manner as to be leakproof, except that self-flashing

    5. Where exterior porches, decks or stairs attach to a wall
    or floor assembly of wood-frame construction.
    6. At wall and roof intersections.
    7. At built-in gutters.


    Mike Schulz License 393
    Affordable Home Inspections
    www.houseinspections.com

  15. #15
    Join Date
    Mar 2007
    Location
    Georgetown, KY
    Posts
    538

    Default Re: Effloresence on brick veneer

    Mike,

    Don't forget this

    http://www.lrc.ky.gov/KRS/198B00/738.PDF

    from these:

    Statutes and Regulations


    So simple to get around, but it's there nonetheless.

    Erby Crofutt, Georgetown, KY - Read my Blog here: Erby the Central Kentucky Home Inspector B4 U Close Home Inspections www.b4uclose.com www.kentuckyradon.com
    Find on Facebook at: https://www.facebook.com/B4UCloseInspections

  16. #16
    Join Date
    Mar 2007
    Location
    Fuquay Varina, NC
    Posts
    1,074

    Default Re: Effloresence on brick veneer

    That is unbelievable

    I guess they are always correct and should not be second guessed.

    Instead of saying "code" say "standards" in the report.

    But I know I did not need to tell you that. By the way. That was a real good write up. I'm impressed.

    I really never under stood this one though:
    1. At top of all exterior window and door openings in such
    a manner as to be leakproof, except that self-flashing

    Mike Schulz License 393
    Affordable Home Inspections
    www.houseinspections.com