Re: MWBC Three circuit breakers?
Break, Break!!!! Radio check
Ya'll run out of ink arguing with Lisa?
The beatings will continue until morale has improved. mgt.
-
05-20-2014, 07:50 PM #3
Re: MWBC Three circuit breakers?
Vern I can't make out the pic.
How did you see 3? Do you mean a red, a black and the white from one conductor are each on an adjacent breaker?
The two that are on the same bus will not be going to the same fixture. There is no potential between them. So one of those two goes off to another fixture or it should not be there. The other one could be operating a 240 volt device with the third wire.
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
-
05-20-2014, 08:00 PM #4
Re: MWBC Three circuit breakers?
I've never seen this done before and it is hard to describe. One set of 3 wires leaves the panel at the top, the other set of three wires leave the panel at the bottom. Three circuit breakers in a row have the center breaker supplying one leg of both the top and bottom set of wires. As far as loading I don't see a problem but need another set of eyes.
The beatings will continue until morale has improved. mgt.
-
05-20-2014, 08:07 PM #5
Re: MWBC Three circuit breakers?
Your drawing shows 3 breakers and 2 loads, and, not, those are not MWBC.
-
05-20-2014, 08:12 PM #6
-
05-20-2014, 08:13 PM #7
Re: MWBC Three circuit breakers?
-
05-20-2014, 08:16 PM #8
-
05-20-2014, 08:49 PM #9
Re: MWBC Three circuit breakers?
Come on Jerry, I gotta bag this thing up and send it. You got anything?
The beatings will continue until morale has improved. mgt.
-
05-20-2014, 09:20 PM #10
Re: MWBC Three circuit breakers?
-
05-20-2014, 09:29 PM #11
Re: MWBC Three circuit breakers?
Seriously, if the shared circuit breaker is in the center of the three breakers, I don't see a problem with over loading of any wires. I know this is not the MWBC we see all the time, but why wouldn't they have called it a three wire circuit if something like this was not anticipated?l
The beatings will continue until morale has improved. mgt.
-
05-20-2014, 09:34 PM #12
Re: MWBC Three circuit breakers?
MWBC - see drawing
-
05-20-2014, 09:46 PM #13
Re: MWBC Three circuit breakers?
The beatings will continue until morale has improved. mgt.
-
05-21-2014, 05:02 AM #14
Re: MWBC Three circuit breakers?
Vern,
Your N connections are at the center of the loads with 240 volt connection across each of the loads.
If you disregard the N connections then there are 2 - 240 volt loads sharing a common connection, which could overload that common connection and wire.
-
05-21-2014, 05:33 AM #15
-
05-21-2014, 08:29 AM #16
Re: MWBC Three circuit breakers?
Then what you have is still ... Wrong!

2 MWBC requires 4 breakers, not 3.
It may be working, but you've seen the discussions here about wiring up MWBC off the same phase leg (which means they are not MWBC) and the neutral current doubles?
That same thing is happening on that hot which is common to both.
Doesn't matter if it is a neutral or a hot, put twice as much current on it and it heats up ... when wires heat up they have a tendency to start fires - that's what is wrong with it.
-
05-21-2014, 08:35 AM #17
Re: MWBC Three circuit breakers?
The beatings will continue until morale has improved. mgt.
-
05-22-2014, 04:38 AM #18
Re: MWBC Three circuit breakers?
Even on a larger monitor I can't see enough detail, but get the impression that 2 b/r/w cables were just spliced in the panel and placed on one half of two tandems on opposite legs of the panel. The red just look like they were spliced to blue leads at least once. I can't see where the other blue comes from or the blacks associated with the reds.
All answers based on unamended National Electrical codes.
-