    Default Grounded conductor split between two terminals

    Any real hazard associated with this?

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Grounded conductor split between two terminals

    Define "real" and "hazard".

    Only when something goes not good ("wrong").

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Grounded conductor split between two terminals

    The code requires the conductor to terminate in an individual hole. Lug adapters are available for larger,conductors.

    All answers based on unamended National Electrical codes.

  4. #4
    Join Date
    Apr 2008
    Location
    Western Massachusetts
    Posts
    536

    Default Re: Grounded conductor split between two terminals

    Quote Originally Posted by Jim Port View Post
    The code requires the conductor to terminate in an individual hole. Lug adapters are available for larger,conductors.
    Yeah, but that’s an extra $2.50 and requires the yahoo that did this know what they’re doing. I suppose it’s better than what you normally see: half the strands clipped off and the remainder haphazardly shoved in there.


  5. #5
    Join Date
    Mar 2007
    Location
    Atlanta, Georgia
    Posts
    1,088

    Default Re: Grounded conductor split between two terminals

    Either leg could potentially carry the entire load of the full size wire. Since the leg is roughly half the size of the wire, it is undersized and could overheat leading to fire.

    Is there a potential for arcs to jump between the two legs near where they split?

    "The Code is not a peak to reach but a foundation to build from."

  6. #6
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Grounded conductor split between two terminals

    The hazard would be if one were loose forcing the current onto the now undersized conductor. You could get some arcing at the loose connection to the bus.

    All answers based on unamended National Electrical codes.

  7. #7
    Join Date
    May 2012
    Location
    eastpoint fl
    Posts
    49

    Default Re: Grounded conductor split between two terminals

    Quote Originally Posted by Corn Walker View Post
    Yeah, but that’s an extra $2.50 and requires the yahoo that did this know what they’re doing. I suppose it’s better than what you normally see: half the strands clipped off and the remainder haphazardly shoved in there.
    I think they did that too, on the top lug.


  8. #8
    Join Date
    Nov 2010
    Location
    California
    Posts
    97

    Default Re: Grounded conductor split between two terminals

    That is a listing violation. The equipment label will state what size wire can be in the hole and that ain't it. Strands are broken and damaged.


  9. #9
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,871

    Default Re: Grounded conductor split between two terminals

    Quote Originally Posted by Jim Port View Post
    The hazard would be if one were loose forcing the current onto the now undersized conductor. You could get some arcing at the loose connection to the bus.
    Thats Jim. got it.