Results 1 to 17 of 17
Thread: Double Tapped Main Lugs
-
07-15-2014, 04:48 PM #1
Double Tapped Main Lugs
Service Conductor.jpg
Are the main lugs ever rated for more than one conductor? This is an ITE Pushmatic box with 200 Amp disconnect. Is there any definitive code or standard covering this issue? Under what circumstances, if any, is this allowed? I have seen this a number of times and I haven't been able to find any standards regarding it. If it is just manufacturers documentation, how do we find this?
THanks for the help.
-
07-15-2014, 10:37 PM #2
Re: Double Tapped Main Lugs
It's wrong.
1. Lugs are for one conductor unless it is stamped on the lug.
2. When a lug is rated, listed and labeled for more than one conductor they usually are required to be the same size.
3. There is probably no overcurrent protection for the circuit tapped off the lug except the utility company fuse at the pole or transformer.
-
07-16-2014, 05:26 AM #3
Re: Double Tapped Main Lugs
As Alton noted, it is wrong and I find it fairly often in old panels. Being a Pushmatic, I doubt you will easily find a reference from the manufacturer. I would not worry about documenting that it is wrong, call it out and just say it is wrong and needs an electrician to correct.
Sometimes we are too concerned about providing proof to justify our findings when simply reporting what we find is all that is needed. If someone wants proof let them find the proof that it is correct!
-
07-16-2014, 05:31 AM #4
-
07-16-2014, 10:49 AM #5
Re: Double Tapped Main Lugs
Incorrect! Everything IS leagal untill proven otherwize. Otherwize, only opinions would be necessary instead of legal standards. It is this type of mind set that leads to abuse.
Missing from the pics that have been posted of legal (approved) multi-conductor terminals: There are terminals rated/approved for two conductors under one set screw. I've used them many times, usually in commercial and industrial equipment. Manufacturers often have these as options.
These terminals are characterized by oval or what appears like two holes connected togeather.
They are quite obvious upon observation.
-
07-16-2014, 11:21 AM #6
-
07-16-2014, 01:44 PM #7
Re: Double Tapped Main Lugs
To Bob S, I disagree. Driving 60 in 40 is always illegal, it just becomes a problem when caught. Installing work not in conformance with the standards enforced is illegal, whether it mleads to a problem or not.
Since those are not multi-conductor terminals they are not code compliant. If the NEC has been adopted that would then be a violation of a legally adopted standard.
-
07-16-2014, 06:20 PM #8
Re: Double Tapped Main Lugs
That's like saying that when a tree falls in the forest because there is no one around to hear the sound.
It is illegal (I dislike that term in this instance) WHETHER OR NOT someone is caught or something is proven or not.
A tree falling in the forest DOES make the very same noise ... whether or not anyone is there to hear it.
-
07-18-2014, 02:53 AM #9
Re: Double Tapped Main Lugs
Even if you could apply tap rules & IMO they do not apply in this case, it fails miserably.
-
07-18-2014, 03:12 AM #10
-
07-18-2014, 06:22 AM #11
Re: Double Tapped Main Lugs
I believe Rollie is talking about how it does not come close to meeting the tap rules properly.
- - - Updated - - -
I believe Rollie is talking about how it does not come close to meeting the tap rules properly.
- - - Updated - - -
I believe Rollie is talking about how it does not come close to meeting the tap rules properly.
All answers based on unamended National Electrical codes.
-
07-18-2014, 06:31 AM #12
Re: Double Tapped Main Lugs
If you choose not to decide, you still have made a choice.
-
07-18-2014, 08:16 AM #13
Re: Double Tapped Main Lugs
Hey bob.
A 200 amp disconnect feeds that large conductor.
Someone has slipped a #10 or similar gauge wire in there. It's a no-brainer.
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
-
07-18-2014, 10:30 PM #14
-
07-20-2014, 05:20 AM #15
Re: Double Tapped Main Lugs
Are these neutral lugs the approved type or is this illegal also?
- - - Updated - - -
Are these neutral lugs the approved type or is this illegal also?
-
07-21-2014, 08:12 AM #16
Re: Double Tapped Main Lugs
Ken, they still look like the standard lug that Square D uses that is only for one cnductor.
All answers based on unamended National Electrical codes.
-
07-25-2014, 11:34 AM #17



Reply With Quote


Bookmarks