		Thread: Venting Issues
- 
	11-18-2007, 09:47 AM #1 Venting Issues Venting Issues50,000 BTU GFAF and 40,000 BTU gas WH venting into 8" single wall pipe system passing through attic and meal chimney chase? What concerns (other than the birds nest, the rain cap and the single wall pipe passing through the attic) do others here see with this? 
 Similar Threads:
 
- 
	11-18-2007, 09:56 AM #2 Re: Venting Issues Re: Venting IssuesMaybe it's the photo angle, but in the first one it looks like the wh flue pipe runs downhill. 
 "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
 www.ArnoldHomeInspections.com
 
- 
	11-18-2007, 11:18 AM #3 Re: Venting Issues Re: Venting IssuesI agree. Hard to tell from the photo angle but the WH flu does not appear to have proper slope. 
 "Baseball is like church. Many attend but few understand." Leo Durocher
 Bruce Breedlove
 www.avaloninspection.com
 
- 
	11-18-2007, 11:30 AM #4
 
- 
	11-18-2007, 11:57 AM #5 Re: Venting Issues Re: Venting IssuesNo listed vent system to pass through unconditioned space 
 improper support
 common vent oversized
 vent not protected from damage in accessible portion of attic
 severely restricted vent termination with unlisted hardware cloth doubled
 oversized vent connector on WH (I'm guessing this WH has a 3" draft hood)
 I doubt there is an attic insulation shield and we know there is no listed firestop because there is no listed venting.
 
 The entire installation should be replaced with a properly sized and installed listed B-vent.
 HTH
 Bob
 Keep the fire in the fireplace.
 
- 
	11-18-2007, 01:05 PM #6 Re: Venting Issues Re: Venting IssuesThanks, 
 
 Looks like I got it all - reading and study here and elsewhere must be doing some good!
 
 There was an "insulation shield', and it was even pretty clean on the attic side (no pic), but here's the bottom.
 
 As for the WH, it's going as Spackle does not not appear to be a permanent repair for leaking water heaters.
 
 
- 
	11-18-2007, 01:50 PM #7 Re: Venting Issues Re: Venting IssuesIs there a 30" wide path to and in front of that panel shown between the two units, with at 30" x 36" working space in front of that panel? (Okay, the walkway may be 24" wide, but the working space is 30" x 36".) 
 
 


 
 
					
					
 
				
				
				