I just got sued: Lightning strike and CSST
Just this week I received notice from an insurance company's legal firm that they are seeking a $103,000 reimbursement check from me for fire damage sustained from a lightning strike on a home I inspected 3 years ago.
The lightning strike happened a year and half ago. The legal team went after the Ward company claiming defective csst. The Ward legal people pointed the finger at me because I failed to follow TREC sop "The inspector shall report as deficient appliances and metal pipes that are not bonded or grounded.' The one time I failed to mention this deficiency, is the one time lightning strikes that particular house. What are the odds.
In the five years that I've been inspecting, only one time did I see the bonding cables on all metal piping and appliances in the attic.
My insurance company is handling this. I'll keep you guys posted.
-
09-21-2013, 11:39 AM #2
Re: I just got sued: Lightning strike and CSST
Thanks for sharing
I have a saying about how insurance companies make money:
#1 By finding ways to raise your rates
#2 Finding ways to deny a claim
and #3 (This applies to you) By finding someone else to pay the claim.
Keep us posted
' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.
-
09-22-2013, 06:15 AM #3
Re: I just got sued: Lightning strike and CSST
It's called Subrogation and has become more and more common in the world. I did not know that TX had CSST in their standards three years ago..... The problem with reporting on bonding is that the majority of the time you really can't verify the bond is or is nor present. Time for us all if you don't already have it, to add canned boilerplate verbiage about CSST, bonding, etc.... CYA!
Glad you have E&O to help defer the legal cost.
Last edited by Scott Patterson; 09-22-2013 at 06:21 AM.
-
09-22-2013, 09:52 AM #4
Re: I just got sued: Lightning strike and CSST
I don't see a lot of CSST in the City but run into some of it in the burbs. Did a house out in the burbs about 6 months or so ago that had lots of CSST. Overall bad install. Having read some of the grounding, lightning strike issues, I did some research and included 3 or 4 PDF's about CSST issues with my report. I wrote up the CSST as hazardous due to the install methods.
Buyer gave seller report, Seller said I was full of ----; then buyer sent seller the pdf's I had sent them, seller shut up and worked out a deal.
On NC around here I often find a ground wire run to the gas meter. Unfortunately the wire is always just hanging in the air, not actually attached. I always write it up and developers instead of buying a bracket and having one of their grunts install it prefer to argue about whose responsibility it is to attach the wire.
Sometimes it all just seems so stupid and useless to talk about it when fixing the problem would take less time.
-
09-22-2013, 10:07 AM #5
Re: I just got sued: Lightning strike and CSST
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
09-23-2013, 05:53 AM #6
Re: I just got sued: Lightning strike and CSST
Hi Gunnar, the attached files are the PDF's I gave the client with their report.
Hope they are helpful
MarkusCSST_Product_Liability_Suit.pdfGastite_01.pdf
The following is the title of another PDF I sent them but it doesn't seem to want to upload. I think its too big: Validation of Installation Methods for CSST Gas Piping to Mitigate Lightning Related Damage; put out byThe Fire Protection Research Foundation
You can probably find it and download
When I do run into CSST I also send the client the 'Gastite design and installation guide PDF'. I've had too many DIY husbands comment about how easy it will be to add/modify gas piping for the barbeque grill etc. 'oh with this yellow stuff I can run more gas pipe pretty easy'.
I have the 08 install manual, which I should probably find the new version. The interesting thing about it is that Page 2 talks about lightning safety. Not page 4, 27 or 99; The very next page after the cover page.
Sorry I don't know whats going on with these font sizes, I didn't do it on purpose.
-
09-23-2013, 06:19 AM #7
Re: I just got sued: Lightning strike and CSST
my boilerplate According to some authorities, CSST may be particularly susceptible to damage from lightning strikes. During electrical storms, the metallic systems and the building itself can become highly energized. Metal siding, gas piping, water piping, electrical wiring, communication and entertainment cables may be affected. Arcing from one metallic path or conductor to another can take place, resulting in physical damage. (Arcing is electrical energy jumping through air from one conductor to another or from a conductor to ground, typically accompanied by considerable heat, light and sound. Arcing occurs only where there is a significant difference in potential energy between two materials.)
This is especially dangerous with CSST because of the gas inside. There are several cases of CSST leaks related to electrical storms. At least one class action lawsuit has been brought against manufacturers as a result of this. See Csstsettlement.com.
In response to this issue, installation manuals now have a special electrical bonding and grounding procedure for their CSST systems that may help prevent electricity from jumping (arcing) between metallic systems. Some jurisdictions require the CSST be kept away from other metallic systems such as metal ducts, vents and other pipes to reduce the chance of arcing.
Special bonding requirements for CSST (not copper tubing) typically include the following:
- The tubing itself should be electrically continuous and should be directly bonded to a reliable ground-fault current path.
- There should be a minimum 6 AWG (American Wire Gauge) bonding jumper connected to the electrical service grounding system for the building.
- The bond connection to the gas tubing should be accessible and just downstream of the meter, near the service entrance into the house.
- The bond connection should be upstream of any CSST. Listed bonding/grounding clamps (UL 467) should be used, and connections should be made to a brass fitting, steel manifold or unpainted black iron pipe, not to the CSST itself.
- - - Updated - - -
Also CSST(corrugated stainless steel tubing), is being used as a gas supply line in this home.
We recommend installation of Excess Flow Valves in the event of a gas line breach that would shut down the gas flow.
Please click on link for more information on excess flow valves.
http://www.tracpipe.com/CSST_Gas_Pipe_Products/AutoTrip_EFV_Automatic_Gas_Shut_Off_Valve/
-
09-25-2013, 02:56 PM #8
Re: I just got sued: Lightning strike and CSST
I almost never actually see a ground of any kind to the csst. The ground wire talked about wrapped around the gas pipe coming out of the ground??? Not a ground!
On older homes I always state that a ground rod should be incorporated to the grounding system as know one ever knows if PEX or PVC was added to the plumbing lines which will cancel a good ground anyway with the water lines. As far as CSST I always state that I have no idea how well the csst is grounded as I cannot see the full length of all pipe and they should have the system checked. If I just flat out do not see a ground I recommend the same thing.
A few years ago I got a call to cancell an inspection. The reason? The home was hit by lightening and they confirmed there was not a solid ground for the the homes electric system. The home burnt to the ground.
I never shy away at making the call to have the grounding system for any system in the home confirmed.
Sorry to hear about getting sued.
What if they did not have a home inspection? Would they have gone after the plumber? Electrician? You are not the one that did not ground the system! Hell. In most cases you would have never seen the ground or how good it was.
-
09-25-2013, 05:33 PM #9
Re: I just got sued: Lightning strike and CSST
There are now clear requirements on how CSST should be grounded. The grounding should be as close as possible to where the gas piping enters the house (that is my wording, not an exact quote). I suggest that instead of telling your clients you have not idea how it is grounded you should learn how it should be grounded.
-
09-25-2013, 06:57 PM #10
Re: I just got sued: Lightning strike and CSST
And I think you should think before giving uneeded advise like "you should learn how it should be grounded". I just happen to know how it is suppose to be grounded. Do you? I did not say I did not know how it is suppose to be grounded. I said I said I have no idea if it is or if its a good ground. Of course unless I can see that it appears to be a good ground.
-
09-27-2013, 04:55 PM #11
-
09-27-2013, 05:09 PM #12
Re: I just got sued: Lightning strike and CSST
I'll be a little picky here. Piping is not grounded. Piping is bonded to a ground. Subtle difference and in the grand scheme of life, won't change anyone's life.
As for being sued, we are in a business where we are expected to be perfect at every inspection. That's a high hurdle to get over every day of every week of every year. Finding bonding can be difficult. I think having a boiler plate disclosure is appropriate and might even mitigate or derail a suit...... occasionally.
If you choose not to decide, you still have made a choice.
-
09-27-2013, 05:19 PM #13
-
09-28-2013, 02:42 AM #14
Re: I just got sued: Lightning strike and CSST
Here's a good link about CSST bonding. I see it a lot in my area and only once did I find the bonding wire and that was because is was a gas company install.
CSST Safety Solution
-
09-28-2013, 04:42 AM #15
Re: I just got sued: Lightning strike and CSST
http://www.grefesidney.com/documents...A531161169.pdf
- CSST gas line is extremely thin, with walls typically around 0.008" in thickness. Blackiron gas pipe is typically 0.12" in thickness. Put another way, the walls of black iron pipe are 15times thicker than the walls of CSST tubing. When this is considered, perhaps it is notsurprising that the amount of electrical energy needed to defeat traditional black iron pipe isabout 15 times more than the energy needed to defeat the much thinner walls of CSST tubing.
When electrical energy from lightning is conducted through CSST tubing, electricalarcing can be created between the CSST and any grounded metallic object, as the lightningenergy seeks a ground source. This arcing can instantaneously burn a small hole, ranging fromthe size of a pin-head to a pencil eraser, right through the very thin wall of the CSST. The arcingevent can easily ignite the escaping gas being carried by the CSST, which can then serve as ablow-torch with an endless gas fuel source more than sufficient to ignite nearly any type ofstructure.
Lightning strikes the United States more than 25 million times each year and accordingto Underwriters Laboratories (UL), lightning accounts for more than $1 billion in annualstructural damage. A single bolt of lightning can carry over 100 million volts of electricity, andin reality, there are no construction methods or safety measures that can completely protect a
structure from a direct lightning strike. CSST gas pipe, however, is susceptible to damage fromnon-direct lightning strikes as well, even strikes which may be recorded a significant distanceaway from the structure. “Lightning does not have to strike a building directly in order for theCSST to be affected,†explains Guy Maxwell, president of the Lightning Safety Alliance. “Thereports of CSST related fires that I have seen have involved strikes that were near the structure.â€
CSST was originally developed in the late 1980s, but most CSST product has beeninstalled since 2003. Any building that has had natural gas piping work done since 1990 couldhave CSST installed. According to the National Fire Protection Association (NFPA), no tests onthe effects of lightning on CSST were conducted prior to its approval for use. One CSSTmanufacturer has acknowledged that the installation of a lightning protection system addressesthe lightning hazard associated with CSST, yet homes with CSST are rarely equipped withlightning protection systems.
- CSST gas line is extremely thin, with walls typically around 0.008" in thickness. Blackiron gas pipe is typically 0.12" in thickness. Put another way, the walls of black iron pipe are 15times thicker than the walls of CSST tubing. When this is considered, perhaps it is notsurprising that the amount of electrical energy needed to defeat traditional black iron pipe isabout 15 times more than the energy needed to defeat the much thinner walls of CSST tubing.
-
09-28-2013, 07:04 AM #16
Re: I just got sued: Lightning strike and CSST
To add fuel to this fire( little pun...).... Let's not forget about the CSST that is covered with the black plastic sheathing. It is designed to not be bonded unless the AHJ just wants it done.....
-
09-28-2013, 07:16 AM #17
Re: I just got sued: Lightning strike and CSST
Scott
Never seen black sheathing, only yellow, at least up here.
-
09-28-2013, 09:35 AM #18
Re: I just got sued: Lightning strike and CSST
Its erroneous statements like that (Red colored, bolded & underlined statement by SP, above) that gets HI's & HO's in trouble.
It (only the latest generation black-jacketed SS Tube, the earlier black counterstrike omegaflex still requires special) is still required to be bonded, the manufacturer instructions just don't require ADDITIONAL bonding steps to counteract the inherent deficiency in thin-walled yellow-jacketed SS tube and the earlier version(s) of black jacketed counterstrike, IF the black jacket is intact and the product is overall installed properly, the tubing system IS bonded as per NFPA 70 (national electric code unammended) and NFPA 54 (national fuel gas code unammended) AND a lightning arrestor system is properly designed and installed.
Lets get it right.
For RW, supplying the CSA info at the end of the following snippets quoted from the link provided at the end.
There are no additional bonding requirements for TracPipe® CounterStrike® imposed by the manufacturer's installation instructions. With TracPipe® CounterStrike®'s improved properties, TracPipe® CounterStrike® is to be bonded in accordance with current requirements of the National Electrical Code (NFPA 70), and the National Fuel Gas Code (NFPA 54), and with any local requirements that may be in excess of the national codes. This may result in the avoidance of additional bonding costs which are required for conventional CSST.TracPipe® CounterStrike® is listed by CSA to ANSI LC 1. TracPipe® CounterStrike® meets building code requirements (ASTM E84) with respect to flame spread and smoke density...
Corrugated Stainless Steel Tubing - Lightning Protected Gas Pipe
-
12-21-2013, 05:01 PM #19
Re: I just got sued: Lightning strike and CSST
My E&O underwriters just informed me they will no longer insure me. Surprised?
-
12-21-2013, 05:22 PM #20
Re: I just got sued: Lightning strike and CSST
, but expected. The worst thing that an agent can have is a claim paid out.
-
12-21-2013, 06:15 PM #21
-
12-21-2013, 06:37 PM #22
Re: I just got sued: Lightning strike and CSST
Please update us on if you have any problems getting re-insured.
A friend of mine just wrapped up a lawsuit where his insurance settled for a few bucks over his deductible and immediately jacked his rate up. BUT, the amazing thing is that the mediator asked the insurance attorney why he was settling when the plaintiff didn't have any case at all.
It was cheaper for the company than any further litigation and winning didn't matter to them. Only what it cost them was what mattered. To hell with what it cost the inspector. Of course, the inspector could have continued the fight on his own but that would have been even more costly, even if he won.
If you choose not to decide, you still have made a choice.
-
12-21-2013, 09:00 PM #23
Re: I just got sued: Lightning strike and CSST
-
12-22-2013, 07:36 AM #24
Re: I just got sued: Lightning strike and CSST
Don't forget to sue the agent to share in the damages you paid (get half your money back).
-
12-29-2013, 04:07 PM #25
Re: I just got sued: Lightning strike and CSST
Dumb question and I do know the answer but if someone did not bond some piping or any type of bond or ground fir the systems in the home why would they not go after just the installer of that gas pipe or the installer of the system. Why would they keep going in circles to get a home inspector.
Example
Someone does some bad wiring in a home and a section that started a fire happened to have the insulation pushed back away from it but was done by someone else hooking some other circuit into the line after the home inspection....they are going after a home inspector?
Example (three years is a long time)
He did not mention it. Does that mean there was never a bond. If never a bond go after the installer. If there was a bond and it was a poor bond or someone changed something and removed the bond???? I guess that is the inspectors fault as well? Obviously if the original installer never bonded it and should have why is the inspector singled out. Mentioned it or not there was never a bond...go after the installer. yeah yeah, he did not go by SOPs! There was still never a bond.
Just freaking criminal.
-
12-29-2013, 05:19 PM #26
Re: I just got sued: Lightning strike and CSST
Typical practice for attorneys is to sue everybody who was in any way involved. Most cases settle without going to court. Each company or insurance company often figures it is cheaper or there is less risk to settling than fighting. It is not fair, but attorneys make the laws.
-
12-29-2013, 05:38 PM #27
Re: I just got sued: Lightning strike and CSST
Keep in mind that the date of the installation and the bonding requirements at that time take precedence ... while not forgetting what has been learned about the necessity for bonding since that time.
Regardless of bonding the CSST, the CSST can be damaged by a lightning strike, not sure that the additional bonding would prevent that damage - that is up to people much smarter than me (much higher pay grade too).
The CSST *is* bonded - the CSST is bonded through the electrical/gas equipment it is connected to.
The key is the "additional" bond required *by current manufacturer's installation instructions" - keep in mind that we are referring to the regular 'yellow' outer jacketed CSST, not the newer 'strike resistant' CSST with the newer outer jacket which is supposed to help dissipate the energy from the strike.
The reason they go after the home inspector is that they go after "everyone" - like throwing spaghetti against the wall and seeing what sticks. Using that California case, the home inspector may be able to bring the real estate agent and the seller in to get part of their money back, even bringing in the builder, the contractor who installed it, etc. ... again, the practice of 'shotgunning' everyone to see what sticks to whom.
-
12-30-2013, 02:34 PM #28
Re: I just got sued: Lightning strike and CSST
[QUOTE=Frank Adame;I received notice from an insurance company's legal firm that they are seeking a $103,000 reimbursement check from me for fire damage sustained from a lightning strike on a home I inspected 3 years ago.
Here is a case that might ease your mind. CCST not necessarily lightning p-roof even if grounded.
[url=http://www.structuretech1.com/2010/11/alert-jury-rules-that-csst-is-a-defective-product-in-landmark-case/]ALERT: Jury Rules That CSST Is A Defective Product In Landmark Case | Structure Tech Home Inspections[/url]
Tks for post. gonna check my rentals for grounded meter - CSST or not.
-
12-30-2013, 06:03 PM #29
Re: I just got sued: Lightning strike and CSST
[QUOTE=james hiatt;235604]
Originally Posted by Frank Adame;I received notice from an insurance company's legal firm that they are seeking a $103,000 reimbursement check from me for fire damage sustained from a lightning strike on a home I inspected 3 years ago.
Here is a case that might ease your mind. CCST not necessarily lightning p-roof even if grounded.
[url=http://www.structuretech1.com/2010/11/alert-jury-rules-that-csst-is-a-defective-product-in-landmark-case/
Dale Griffis
January 4, 2012, 10:42 pm
Actually, the biggest problem with standard CSST is the bond. I’ll explain. All gas piping must be bonded with a dedicated copper ground to the ground buss in the electrical panel box. The problem arises when the communications guys cross the CSST with their low voltage wiring. When the lightning strikes, it actually strikes the communication lines ( which aren’t bonded ) and arcs to the thin CSST, sometimes in several places, which subsequently burns small holes in the CSST and ignites the gas that is now escaping at the same time. I have installed miles of Stainless gas lines and have done my fair share of repairing after the fires. Every time without exception it has been the communication lines that caused the problem. I find CSST to be a good product, there just needs to be care exercised when installing low voltage near it.
-
12-30-2013, 07:25 PM #30
Re: I just got sued: Lightning strike and CSST
While that is what the article said, the installation instructions which I recall having seen all specify for the bond to be 'in accordance with NEC/NFPA 70', and that states: (bold and underlining are mine)
- (B) Other Metal Piping. Where installed in or attached to a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with 250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.
Note that it is not to "electrical panel box", it is to the service equipment or grounding electrode system.
-
12-30-2013, 08:10 PM #31
Re: I just got sued: Lightning strike and CSST
The reason the insurance company comes after the inspector is because in Texas we have insurance which paints a big target on our back. Good luck finding the installer or even the builder. We have become the low hanging fruit on the subrogation (sp?) plan of insurance companies.
-
12-31-2013, 07:50 AM #32
-
12-31-2013, 09:15 AM #33
Re: I just got sued: Lightning strike and CSST
Yes, it is a good idea to keep all conductors away from CSST, however, if there is a lightning strike not having any conductors near the CSST is not going to protect the CSST as the lightning strike will go everywhere and hit anything it can trying to find a path to ground. Do you remember those photos I posted years ago of a lightning strike which splintered a truss and exploded NM cable on it way to ground?
- - - Updated - - -
Yes, it is a good idea to keep all conductors away from CSST, however, if there is a lightning strike not having any conductors near the CSST is not going to protect the CSST as the lightning strike will go everywhere and hit anything it can trying to find a path to ground. Do you remember those photos I posted years ago of a lightning strike which splintered a truss and exploded NM cable on it way to ground?
-
02-01-2014, 09:55 PM #34
Re: I just got sued: Lightning strike and CSST
Here's my boiler on CSST bonding.
This house has CSST gas piping. All CSST gas piping manufacturers require that their product be bonded to the house electrical grounding system. The bonding is intended to prevent damage to the CSST that could happen from lightning strikes. Of all the visible portions of CSST in this house, I did not see any of it bonded. Have a qualified electrician bond this CSST to meet the installation requirements of its manufacturer. The following link is to a document with the manufacturers bonding instructions.
I then leave in the applicable link depending what brand is present, and cut out the other two.
http://www.wardflex.com/images/Techn...tin_WF2008.pdf
http://www.ci.faribault.mn.us/assets...ipebonding.pdf
http://www.gastite.com/include/langu.../TB2010-01.pdf
-
02-02-2014, 10:46 AM #35
Re: I just got sued: Lightning strike and CSST
Excellent John!
Just out of curiosity, do you include the comment in the Electrical portion of your report or the Gas Piping / Plumbing section of your report?
- - - Updated - - -
Excellent John!
Just out of curiosity, do you include the comment in the Electrical portion of your report or the Gas Piping / Plumbing section of your report?
-
02-02-2014, 03:47 PM #36
Re: I just got sued: Lightning strike and CSST
Hank,
I put the comments about bonding CSST into the electrical section of the report.
Other types of CSST problems like lack of proper protection (strike plates) and incorrect routing or supporting go into the plumbing section of the report.
-
03-27-2014, 06:33 AM #37
Re: I just got sued: Lightning strike and CSST
This was on just last week.
TODAY investigates: Dangers of CSST tubing - Video on TODAY.com
Alpha Home Inspections
417- 334-7047
-
04-16-2014, 07:14 AM #38
Re: I just got sued: Lightning strike and CSST
[QUOTE= My insurance company is handling this. I'll keep you guys posted.[/QUOTE]
Never let your insurance company handle something like this all by itself. Hire your own attorney at least to review the facts and give an opinion regarding culpability in writing and to your insurance. Also that atty should review any information available from existing cases regarding percentage liability….. The insurance will tell you that IF they are to insure you that they MUST handle your defense etc. However your atty can let them know that if they ignore YOUR legal rights (and his legal opinions) that they legally will not be able to use the settlement against you in future rates or to terminate your insurance. In other words you can make it very hard for the ins to play games with you instead of the plaintiff.
Remember, you did not obtain the permit, do the work and illegaly install the system and you did not cause the lightening strike. Therefore your culpability is severely reduced. Now, if the bonded ground was visible and had been damaged (broken by a weed wacker lets say) and you missed it then you have much more liability.
The issue is that Insurance companies are NOT THERE FOR YOUR BENEFIT, they are there to minimize thier own losses and make money. Thier interests are NOT your interests and never will be.
Spend the few hundred and do some research on your own as well to assure that COURT CASES that exist uphold the suit against you or not and to what percentage of total liability. Remember YOU are the one being sued, not your insurance! You have rights of defense. The ins company will try and tell you that if thier attys dont handle it then you are not insured. I doubt that will hold up in a court in any state. The action is against you. They must look after YOUR interests in the actions as well as limiting liability.
-
08-14-2014, 07:48 AM #39
Re: I just got sued: Lightning strike and CSST
In NY (at least in my area) it is still required to be bonded (additional bonding), just like the yellow jacketed csst.
- - - Updated - - -
In NY (at least in my area) it is still required to be bonded (additional bonding), just like the yellow jacketed csst.
-
08-14-2014, 08:40 AM #40
Re: I just got sued: Lightning strike and CSST
Two weeks ago I talked to the head building official for Wichita Kansas. He said additional csst bonding is not required there because the metallic tubing material is a better bonding conductor than a #6 bonding wire. I'm not making this up!
-
08-15-2014, 05:34 AM #41
Re: I just got sued: Lightning strike and CSST
CSST is just an accident waiting to happen! Bonded or not the thin wall CSST is just no match for a lighting strike, it's going to punch a hole in it. With Lubbock TX outlawing its use, my bet is that this will expand through other TX towns and parts of the country. You just can't beat "black" pipe for gas distribution in a home.
-
08-15-2014, 05:31 PM #42
Re: I just got sued: Lightning strike and CSST
you should all be recommending Excess flow valve installation even where the system is bonded.
Code is minimum, we are trying to save lives.
-
08-15-2014, 07:33 PM #43
Re: I just got sued: Lightning strike and CSST
-
09-03-2015, 12:08 PM #44
Re: I just got sued: Lightning strike and CSST
Sept 2015......any update on this case?