Re: sprinkler shut off before main shut off
-
08-22-2014, 06:14 AM #3
Re: sprinkler shut off before main shut off
photo i hope
-
08-22-2014, 11:29 AM #4
Re: sprinkler shut off before main shut off
Hi Charlie,
When you click "Upload Photo" a new window pops up. Any chance your browser is blocking the pop-up?
View The List Of InspectionNews Member Benefits!
-----------------
Sincerely,
Brian Hannigan
InspectionNews.net / InspectionReferral.com
Helping Inspectors $ucceed Since 1997TM
Facebook: https://www.facebook.com/InspectionNews
Twitter: @InspectionNews
-
08-22-2014, 06:24 PM #5
Re: sprinkler shut off before main shut off
I see it all the time in my area. They usually want street pressure and not pressure after the regulator.
If needed, they can always shut off at the meter.
-
08-23-2014, 07:13 AM #6
Re: sprinkler shut off before main shut off
here is photo yeah
-
08-23-2014, 07:39 AM #7
Re: sprinkler shut off before main shut off
Nothing wrong with doing it as shown, however, if water pressure before the PRV is over 80 psi then there is a problem.
' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.
-
08-23-2014, 11:08 AM #8
Re: sprinkler shut off before main shut off
-
08-23-2014, 12:53 PM #9
Re: sprinkler shut off before main shut off
Last edited by Rick Cantrell; 08-23-2014 at 01:01 PM.
' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.
-
08-23-2014, 07:02 PM #10
Re: sprinkler shut off before main shut off
I would hope that the sprinkler does not feed the hose bibb (not sure why it would?).
Granted, that sprinkler line in the photo is copper and I don't know what the maximum pressure rating of that copper system is, but it is not uncommon for CPVC sprinkler systems to have 150 psi and greater (I've seen some at 200 psi) and the sprinkler piping is, naturally, within the footprint of the building (has to be for the heads to be in the right areas).
The maximum 80 psi pressure limitation is for the domestic water system, not the fire sprinkler system. The piping is not the concern for the pressure in the domestic water system as much as it is for the pressure at the fixtures and appliances (one example is that the water heater T&P would open if the domestic water pressure was 150 psi).
-
08-24-2014, 05:06 PM #11
Re: sprinkler shut off before main shut off
THIS IS THE IRRIGATION SPRINKLER SYSTEM
-
08-24-2014, 08:56 PM #12
-
08-25-2014, 05:28 AM #13
Re: sprinkler shut off before main shut off
I've set them up this way on purpose in the past. It allows one to keep the irrigation system working while the house water is shut off, for maintenance or a vacation, or to shut down the sprinklers for repairs without killing the house water.
True Professionals, Inc. Property Consultant
877-466-8504
-
08-25-2014, 05:57 AM #14
Re: sprinkler shut off before main shut off
I see this from time to time.....not a problem.
If you choose not to decide, you still have made a choice.
-
08-25-2014, 06:35 AM #15
Re: sprinkler shut off before main shut off
This installation appears to be code compliant as long as a backflow prevention device is installed on the irrigation piping to prevent cross contamination with the potable water system.