1. Distance from supply
2. Boiler just starting up, water entering the loops will take some time to heat the mass, more so if the tubing is in concrete.
3. Insulation/radiant barrier improperly installed in concrete.
Was the heating system running when you inspected or did you activate the system?
-
11-04-2014, 07:44 AM #3
Re: Hot water floor heating
It's only a degree or two different. I would not even worry about it. Like Ray noted, it could be caused many reasons.
-
11-04-2014, 06:00 PM #4
Re: Hot water floor heating
If the tubing is fed from a common manifold at the end then the flow rate in each tube will vary. Slab temperature can also vary from sunlight or distance from exterior, etc.
-
11-05-2014, 02:06 PM #5
-
11-05-2014, 06:33 PM #6
Re: Hot water floor heating
-
11-17-2014, 10:01 AM #7
Re: Hot water floor heating
I would guess that the warmer and cooler rectangles correspond to something on the underside of the floor.
Perhaps a closet for the warmer area?
-