Results 1 to 11 of 11
    Nampa, Idaho
    Default Main service disconnect 200 amp, panel 125 amp?
    The homes main electrical service is 200 amps, it's located on a power pole near home and spits off to serve both home and outbuildings. My concern is that the panel in home is rated at 125 amps and has no disconnect other than the main 200 amp. This is the first time is have seen this type of setup, want to make sure I am correct in calling for the homes panel to have a 125 amp disconnect installed.
    Default Re: Main service disconnect 200 amp, panel 125 amp?
    Were there multiple breakers in the meter main?
    Nampa, Idaho
    No just the 200 amp main at the exterior service entrance.
    It sounds like there are several issues. The service is at the pole but the remote panel does not have a means of disconnect along with improper overcurrent protection.
    Nampa, Idaho
    Yes that appears to be the case, also ground wires in remote panel should be on separate bus bar bonded to panel.
    Along with grounding electrode systems at each building as well as at the pole.
    Were the feeders run to the separate buildings from the pole mounted service equipment 3-wire (no separate neutral and ground) or 4-wire (separate neutral and ground)?
    Do you know when that work was done?
    Nampa, Idaho
    House panel is grounded to water supply pipes only, main service has ground rod. Feeders serving outbuildings were 3-wire. Majority of the outbuilding electrical needs updated and replaced, lots of old fused panels with many improper wiring issues, over sized fuses, no ground rods, etc.
    Holladay, UT
    Trent, When you say it "spits off to serve both home and outbuildings" was the 200 Amp breaker double tapped to feed two sub panels.
    http://acloserlookslc.com/
    Nampa, Idaho
    No the main 200 amp lugs were not double tapped. This place was a small farm with many outbuildings. It really just needs to be updated to a 320-400 amp service. Outbuilding wiring was a rats nest of old fuse panels and wiring.
    Chico,Ca
    That pole mounted panel is a Unicorn, they made a "Pick-A-Amp" breaker based on Zinsco, all you had to do was change the rating plug if you needed 100a or 200A, see photos below. Rating plug. Unicorn Breaker next to Milbank 3 pole, who bought Unicorn. My question is does the main have that feature?
    May 2011
    Clarkesville, Georgia
    Why? Do they have enough load to justify?