    Same house as the portal in the joist. How can I add strength to this area?

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Atlanta, Georgia
    Posts
    1,088

    Default Re: Best way to repair?

    Add perpendicular headers to transfer the load to the adjacent joists and sill.

    "The Code is not a peak to reach but a foundation to build from."

  3. #3
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Best way to repair?

    It is adjacent to a block wall. If that wall rests on a spread footing, you could put a post on a concrete pier under the joist. Just make sure the post is well clear of the dirt and has a moisture barrier, protection from the damp concrete.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  4. #4
    Daryl Roche's Avatar
    Daryl Roche Guest

    Default Re: Best way to repair?

    Quote Originally Posted by John Kogel View Post
    It is adjacent to a block wall. If that wall rests on a spread footing, you could put a post on a concrete pier under the joist. Just make sure the post is well clear of the dirt and has a moisture barrier, protection from the damp concrete.
    This joist sit next to the block wall and the sill joist sits on the outside edge of this wall so there is approx. eight inches of space between the two. Probably will go with the perpendicular method. Just shook my head and told him I'd get it fixed after the first of the year. The metal duct line above it is the new dryer vent line Installed to correct the use of flex. insulated heating line used for the last fifteen feet of the run. Thanks for the responses.


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Best way to repair?

    I would just build up a ledger bolted to that wall, build it out far enough to support that joist, no need to perpendicular headers or doubling of joists the headers are transferring the load to ... the joist is now carried on the new ledger.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Mar 2012
    Location
    Lansdale, PA
    Posts
    876

    Default Re: Best way to repair?

    A relatively simple fix is to notch out a piece of the sill adjacent to the notched joist (or notch the bottom of the joist 1-1/2" high) and run a 2x6 flat resting on the FW or sill over the bottom of the next joist. Attach through the 2x6 into the bottom of the joist with two lag bolts. Because of the leverage the load on the 2x6 and lag bolts is small.


  7. #7
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: Best way to repair?

    There is a leak at the 45 deg. fitting.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  8. #8
    Join Date
    Mar 2007
    Location
    Orlando, FL
    Posts
    1,596

    Default Re: Best way to repair?

    Quote Originally Posted by Raymond Wand View Post
    There is a leak at the 45 deg. fitting.
    Looks more like a burr.


  9. #9
    Daryl Roche's Avatar
    Daryl Roche Guest

    Default Re: Best way to repair?

    Quote Originally Posted by Raymond Wand View Post
    There is a leak at the 45 deg. fitting.
    I'll check that out . Shouldn't be any water there it's the exhaust vent for hot water tank but, we'll take a look. THanks for all of the replies.