NFPA 211
11.3.2 The minimum thickness of hearth extension shall be
2 in. (51 mm).
11.3.3 Where the fireplace opening is less than 6 ft2 (0.56 m2),
the hearth extension shall extend as follows:
(1) At least 16 in. (406 mm) in front of the facing material
(2) At least 8 in. (203 mm) beyond each side of the fireplace
opening (See Figure 11.3.3.)
11.3.4 Where the fireplace opening is 6 ft2 (0.56 m2) or
larger, the hearth extension shall extend as follows:
(1) At least 20 in. (508 mm) in front of the facing material
(2) At least 12 in. (305 mm) beyond each side of the fireplace
opening (See Figure 11.3.3.)
11.3.5 Where a fireplace is elevated above or overhangs a
floor, the hearth extension also shall extend over the area under
the fireplace.
Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
01-12-2015, 11:42 AM #3
Re: Hearth extension code?
Thanks Marc. You're the man.
-
01-12-2015, 05:58 PM #4
Re: Hearth extension code?
Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
01-13-2015, 10:51 AM #5
Re: Hearth extension code?
-
01-15-2015, 09:56 AM #6
Re: Hearth extension code?
Chapter 11.1 of NFPA 211 applies to Factory-built fireplaces: 11.1.2 " Hearth extensions shall be provided in accordance with the manufacturer's instructions or shall be of masonry or on-combustible construction in accordance with Section 11.3 (see above). [manufacturer's instructions always take precedence over the code.]
-
01-15-2015, 12:05 PM #7
Re: Hearth extension code?
Not if the code is more restrictive.
The codes reference the code AND the manufacturer's installation instructions, which means the most restrictive of the two apply.
Mamy (most) codes state "the most restrictive" shall apply, and "this code and the manufacturer's installation instructions" and even something similar to 'unless the manufacturer's installation instructions violate this code, then the code shall apply'.
-
09-20-2015, 02:27 PM #8
Re: Hearth extension code?
Haven't done the inspection yet, that's tomorrow so I can't post my own pic. However, looking at the OPs pic and from what I can see with listing pics, the fireplace looks very similar, I.e factory built and elevated 18" or so. The differences being that with tomorrow's challenge, the fireplace has glass doors and the floor directly below them is tile, as is the whole of the ground floor. The hearth itself is not raised but also of a non-combustible material - floor tile but set on a diagonal to differentiate from the rest of the floor. I'm of the opinion that it still does not negate the requirement for a raised hearth.
This is a 2006 tract home, without modification (I'm told) and clearly passed AHJ final occupancy inspection and approval. Thoughts?
-
09-21-2015, 06:13 AM #9
Re: Hearth extension code?
If it has a glass panel covering the front of the fireplace with direct vent gas logs, the hearth is a non-issue. The NFPA 211 was primarily written to cover wood burning fireplaces, where logs, embers, etc could fall out of the opening….. Sometimes common sense needs to win…

-
09-23-2015, 01:56 PM #10
Re: Hearth extension code?
Having a hard time posting a pic...but anyway, the fire box and hearth is s I first saw. A Superior fire box, capable of handling logs and other flamables with bi-fold glass doors (not fixed as they would be for a vented gas log set) and a mesh spark screen. Hearth is level with surrounding tile floor and not raised. Any extensions, as required, is thereby moot. Firebox is 16" above tile.
Definately a hazard to young'uns, walking into the fire when lighted.