    Default 100 amp service wires used for a 200 amp panel ?

    I know this is wrong, but just want to hear from you guys. The service panel is rated for 200 amp, but the service wires were small. I think the service wires were rated for 100 amp 2 AWG, I took a picture of the round meter base, but forgot to actually look at the meter for the 100 amp label.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: 100 amp service wires used for a 200 amp panel ?

    Quote Originally Posted by Sam Morris View Post
    I know this is wrong, but just want to hear from you guys. The service panel is rated for 200 amp, but the service wires were small. I think the service wires were rated for 100 amp 2 AWG, I took a picture of the round meter base, but forgot to actually look at the meter for the 100 amp label.
    Sam, are you sure the wires are not tinned copper?

    The beatings will continue until morale has improved. mgt.

  3. #3
    Join Date
    Dec 2008
    Location
    Erwin, TN
    Posts
    330

    Default Re: 100 amp service wires used for a 200 amp panel ?

    Quote Originally Posted by Vern Heiler View Post
    Sam, are you sure the wires are not tinned copper?
    Aluminum clad copper, not the same think ? Aluminum


  4. #4
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: 100 amp service wires used for a 200 amp panel ?

    Quote Originally Posted by Sam Morris View Post
    Aluminum clad copper, not the same think ? Aluminum
    Tinned or clad, copper is copper!

    The beatings will continue until morale has improved. mgt.

  5. #5
    Join Date
    Dec 2008
    Location
    Erwin, TN
    Posts
    330

    Default Re: 100 amp service wires used for a 200 amp panel ?

    Quote Originally Posted by Vern Heiler View Post
    Sam, are you sure the wires are not tinned copper?
    May have been, the wires where small 2/0 I think. Not thick enough for 200 amp


  6. #6
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: 100 amp service wires used for a 200 amp panel ?

    Quote Originally Posted by Sam Morris View Post
    May have been, the wires where small 2/0 I think. Not thick enough for 200 amp
    2/0 copper service is good for 200amp

    The beatings will continue until morale has improved. mgt.

  7. #7
    Join Date
    Dec 2008
    Location
    Erwin, TN
    Posts
    330

    Default Re: 100 amp service wires used for a 200 amp panel ?

    Quote Originally Posted by Vern Heiler View Post
    2/0 copper service is good for 200amp
    Minimum conductor size for 200 amp service is 3/0 Awg CU and 4/0 for AL ?


  8. #8
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: 100 amp service wires used for a 200 amp panel ?

    Quote Originally Posted by Sam Morris View Post
    Minimum conductor size for 200 amp service is 3/0 Awg CU and 4/0 for AL ?
    Just checked my "Code Check" to make sure. 2/0 copper is listed for 200 amps

    The beatings will continue until morale has improved. mgt.

  9. #9
    Join Date
    Dec 2008
    Location
    Erwin, TN
    Posts
    330

    Default Re: 100 amp service wires used for a 200 amp panel ?

    Quote Originally Posted by Vern Heiler View Post
    Just checked my "Code Check" to make sure. 2/0 copper is listed for 200 amps
    Stand corrected, looking at the wrong side THANK YOU


  10. #10
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: 100 amp service wires used for a 200 amp panel ?

    The rating of a panel is the maximum ampacity it can be used with. Using a 200 amp panel and feeding it with 100 amps is perfectly acceptable as long as the OCP is properly rated.

    All answers based on unamended National Electrical codes.

  11. #11
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: 100 amp service wires used for a 200 amp panel ?

    Quote Originally Posted by Jim Port View Post
    The rating of a panel is the maximum ampacity it can be used with. Using a 200 amp panel and feeding it with 100 amps is perfectly acceptable as long as the OCP is properly rated.
    Yes, but ... the photo shows a 200 amp disconnect - however, the tinned copper conductors are probably 200 amp rated.

    That said, though, tinned copper indicates (and it looks like) rubber insulation, and the rubber insulation is quite likely dried out and deteriorated, which can lead to ground-fault leakage and worse.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  12. #12
    Join Date
    Dec 2008
    Location
    Erwin, TN
    Posts
    330

    Default Re: 100 amp service wires used for a 200 amp panel ?

    So what you're saying is I can have 100 amp rated service wires connected to a 200 amp rated panel and that would be acceptable?


  13. #13
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: 100 amp service wires used for a 200 amp panel ?

    Quote Originally Posted by Sam Morris View Post
    So what you're saying is I can have 100 amp rated service wires connected to a 200 amp rated panel and that would be acceptable?
    IF ... if the disconnect in the panel was 100 amp rated.

    The disconnect rating *must not be rated higher than* the rating of the panel mains or the rating of the service entrance conductors.

    If someone comes along later and replaces the disconnect with one which has a rating higher than the panel rating or the rating of the conductors ... well ... that person just created a problem which did not exist before.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  14. #14
    Join Date
    Dec 2008
    Location
    Erwin, TN
    Posts
    330

    Default Re: 100 amp service wires used for a 200 amp panel ?

    Quote Originally Posted by Jerry Peck View Post
    IF ... if the disconnect in the panel was 100 amp rated.

    The disconnect rating *must not be rated higher than* the rating of the panel mains or the rating of the service entrance conductors.

    If someone comes along later and replaces the disconnect with one which has a rating higher than the panel rating or the rating of the conductors ... well ... that person just created a problem which did not exist before.
    Doesn't the meter base look like its rated for 100 amp, I will be going back tomorrow to check the rating on it, wouldn't that also matter ?. The service wires to the electrical where small 2/0 , they look big in the pictures.


  15. #15
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: 100 amp service wires used for a 200 amp panel ?

    Why do you think a 100 amp feed cannot supply a panel rated for a higher ampacity? You could feed 60 amps into a 200 amp panel if the loads were below the feeder rating.

    All answers based on unamended National Electrical codes.

  16. #16
    Join Date
    Sep 2014
    Location
    Tennessee
    Posts
    7

    Default Re: 100 amp service wires used for a 200 amp panel ?

    Quote Originally Posted by Sam Morris View Post
    Doesn't the meter base look like its rated for 100 amp, I will be going back tomorrow to check the rating on it, wouldn't that also matter ?. The service wires to the electrical where small 2/0 , they look big in the pictures.
    Yes, the meter base rating does matter; for two reasons. They are rated for maximum amperage capacity along with space for the conductors. The meter base should be upgraded to match the service.


  17. #17
    Join Date
    Dec 2007
    Location
    Chico,Ca
    Posts
    454

    Default Re: 100 amp service wires used for a 200 amp panel ?

    The use of 2/0 CU, & 4/0 AL, for a 200A residential service has to meet certain criteria to be allowed to undersize the conductors & the table allowing it was removed in the 2014 NEC, now (where the 2014 NEC has been adopted) it has to be done a little bit differently.


  18. #18
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: 100 amp service wires used for a 200 amp panel ?

    Quote Originally Posted by Rollie Meyers View Post
    The use of 2/0 CU, & 4/0 AL, for a 200A residential service has to meet certain criteria to be allowed to undersize the conductors & the table allowing it was removed in the 2014 NEC, now (where the 2014 NEC has been adopted) it has to be done a little bit differently.
    Many electrical contractors/electricians tried to apply that table to other-than-dwelling units and had to resize the conductors they had pulled in, which meant resizing the raceway as well.

    With that table gone in the 2014 NEC ... all those conductor sizes everyone has remembered for years and years will no longer be applicable - they will need calculations done to justify any reduction from Table 310.16.

    It will throw a wrench in the works for home inspectors with that table gone.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  19. #19
    Join Date
    Dec 2007
    Location
    Chico,Ca
    Posts
    454

    Default Re: 100 amp service wires used for a 200 amp panel ?

    Quote Originally Posted by Jerry Peck View Post
    Many electrical contractors/electricians tried to apply that table to other-than-dwelling units and had to resize the conductors they had pulled in, which meant resizing the raceway as well.

    With that table gone in the 2014 NEC ... all those conductor sizes everyone has remembered for years and years will no longer be applicable - they will need calculations done to justify any reduction from Table 310.16.

    It will throw a wrench in the works for home inspectors with that table gone.
    You can still use the reduced size conductors in a residence under the 2014 NEC, just going to have to do calculations to prove it.


  20. #20
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: 100 amp service wires used for a 200 amp panel ?

    Quote Originally Posted by Rollie Meyers View Post
    You can still use the reduced size conductors in a residence under the 2014 NEC, just going to have to do calculations to prove it.
    "have to do calculations to prove it"

    That is what I was referring to - many contractors (most, if not all), and most (if not all) home inspectors, went by the table ... which will not be there.

    That means that there is not 'quick and easy' 'looksee' to determine the rating of the service based on conductor size.

    Now it will be the main service disconnect rating, and then checking to see if the conductors match that rating and ... oops - the table is gone ... what is the rating of those smaller conductors now?

    Will not be as easy as it was looking at the table.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  21. #21
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: 100 amp service wires used for a 200 amp panel ?

    Quote Originally Posted by Kevin Wood View Post
    It is a 200 amp Main Breaker. So the service must match. #2/0 is fine here too.
    Here, with that table no longer in the code, and without calculations, might need 3/0 copper.