    I know this is not an HVAC topic but I cannot find the area in the forum that covers Dryer vents, so here goes:

    I am seeing more and more of new construction large houses with this dryer vent length disclaimer, when the vent length is extended due to the large attic space the dryer vent go through. The IRC used to be 25 feet, but now it appears the length has been increased in a new code release? When I read the new revision, there are enough exceptions to cause it to be confusing. I cannot seem to find any consensus on dryer vent length. Then there are some dryers that are rated for extended length vents. Those of you that are seeing these extended length vents, how are you handling them on your reports?

    IMG_2181.JPGIMG_2182.JPG

    Similar Threads:
    Member Benefits1

  2. #2

    Default Re: Extended length vent

    Quote Originally Posted by Gene South View Post
    I know this is not an HVAC topic but I cannot find the area in the forum that covers Dryer vents, so here goes:

    I am seeing more and more of new construction large houses with this dryer vent length disclaimer, when the vent length is extended due to the large attic space the dryer vent go through. The IRC used to be 25 feet, but now it appears the length has been increased in a new code release? When I read the new revision, there are enough exceptions to cause it to be confusing. I cannot seem to find any consensus on dryer vent length. Then there are some dryers that are rated for extended length vents. Those of you that are seeing these extended length vents, how are you handling them on your reports?

    IMG_2181.JPGIMG_2182.JPG
    At least you are fortunate enough to have found one with the warning and the developed length filled in. Many times you will find no sticker and no length. Dryers, many dryers, now have the ability to use longer than the old standard 25 feet, minus 2.5 feet for 45 degree fittings and minus 5 feet for 90's.

    As long as the dryer installed is rated for the length they are fine. If the sticker is missing or the length not identified and a person puts a standard dryer in that is not rated for the length it is a fire hazard.

    Oh, and this is the correct area. HVAC stands for Heating Ventilation and Air Conditioning.

    Last edited by JeffGHooper; 04-07-2015 at 10:47 AM.
    PROFESSIONAL CONSULTING AND INSPECTION COMPANY INCLUDING FORENSIC INVESTIGATIONS

    http://jeffghooper.com/

  3. #3
    Join Date
    Sep 2007
    Location
    Morris, Illinois
    Posts
    41

    Default Re: Extended length vent

    Dryer vent length should not exceed dryer manufacturer recommendations. Vent length may differ from appliance to appliance. Exceeding recommendations may create a fire hazard, or at the minimum reduce clothes dryer efficiency - for example; it takes longer to dry clothes.

    Jess
    www.aplusinspector.com
    (815) 941-2345

  4. #4
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Extended length vent

    If you find the sticker, I would leave it at that, assuming of course that is is not an obvious lie!
    I might mention it to a client to keep that in mind while shopping for that new dryer.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Extended length vent

    Dryer exhaust duct length (it's not a "vent") is, and has been, required to be posted on a permanent plaque at the dryer connection end when the dryer exhaust duct is not visible to determine the effective length.

    I know this is in the Mechanical Code, and I'm pretty sure it is in the Residential Code but will need to verify that.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Extended length vent

    From the IRC:
    - M1502.4.5 Length identification.
    - - Where the exhaust duct is concealed within the building construction, the equivalent length of the exhaust duct shall be identified on a permanent label or tag. The label or tag shall be located within 6 feet (1829 mm) of the exhaust duct connection.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Join Date
    Apr 2008
    Location
    McKinney Texas
    Posts
    501

    Default Re: Extended length vent

    Quote Originally Posted by Jerry Peck View Post
    From the IRC:
    - M1502.4.5 Length identification.
    - - Where the exhaust duct is concealed within the building construction, the equivalent length of the exhaust duct shall be identified on a permanent label or tag. The label or tag shall be located within 6 feet (1829 mm) of the exhaust duct connection.
    Thanks Jerry. You're da Man, as always.......


  8. #8
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: Extended length vent

    A few days ago, I saw a booster fan for the dryer vent. I had never seen one before. I wonder if there are issues with lint collecting on the fan blades.