Results 1 to 4 of 4
Thread: How does this panel meet code?
-
04-22-2015, 01:54 PM #1
How does this panel meet code?
This panel is a Thomas and Betts 200 ampere panel installed 15 years ago. 40 slots. There are two terminal strips for neutrals and grounds each with 20 terminals. As I rear the labeling, I assume only one neutral wire is permitted per screw and two ground wires. Unless you install a bunch of two-wire 240-volt circuits how do you connect all of the wires? Am I missing something?
Similar Threads:
-
04-22-2015, 04:23 PM #2
Re: How does this panel meet code?
if it comes down to needing more terminals one can install an additional ground bar for the grounds. thus freeing up terminals on the neutral bars for the neutrals.
-
04-22-2015, 07:48 PM #3
Re: How does this panel meet code?
-
04-22-2015, 09:22 PM #4
Re: How does this panel meet code?
The theory is that the person choosing this panel may be using MWBC, a of 240 circuits, conduit or a ground bar as mentioned above.
I know, it encourages double and triple taps in homes, but it is what it is



Reply With Quote

Bookmarks