No emergency heat setting at thermostats
Split system heat pump. No emergency heat setting at any thermosats. There were three thermostats as it had three zones....none had the emergency heat setting. Honeywell thermostat, click on the mode for cool, heat or off. Heat pump was operated in both heat and cool as the temperature was right around 67 F. Anyone else ever see this.
Similar Threads:
-
08-07-2015, 04:22 AM #2
Re: No emergency heat setting at thermostats
They make all kinds of t-stats. Was this a new install? Maybe that's all they had on the truck that day...
Was there a zone controller? Many of those have an EM heat function. Also, some T-stats will go into EM mode if you increase the Set Temp 2 degrees above current temp.
Dom.
-
08-07-2015, 05:49 AM #3
Re: No emergency heat setting at thermostats
Are there heat strips?
-
08-07-2015, 05:57 AM #4
Re: No emergency heat setting at thermostats
Are you sure they were heat pump units? Check those condenser model numbers and this will tell you real quickly…
-
08-07-2015, 06:47 AM #5
Re: No emergency heat setting at thermostats
-
08-07-2015, 04:09 PM #6
Re: No emergency heat setting at thermostats
Moving the thermostat up 2 degrees (or even 1 degree with digital thermostats) should activate the electric resistance heat, but there should still be an emergency heat setting.
On many of the newer thermostats your have to set up the thermostat based upon what type of system you have. Some have about 10 to 12 options. I came across this with two heat pumps where whoever installed the thermostat did not set it up correctly.
-
08-07-2015, 05:49 PM #7
Re: No emergency heat setting at thermostats
As a previous responder noted, look at the master controller (usually at the AHU) for an emergency button. With a multi zone unit (i.e. more than one thermostat) trying to lock out the heat pump to allow the backup heat to function simply won't work (unless you have REALLY intelligent thermostats).
-
08-09-2015, 06:54 PM #8
Re: No emergency heat setting at thermostats
Look for the reversing valve inside the exterior condenser unit. 98%+ (my made up figure) of heat pump condensers cos will have a visible reversing valve.