Results 1 to 27 of 27
  1. #1
    Join Date
    Mar 2007
    Location
    Daniel Island, SC.
    Posts
    240

    Default New Construction garage roof trusses

    These trusses were seen today in a single car detached garage. The bottom cord was spliced in the middle of each truss and truss plates were installed on both sides. The splice was directly down the center of the garage. It would seem to me that any heavy load stored in the attic of this garage would be a problem for that joint since there is no support under it. Am I over reacting here. Your thoughts please!

    Thanks, Jim

    2015-09-24 11.42.36.jpg2015-09-24 11.42.21.jpg

    Similar Threads:
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: New Construction garage roof trusses

    Quote Originally Posted by JIM MURPHY View Post
    These trusses were seen today in a single car detached garage. The bottom cord was spliced in the middle of each truss and truss plates were installed on both sides. The splice was directly down the center of the garage.
    This is quite common, and, provided the trusses where properly engineered, the trusses should be suitable for their intended use (no storage or limited storage) as per the required design in the code (I do not recommend, as a previous and off the wall poster did, that one presumes that the truss engineer did not know what they were doing).

    It would seem to me that any heavy load stored in the attic of this garage would be a problem for that joint since there is no support under it.
    Sure, one could throw a 50 ton electric hoist up there and lift their Sherman tank with it - but that is not in any standard design rating.

    Am I over reacting here. Your thoughts please!
    Yes ...

    But then, I also did with K.W.'s preceding post, however necessary my explanation was for K.W., it was not meant as a comment on your question, only on K.W.'s response. Take care and have a good day, Jim.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Apr 2013
    Location
    High Springs, Florida
    Posts
    174

    Default Re: New Construction garage roof trusses

    Quote Originally Posted by JIM MURPHY View Post
    These trusses were seen today in a single car detached garage. The bottom cord was spliced in the middle of each truss and truss plates were installed on both sides. The splice was directly down the center of the garage. It would seem to me that any heavy load stored in the attic of this garage would be a problem for that joint since there is no support under it. Am I over reacting here. Your thoughts please!

    Thanks, Jim

    2015-09-24 11.42.36.jpg2015-09-24 11.42.21.jpg
    It is designed by an engineer. No addition loads should be induced.


    www.1stproinspection.com

    Certified Master Inspector
    Like Us On Facebook
    https://www.facebook.com/1stproinspection/

  4. #4
    Join Date
    Mar 2007
    Location
    Orlando, FL
    Posts
    1,596

    Default Re: New Construction garage roof trusses

    You may not have noticed, but the ones in most attics are like that also.

    And when necessary, I stand or step on the seam all the time, no issues....

    Dom.


  5. #5
    Join Date
    Mar 2007
    Location
    Daniel Island, SC.
    Posts
    240

    Default Re: New Construction garage roof trusses

    Thanks to all for your comments!

    Jim

    - - - Updated - - -

    Thanks to all for your comments!

    Jim


  6. #6
    Join Date
    Mar 2012
    Location
    Lansdale, PA
    Posts
    876

    Default Re: New Construction garage roof trusses

    Most truss members are designed mainly for tension or compression loading. However, truss connectors can handle bending. Assuming that the load does not exceed the design load there should be no problem. That is a common location for splices.


  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: New Construction garage roof trusses

    Quote Originally Posted by Dom D'Agostino View Post
    You may not have noticed, but the ones in most attics are like that also.

    And when necessary, I stand or step on the seam all the time, no issues....

    Dom.
    Quote Originally Posted by Kevin Wood View Post
    Because of load bearing walls,they are fine in an attic.
    (sigh)

    Most trusses like that are clear span from bearing near one end to bearing near the other end - and there are no load bearing walls. Load bearing walls are common for conventional framing with sawn lumber. And, yes, I said "most" because there are trusses which require intermediate bearing points, but I also said "like that" because those look like they are clear span trusses.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Mar 2012
    Location
    Lansdale, PA
    Posts
    876

    Default Re: New Construction garage roof trusses

    Quote Originally Posted by Kevin Wood View Post
    Because of load bearing walls,they are fine in an attic.
    It is apparent that you know very little about roof trusses.


  9. #9
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: New Construction garage roof trusses

    Hi Jim, thats probably a legit install even though it looks like crap.
    On a side note, and forgive me if you already know, whenever I see something questionable I try to find a manufacturer label. That allows me to call the Manuf. and ask them directly. Amazing some of the great info you can get sometimes.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: New Construction garage roof trusses

    Quote Originally Posted by Mark Reinmiller View Post
    It is apparent that you know very little about roof trusses.
    Quote Originally Posted by Kevin Wood View Post
    I guess that is why I see cracks in the middle of the ceiling on some inspections. I didn't know contractors were so stupid.
    Kevin,

    I know you are trying to show us just how much you know ... I want you to know that you have succeeded beyond your wildest dreams.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: New Construction garage roof trusses

    Quote Originally Posted by Kevin Wood View Post
    I would love to challenge you in court.
    I am sure you would love to, just like you've shown us how much knowledge you really have.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  12. #12
    Join Date
    Mar 2015
    Location
    Colorado
    Posts
    27

    Default Re: New Construction garage roof trusses

    Okay. Let's keep it collegial.

    The photos and discussion would lead one to surmise that the trusses are of fink-type ("W") design with the bottom chords center spliced using steel gang nail plates at the butt joints in the center of the two-piece bottom chords.

    Multiple factors can come into play here. Assuming that the trusses weren't mishandled during transporting and placement, their design is currently accepted by the organizations which test and approve them. They fall under the general category of light weight construction materials. While not designed or intended for storing items on top of their bottom chords, placing things such as a few pieces of long lumber, holiday decorations, and other relatively low weight items typically doesn't adversely affect their performance. In fact, it's common to attach gypsum board to the underside of such trusses and to place insulation on top of ceiling material attached to their undersides without adversely affecting them.

    A separate issue is the performance of steel gang nail plates under high temperature conditions. It's not uncommon to find truss joints separation in parts of the country where there are high temperature and low humidity conditions (Phoenix, Las Vegas, Tucson, etc.). When the truss lumber shrinks, the short gang nail plate spikes don't provide sufficient penetration (bite) and separation occurs. Also, during fires, the steel plates conduct enough heat into the wood such that the wood chars and the joints fail. Firefighters have been injured and killed due to this particular type of failure. There are always unintended/unanticipated consequences with new technologies. That's why it's always best to learn as much as possible and to keep up with new developments and research. Forums such as this one can be valuable in that regard.

    Keep up the good work, everyone and remember, play nicely.


  13. #13
    Join Date
    May 2010
    Location
    No. San Diego Co., CA
    Posts
    562

    Default Re: New Construction garage roof trusses

    The trusses in my 3 car garage are virtually the same as those posted - a little better quality lumber and larger plate perhaps, as is my neighbor's across the way. I saw him working on his double car roll up door a week or two back and asked what the problem was. For some reason ( his words) his automatic door had failed and the door had slipped of its tracks. He is an auto mechanic and his son an avid race car driver...they had stored spare wheels, tires, engine blocks, jacks and tools on plywood shelving, spanning the bottom chords. Everything across the width of the span over the double doors had bowed downwards from all the weight, causing the door tracks to spread apart. Not a cheap fix by any means.


  14. #14
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: New Construction garage roof trusses

    Quote Originally Posted by Ian Page View Post
    He is an auto mechanic and his son an avid race car driver...they had stored spare wheels, tires, engine blocks, jacks and tools on plywood shelving, spanning the bottom chords. Everything across the width of the span over the double doors had bowed downwards from all the weight, causing the door tracks to spread apart. Not a cheap fix by any means.
    He could have broken things with heavier trusses as heavier trusses would have let him store more in them.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  15. #15
    Join Date
    Mar 2007
    Location
    NoCal
    Posts
    261

    Default Re: New Construction garage roof trusses

    "It would seem to me that any heavy load stored in the attic of this garage would be a problem for that joint since there is no support under it."

    It seems to me that you are right...don't use it for storage.


  16. #16
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: New Construction garage roof trusses

    Quote Originally Posted by Chris Weekly View Post
    "It would seem to me that any heavy load stored in the attic of this garage would be a problem for that joint since there is no support under it."

    It seems to me that you are right...don't use it for storage.
    Don't use it for storage in excess of the storage it is designed for - it may very well be designed for 'storage', just not for storing race car wheels, tires, engines, transmissions, concrete blocks, bags of concrete mix, etc.

    Personal responsibility needs to be taken into account - store some 'normal' attic storage items and no problem, store the Hummer up there and, yeah, it will likely fail.

    The codes now call for higher load rated trusses to accommodate attic storage when the area and height meet specified requirements - but those higher rated trusses still do not take into account those 'unusual' things being stored in the attic.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  17. #17
    Join Date
    Mar 2007
    Location
    NoCal
    Posts
    261

    Default Re: New Construction garage roof trusses

    Right...so...the owner, tenant, occupant will abide by the engineered or maximum permissible load. Do they have a clue there is such a thing?
    Probably less knowledge of truss loads than the construction crew who stacked the trusses...and they were supposed to abide by the 114 page manual for installing trusses.

    "I doubt anyone I've seen installing trusses has ever looked at, much less actually read and understood the requirements for handling metal plate connected wood trusses:
    - http://support.sbcindustry.com/docs/...nfio8j0p9515d2"

    So when it comes to storage in the garage framing I suggest cardboard boxes or empty suitcases ...no car engine hoists, engine blocks or transmissions, or anything larger than a bread box.


  18. #18
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: New Construction garage roof trusses

    Chris,

    When someone lacks the common sense to NOT store really heavy items in the attic ... well ... you can't fix stupid.

    Sometimes stupid fixes itself, such as a redneck's last words ... 'Hey, Bubba, watch this ... '

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  19. #19
    Join Date
    Mar 2007
    Location
    NoCal
    Posts
    261

    Default Re: New Construction garage roof trusses

    Yup...
    I had to throw in the extra two dots on this message. It was too short otherwise. Brian does not want a senseless remark to go out on the Inspection News wire.


  20. #20
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: New Construction garage roof trusses

    On several occasions I have taken a look at what was stored in the open space above a garage and found engine blocks and transmissions.
    Generally, I'm surprised and say something like "Holy Smokes, there's an engine block up here!" to which the homeowner will reply "Yeah! You can't believe how hard it was to get it up there".

    I have never replied "Duh", but have seriously wanted to. As a result, I have a standard comment warning people about storing stuff in attic and above garages. As we all know, you can warn 'em, but who knows if they listen?

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  21. #21
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: New Construction garage roof trusses

    Quote Originally Posted by Gunnar Alquist View Post
    Generally, I'm surprised and say something like "Holy Smokes, there's an engine block up here!" to which the homeowner will reply "Yeah! You can't believe how hard it was to get it up there".
    I would probably respond with something like 'Yeah, there is probably a reason for it being hard to do ... like ... it shouldn't be done ... ' then turn and walk away shaking my head side-to-side and whispering to myself ... 'Stupid is as stupid does' ...

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  22. #22
    Join Date
    Mar 2007
    Location
    NoCal
    Posts
    261

    Default Re: New Construction garage roof trusses

    Quote Originally Posted by Gunnar Alquist View Post
    Generally, I'm surprised and say something like "Holy Smokes, there's an engine block up here!" to which the homeowner will reply "Yeah! You can't believe how hard it was to get it up there".
    Wow! You gotta laugh at some of the things people do.
    Well, getting it down may be easier...mattress on the garage slab and a heave ho.
    I often will ask the seller to move all the things in the attic so I can have access. Most just give me a goofy, confused look. Is this guy serious? Yeah, at least I asked in front of the buyer...limited inspection.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  23. #23
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: New Construction garage roof trusses

    Quote Originally Posted by Chris Weekly View Post
    I often will ask the seller to move all the things in the attic so I can have access. Most just give me a goofy, confused look. Is this guy serious? Yeah, at least I asked in front of the buyer...limited inspection.
    A good response with the attic shown in your photo is to the effect of 'Well, see that paper facing on the insulation ... (they nod that they see it) ... I need to see just how much of the attic has that exposed paper facing ... because NONE of that paper facing is allowed to be left exposed.'



    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  24. #24
    Join Date
    Mar 2007
    Location
    NoCal
    Posts
    261

    Default Re: New Construction garage roof trusses

    Yup...(again with the dot, dot, dot)
    anyway, sure. I told them about the insulation facing and will include a photo of the warning on the facing paper.

    - - - Updated - - -

    oh, and all that heavy storage - legal files filled to the brim, and lots of 'em, has caused the kitchen ceiling below this to bow under the weight with stress cracks in the drywall. No engine blocks that I could see.


  25. #25
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: New Construction garage roof trusses

    With a lot of paper stored, you really don't need an engine block, that's for sure.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  26. #26

    Default Re: New Construction garage roof trusses

    Roof trusses are generally intended to carry only the load of a dry wall or plaster ceiling and the weight of insulation commonly used in the area of manufacture. Unless specifically designed for storage nothing should be stored in the attic. That means no artificial Christmas trees, engine blocks or transmissions etc.

    - - - Updated - - -

    Roof trusses are generally intended to carry only the load of a dry wall or plaster ceiling and the weight of insulation commonly used in the area of manufacture. Unless specifically designed for storage nothing should be stored in the attic. That means no artificial Christmas trees, engine blocks or transmissions etc.


  27. #27
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: New Construction garage roof trusses

    Quote Originally Posted by Don Hawley View Post
    Roof trusses are generally intended to carry only the load of a dry wall or plaster ceiling and the weight of insulation commonly used in the area of manufacture. Unless specifically designed for storage nothing should be stored in the attic. That means no artificial Christmas trees, engine blocks or transmissions etc.
    Roof trusses which have storage space in them (some have space which permits storage, others do not have any practical usable space within the truss design) are typically required to be designed for storage at, as I recall, 40 psf.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •