Results 1 to 8 of 8
  1. #1
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,871

    Default Metal raceway as support for pool J box

    Im wondering where in this section does it specify only metal raceway as supports.

    (E) Raceway-Supported Enclosure, Without Devices,
    Luminaires, or Lampholders. An enclosure that does not
    contain a device(s), other than splicing devices, or supports
    a luminaire(s), a lampholder, or other equipment and is
    supported by entering raceways shall not exceed 1650 cm3
    (l00 in?) in size. It shall have threaded entries or identified
    hubs. It shall be supported by two or more conduits
    threaded wrenchtight into the enclosure or hubs. Each conduit
    shall be secured within 900 mm (3 ft) of the enclosure,
    or within 450 mm (18 in.) of the enclosure if all conduit
    entries are on the same side.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Metal raceway as support for pool J box

    Quote Originally Posted by Marc M View Post
    Im wondering where in this section does it specify only metal raceway as supports.
    It doesn't.

    That section calls for two conduits, the exception allows for one conduit and even the exception specifies IMC, RMC, EMT, (all the preceding being metal), and PVC, RTRC.

    The type of conduit would need to meet the requirements of the use, in this case, it would be emerging from grade and above 18 inches below grade, so the conduit would need to be RMC (Rigid Metal Conduit), IMC (Intermediate Metal Conduit), or Sch 80 PVC (nonmetallic Rigid Polyvinyl Chloride Conduit).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,871

    Default Re: Metal raceway as support for pool J box

    10 / 4..
    thanks


  4. #4
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Metal raceway as support for pool J box

    Since only metallic raceways are threaded you kind of need to read into the requirements.

    All answers based on unamended National Electrical codes.

  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Metal raceway as support for pool J box

    Quote Originally Posted by Jim Port View Post
    Since only metallic raceways are threaded you kind of need to read into the requirements.
    Threaded adapters are available for PVC, so we don't want to read too deeply into what is not there.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Metal raceway as support for pool J box

    Quote Originally Posted by Jerry Peck View Post
    Threaded adapters are available for PVC, so we don't want to read too deeply into what is not there.
    I know inspectors that will not accept them either as the raceway is not threaded. Also by extension, it is not wrench tight with a glued fitting.

    Now with that in mind, would you accept Carflex with a fitting to support a raceway?

    All answers based on unamended National Electrical codes.

  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Metal raceway as support for pool J box

    Quote Originally Posted by Jim Port View Post
    I know inspectors that will not accept them either as the raceway is not threaded. Also by extension, it is not wrench tight with a glued fitting.
    The threaded fitting is wrench tight.

    Now with that in mind, would you accept Carflex with a fitting to support a raceway?
    I hope you would not accept Carflex for that use as it is not approved to provide protection from physical damage or for protection of conductors emerging from grade (as related to the specific question and graphic submitted by the original poster), however, the code section referenced in the graphics is not specifically and only applicable to that one illustrated use/installation.

    So, going back to the code section, Carflex is not suitable for support of an enclosure anywhere.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,871

    Default Re: Metal raceway as support for pool J box

    Quote Originally Posted by Jim Port View Post
    Since only metallic raceways are threaded you kind of need to read into the requirements.
    crap..cant believe I missed that...
    Reading code is sort of like having to "read between the lines" with some women. Haven't master either yet..


Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •