Results 1 to 4 of 4
Thread: copper and natural gas
-
04-10-2016, 07:28 AM #1
copper and natural gas
Some jurisdictions in our area will not allow copper for use with natural gas. Can anyone shed some light on were to find a national code to reference, we currently call it out as a possible safety issue and leave it to the buyers and sellers to duke it out. What is everyone else doing?
Similar Threads:
-
04-10-2016, 08:30 AM #2
Re: copper and natural gas
From the IRC:
G2414.5.2 (403.5.2) Copper tubing.
Copper tubing shall comply with standard Type K or L of ASTM B 88 or ASTM B 280.
Copper and brass tubing shall not be used if the gas contains more than an average of 0.3 grains of hydrogen sulfide per 100 standard cubic feet of gas (0.7 milligrams per 100 liters).
-
04-10-2016, 02:38 PM #3
Re: copper and natural gas
Don,
The primary problem here is that home inspectors are generalists and there is some specific information that we may not know. JP points out the H2S requirements; however, unless you contact your gas supplier, you are not going to know what the local content is - and you cannot foresee if it will change sometime down the road. As a result, it is easiest to recommend it be changed out. Unless the gas supply for the whole house is plumbed with copper, the correction is straightforward.
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
04-11-2016, 12:24 PM #4
Re: copper and natural gas
Thanks guys
We were getting mixed messages and needed some clarification
Don Hawley
www.HawleyHomeInspectionsLLC.com



Reply With Quote