Results 1 to 10 of 10
Thread: Heat Pump?
-
04-24-2016, 05:38 PM #1
Heat Pump?
Freddie Mac foreclosure with exterior heat pump, York M # YHJD42S41S7A. Thermostat had settings for only heat and cool. When heat set, a high efficiency furnace provided heat, and on cool setting, the heat pump was operational but did not produce cold air. Wondering if this was a wrong install as this was installed after foreclosure process initiated. Also, can heat pump be wired only cooling?
Sidney Alstad
Similar Threads:
-
04-24-2016, 07:07 PM #2
Re: Heat Pump?
Sidney, sorry I do not do foreclosures.
1: Did the serial numbers on the compressor?
The year on manufacturing is 1979 2000 but the fourth letter, # YHJ(D)42S41S7A
does not match the literature on Building Intelligence Center.
Heat Pumps life expectancy is 15 years.
Hope that helps.
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
04-24-2016, 07:15 PM #3
-
04-24-2016, 07:40 PM #4
Re: Heat Pump?
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
04-24-2016, 07:49 PM #5
Re: Heat Pump?
I forgot to ask, was the thermostat set to emergency heat?
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
04-24-2016, 08:22 PM #6
Re: Heat Pump?
Sidney,
A heat pump is, basically, just an air conditioning system wit a reversing valve which reverses the direction of refrigerant flow: a) cooling uses the indoor coil as the evaporator coil and the outdoor coil as the condenser coil - this transfer heat from inside to outside; b) heating uses the indoor coil as the evaporator coil and the outdoor coil as the condenser coil - this transfers heat from outside to inside.
If the unit was wired incorrectly, the thermostat wired incorrect, an incorrect thermostat installed, etc, a heat pump could be wired to 'only heat' or 'only cool'.
Heat pumps typically also have a back up heat strip, thus the thermostat will have an emergency heat setting which allows just the heat strip to operate.
I may be possible to wire it so the emergency heat strip turns on when in cooling mode - which could produce nothing positive (no heating and no cooling).
-
04-25-2016, 03:41 AM #7
-
04-25-2016, 04:58 AM #8
Re: Heat Pump?
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
04-25-2016, 05:03 AM #9
Re: Heat Pump?
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
04-25-2016, 09:08 AM #10
Re: Heat Pump?
High efficiency heat, I am thinking gas heat. While there are dual fuel heat pumps, they will still have Emergency Heat setting on thermostat.
This could be just a gas pak standard HVAC unit. Heat and Cool on thermostat.
The fact that is wasn't getting cold air is another matter. Did compressor kick in?



Reply With Quote