    Default Remote panel rating question.

    Stacked condo / apartment.

    The breaker on the metering box is 100 amp.
    100 amp.JPG
    The remote panel is SIEMENS EQ24125 125 AMP MAX.
    e2.JPG

    The remote is oversized for the main disconnect or am I missing something?
    Well beside what everyone keeps on insisting.

    Similar Threads:
    Member Benefits1
    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  2. #2
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Remote panel rating question.

    Quote Originally Posted by ROBERT YOUNG View Post
    Stacked condo / apartment.

    The breaker on the metering box is 100 amp.
    100 amp.JPG
    The remote panel is SIEMENS EQ24125 125 AMP MAX.
    e2.JPG

    The remote is oversized for the main disconnect or am I missing something?
    Well beside what everyone keeps on insisting.
    Not a problem, it is a 100 amp service with 100 amp protection for everything down stream. Having more robust components than required is not a problem.

    If it were reversed, that would be different. Or if you have additional information that would indicate inadequate power for the unit.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  3. #3
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Remote panel rating question.

    I would just add this comment - Mark the submarine panel with "100 Amp Max." That is something we see here, takes 5 minutes and not much thought.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Remote panel rating question.

    Quote Originally Posted by John Kogel View Post
    I would just add this comment - Mark the submarine panel with "100 Amp Max." That is something we see here, takes 5 minutes and not much thought.
    That could really confuse people - the panel is rated 125 amp on the manufacturer's label inside and someone puts a "100 amp max" label on the outside of the panel?

    Better to have that label state "Protected by 100 amp breaker".

    That way you are not implying that the panel manufacturer does not know what they are doing.

    And if one is concerned that some might not understand that label, one could add this:
    Protected by 100 amp breaker
    (That means all youse id gonna git ta dis panel id 100 amp max)

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,078

    Default Re: Remote panel rating question.

    Quote Originally Posted by Jim Luttrall View Post
    Not a problem, it is a 100 amp service with 100 amp protection for everything down stream. Having more robust components than required is not a problem.

    If it were reversed, that would be different. Or if you have additional information that would indicate inadequate power for the unit.
    The 3 J's, Jim, Jerry and John, much thanks as usual.

    Service size: 100 amp.
    Remote panel: Siemens remote panel. 125 amp. MAX. - 120/240 VOLT. - AC/CA. - Single phase. - Three wires.