Results 1 to 13 of 13
    Sep 2007
    San Antonio TX
    Default How would you write this up
    How would you write this up.
    Richard Stanley's Avatar
    Richard Stanley Guest
    Default Re: How would you write this up
    Open knock outs in j-box and panel.
    debris in panel.
    Double lugged breakers - looks like.
    Can't tell - Are breakers rated for aluminum, Is wire size correct?
    Jesse R Reyes's Avatar
    Jesse R Reyes Guest
    Appears that there is a meter next to the panel. There should be a main breaker. The aluminum wire is blistering. Overload. The panel is in hazards conditions. Recommend that the panel be Ungraded and that an Electrical Contractor may further evaluations.
    Quote Originally Posted by Zibby Swieca View Post
    I would report; "This is a fire waiting to happen. Call an electrician now".
    Closer look:
    "Open knock outs in j-box ... "
    Non-weatherproof box and cover not rated for use outdoors and installed outdoors, also has open knock out - replace with weatherproof box and cover approved for use outdoors (i.e., in "wet locations").
    Is that asbestos cement siding shingles?
    Service equipment has melted insulation which indicates overheating, typically caused by loose connections.
    Service equipment currently has 5 main breakers and space for one more, make sure not to install two breakers in the remaining double pole main breaker location.
    Open knock outs in service equipment has allowed animals/birds to bring combustible debris into the enclosure, combustible debris is in contact with, or close proximity to, energized components - this could lead to fire or electrical shock. Open knock out into wall cavity allows animals/birds to enter into the wall cavity.
    What appears to be the grounding electrode conductor is bolted together - if this is the grounding electrode conductor this is not allowed until after the first grounding electrode,
    That will do for starters to get and electrical contractor out there to correct everything you listed, and everything they find, and everything they create while making corrections.
    Donald Merritt's Avatar
    Donald Merritt Guest
    Look for a dead bird or mouse.
    Georgetown, KY
    Breakers installed with "on" in the down position.
    I like Scott's but always find it necessary (in my own mind and in good reporting practices) to expound a little bit on "why" it's a fire hazard.
    James Duffin's Avatar
    James Duffin Guest
    It looks like a NEMA 3R box mounted sideways. It's made to be mounted verticle...not horizontal.
    Erby, James,
    The photo was just taken sideways. The box (enclosure) is installed vertically - look at the grain in the siding.
    I know, photos should always be taken with 'up' being 'up', or, when trying to fit more into the photo, rotating the photo before using it anywhere so that 'up' is 'up'.
    Don't forget "over-fusing!"
    Shannon Guinn's Avatar
    Shannon Guinn Guest
    I concur with Scott.
    Shannon Guinn Guest
    I also concur with Jerry.
