    Default Wth is this ?!?

    Hi guys just came across this and have never seen it before any help?! Is it ok this wire running through he wall I know cords aren't supposed to run under carpet or into walls but I don't know about this. Any help would be awesome thanks!!!

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: Wth is this ?!?

    Quote Originally Posted by Aaron Scheuerer View Post
    Hi guys just came across this and have never seen it before any help?! Is it ok this wire running through he wall I know cords aren't supposed to run under carpet or into walls but I don't know about this. Any help would be awesome thanks!!!
    Hi Aaron,

    Looks like a plug-in transformer. I seem to recall seeing some of these as a part of the phone system, but I don't know exactly what function they provide.

    Did you unplug it? There is typically information on the underside.

    What is the weird white polygon on the wall? Is that some kind of reflection from the flash?

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  3. #3
    Join Date
    Sep 2009
    Location
    Arnold, MD
    Posts
    37

    Default Re: Wth is this ?!?

    Transformer probably tied to alarm system somewhere nearby


  4. #4
    Join Date
    Mar 2016
    Location
    New Jersey
    Posts
    95

    Default Re: Wth is this ?!?

    Thanks a lot guys!!! Yea the white is an odd reflection from my camera. Should I suggest having this removed ?! No I didn't unplug it because it was screwed into the outlet and I didn't want to damage anything he house was in such piss poor shape


  5. #5
    Join Date
    Sep 2009
    Location
    Arnold, MD
    Posts
    37

    Default Re: Wth is this ?!?

    Definitely don't ever unplug these in case its in use. Its not a defect so no need write it up as one but It's worth excluding any low voltage systems like phones or alarms if you do not plan on testing that system.


  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Wth is this ?!?

    That looks to be the low voltage side, the same rules do not apply to low voltage.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Join Date
    Mar 2016
    Location
    New Jersey
    Posts
    95

    Default Re: Wth is this ?!?

    awesome thanks so much guys!!!


  8. #8
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Wth is this ?!?

    Sorry for the delayed response. I don't read IN as often.
    This is a transformer for an alarm system.
    Alarm system transformers are secured to the outlet by a screw so that it is not accidentally unplugged.
    The wire/ cable to the transformer is phone cable which is 24 ga wire. It is required to be wired with 22ga or better or 18ga fire rated if connected to fire alarm.
    It is allowed to pass through walls, floors, or ceilings unprotected.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  9. #9
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Wth is this ?!?

    That is not a cord. it is a cable. Aaron has given good information.

    All answers based on unamended National Electrical codes.

  10. #10
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Wth is this ?!?

    Quote Originally Posted by Jim Port View Post
    That is not a cord. it is a cable. Aaron has given good information.
    Sorry Jim,what is pictured is a cable.
    One or more insulated wires surrounded by an insulating jacket.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  11. #11
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Wth is this ?!?

    Quote Originally Posted by Rick Cantrell View Post
    Sorry Jim,what is pictured is a cable.
    One or more insulated wires surrounded by an insulating jacket.
    I agree Rick. Check my original post.

    All answers based on unamended National Electrical codes.

  12. #12
    Join Date
    Oct 2014
    Location
    Maryland, DC, and Northern Virginia, electrical only
    Posts
    453

    Default Re: Wth is this ?!?

    Quote Originally Posted by Aaron Scheuerer View Post
    Hi guys just came across this and have never seen it before any help?! Is it ok this wire running through he wall I know cords aren't supposed to run under carpet or into walls but I don't know about this. Any help would be awesome thanks!!!

    NEC
    Article 725 might be a place to start. There are tricky little requirements, I believe, such as firestopping chases that are burrowed up through fire barriers.