Results 1 to 4 of 4

Thread: receptacle type

  1. #1
    Join Date
    Jun 2008
    Location
    Maryland
    Posts
    1,097

    Default receptacle type

    What type of appliance would normally be used with this receptacle? It was installed for the location of a stackable washer / dryer. I'm not use to seeing this type for a dryer connection. I know it should at least be a 4 wire receptacle.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Dec 2007
    Location
    Osceola, AR
    Posts
    311

    Default Re: receptacle type

    Older 30 amp NEMA 6-30r, 3 wire receptacle. In the past commonly used as a receptacle for a clothes dryer.

    Alton Darty
    ATN Services, LLC
    www.arinspections.com

  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: receptacle type

    Depending on its physical size, it's probably a 30 amp 240 volt receptacle.

    No 4th wire was required for a dryer until the 1993/96 NEC.

    Did you check the breaker rating? If the breaker was a 30 amp, the receptacle is okay - however, if the breaker was a 50 amp the receptacle needs to be at least a 50 amp too.

    A stackable dryer may not need a neutral for the dryer as that may only supply the element, the controls may be supplied by the 120 volt circuit.

    To clarify, by "stackable" I am not referring to two separate units which may be "stacked" one on top of the other, I am referring to one appliance made together as one unit with the dryer (usually the dryer) above the washer.

    Last edited by Jerry Peck; 01-30-2017 at 06:47 AM. Reason: Added clarification
    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Jun 2008
    Location
    Maryland
    Posts
    1,097

    Default Re: receptacle type

    30 amp breaker.

    Thanks for the replies gentleman


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •