    "Upper siding is hardiplank. Bottom of hardiplank rests on a wood ledge that is sloped nicely. The wood ledge rests on top of the lower, stone siding wiith caulk between the interface joint."

    "1- Is the hardiplank be at least an 1/8 inch from the wood ledge?"

    I believe it requires a 1/4" space below the Hardieplank.

    "2- Is a flashing cap required between the wood ledge and the stone?"

    Is the stone adhered veneer or installed with an air space like regular brick veneer?

    If adhered veneer, it would be a good idea, but not sure that it would be "required".

    If installed as 'masonry veneer' (like brick veneer), then, yes, it would need a through wall flashing (in this case, a cap flashing) attached to the wall and turned up the wall, extending out and across the air space, extend to the edge of the stone, or to within 1/2" of the edge of the stone (with the intent being to drain/weep all the water from above out and over the masonry veneer).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Mike Huppi's Avatar
    Mike Huppi Guest

    Smile Re: Siding question

    Look at this and see if this answers your question. If not email me and I will send you the Hardi Trim installation guide it is too big for me to load on here.

    Attached Files Attached Files

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Siding question

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Mike Huppi's Avatar
    Mike Huppi Guest

    Default Re: Siding question

    Thats the one thanks

    I see this stuff installed wrong every day. I called out the clearance and flashing needed around penetrations on two different homes today.


  6. #6
    Martin lehman's Avatar
    Martin lehman Guest

    Default Re: Siding question

    I realize these installation instructions are for James Hardie siding, but are the majority of manufacured siding installations basically the same as these?? As far as fastening requirements, not using staples, caulking of joints, clearances, etc.??

    What is your experiance?

    BTW, I always recommend siding maintain 4" clearance above hardscape, not 2". Is the 4" requirement only for wood??


  7. #7
    Will Handley's Avatar
    Will Handley Guest

    Default Re: Siding question

    Quote Originally Posted by Martin lehman View Post
    I realize these installation instructions are for James Hardie siding, but are the majority of manufacured siding installations basically the same as these?? As far as fastening requirements, not using staples, caulking of joints, clearances, etc.??

    What is your experiance?

    BTW, I always recommend siding maintain 4" clearance above hardscape, not 2". Is the 4" requirement only for wood??
    I believe the deflection requirements are 4" from grade and 2" from paved or covered grade surfaces, ie; flat work.

    I call it out on anything than can be damaged by water/moisture conditions.