Results 1 to 12 of 12
Thread: To rail or not to rail...
04-15-2017, 03:08 PM #1
This must be the week with walking the line...
Stairs have a railing but it appears that it may meet the code (??) but not the spirit or intent??
Any advice?
Similar Threads:Jeff Zehnder - Home Inspector, Raleigh, NC
http://www.jjeffzehnder.com/
04-15-2017, 03:49 PM #2
Re: To rail or not to rail...
04-15-2017, 04:27 PM #3
Any other photos of it?
Is the handrail continuous around that corner, at the correct height, with the minimum clearance to the wall? That rail looks like it might meet the requirements of graspability: R311.7.8.3, see 1. for Type 1 handrails.
I From the photo, no, that handrail does not meet the spirit or intent of the code ... but it may very well meet the wording of the code.
I feel that a code inspector could reject that as the handrail is required for the full length of the stairs, and the minimum tread width is addressed in the stair width, and the tread width there is that last section of tread which is perpendicular to the wall it wraps around to, i.e, the stair where the handrail is does not meet the width requirements, and, the stair part which does meet the width requirements does not meet the handrail requirements. One of those finer points that many AHJ miss or don't grasp.
One thing I would put in my report is "that the handrail where it is, which is not where it should be, could very possibly lead to a fall down the stairs, and when that happens - DO NOT CALL ME - I am pointing that out to you RIGHT HERE".
04-15-2017, 04:42 PM #4
The fifth tread from the bottom does not meet the tread width requirement due to the clipped corner on that tread ????
Therefore that entire side of the stairs can not be used to meet code ???
04-15-2017, 07:18 PM #5
Handrails are required on stairwayy We all concur, IRC: The width of each landing shall not be less than the width of the stairway served. Every landing shall have a minimum dimension of 36 inches (914 mm) measured in the direction of travel. Handrail to be 34” Maximum height to be 38”. Measured from nose of stair treads. and 38 inches respectively, measured vertically from the nosing of the treads, shall be provided on at least one side of stairways with a total rise of 30'' or more.
By the looks of it, handrails are required on both sides.
04-16-2017, 08:12 AM #6
As always I appreciate everyone's input.
One of the underlying issues we face is even though we are not supposed to be code inspectors we are supposed to know code and also read the AHJ minds even when they are blank!
04-22-2017, 09:13 AM #7
I can't understand why they didn't choose to put it on the other side of the stairs.
04-23-2017, 08:52 AM #8
04-23-2017, 02:06 PM #9
The answer is easy - new home builder - a penny saved!
04-23-2017, 03:31 PM #10
04-23-2017, 05:26 PM #11
04-25-2017, 09:09 AM #12
Jerry, I agree with the large goose neck and drop the railing they installed was expensive.
After all the fuss the town (AHJ) came back out and decided that another rail was needed on the other side but they did not complain about the one short step.
Thanks again to everyone who gave thoughts and feed back