 Washington Post article: Home Inspectors can go too far.
		
 - 
	05-01-2017, 12:10 PM #2
 Re: Washington Post article: Home Inspectors can go too far.
		
Another article written by an expert realtor……go figure. In Florida, you are required to report on systems and components that are “at the end of their service lives”. Nothing “limits” the scope of a home inspection but the inspectors’ own knowledge:
61-30.801 Standards of Practice, General.
(1) Home inspections performed to these Standards of Practice are intended to provide the client with information regarding the overall condition of installed systems and components of the home based on observation of the visible and apparent condition of the structure and components at the time of the home inspection and to report on those systems and components inspected that, in the professional opinion of the inspector, are significantly deficient or at the end of their service lives. A home inspection does not include the prediction of future conditions.
(2) These standards shall not be construed as limiting the scope of the inspection process in those areas where the inspector is qualified and/or has special knowledge.
 - 
	05-01-2017, 01:23 PM #3
 Re: Washington Post article: Home Inspectors can go too far.
		In TN, the SOP does not address calling out things "near the end of their service lives". However, since I am an ASHI member, the ASHI SOP does require that we report on things that are "near the end of their service lives".
I think inspectors that do not report when things are near the end of their service lives, are doing a disservice to their clients. It can mean a significant expense to a new home owner if they have to replace a water heater, roof, and HVAC systems.
I have found that most consumers have no idea how long components of a home are supposed to last. As inspectors, we know perfectly well that just because something is working (or appears to be working fine), does not mean that its just fine.
Most people will buy a new pair of shoes before they wear holes thru the soles. They will also buy a new car before the old one dies on the side of the road. But, many of those same people believe that they should not replace any part of the house until it dies. Unless they want a fancy new faucet, or tile backsplash they saw on HGTV.
 - 
	05-01-2017, 01:39 PM #4
 Re: Washington Post article: Home Inspectors can go too far.
		Who put that in there? LOL InterNACHIcartoon2.gifthe ASHI SOP does require that we report on things that are "near the end of their service lives".
 - 
	05-01-2017, 02:50 PM #5
 Re: Washington Post article: Home Inspectors can go too far.
		One of the problems with the article is that the author rely does not know what they are talking about, but why should that stop them from blabbering on.
From the article; " “Some inspectors have been known to call out [for replacing] older furnaces” that are operating normally, he says. Why is that a problem? Because under widely recognized professional rules of conduct, inspectors are not supposed to “determine the life expectancy of any component or system.”"
Well I am not sure about WI, but most SOPS by State Lic. or Association or even a HI club say that they are not required to list "life expediences" if it is mentioned at all in the SOP.
Now the caveat is that he who says it has to be able to defend their opinion based on fact and not their ego.
I have always made it a point to inform a buyer of what they will have to be prepared for in the next 8 to 10 years of home ownership, both in items and their potiental replacement costs.
And like Horton:
"I meant what I said and I said what I meant. I will back it up faithfully one-hundred percent!”
Now to have them listen to me and understand rather than allow emotion rule the purchase is another matter all together.
Personally I believe that it should be a requirement, but that would require more experience
 - 
	05-01-2017, 03:09 PM #6
 Re: Washington Post article: Home Inspectors can go too far.
		Lisa,
As far as I know, its been in the ASHI SOP longer than you have been involved in the HI industry. Since ASHI is a Member driven Association, the SOP was designed, and updated by committees, and voted on by the Membership.
Is it your position that reporting on something that is near the end of it's service life a bad idea.?
It's really not that hard to get an estimated life for home components. There are widely recognized sources for this information. I'm guessing that even InterNACHI has this information somewhere in their databases, and available for their members, and general public. Please correct me if I am wrong, that InterNACHI does not provide estimated service life data.
If InterNACHI does in fact provide service life estimates for equipment, but does not include it in its SOP, then I have to ask, to what end are you providing the information?
If you do not currently provide service life estimates for equipment, I have to ask, why not? I would guess that most inspectors (that are worth their weight), would like this information (if they don't already have it).
 - 
	05-01-2017, 07:14 PM #7
 Re: Washington Post article: Home Inspectors can go too far.
		It's best to just give your clients this rather than trying to predict https://www.nachi.org/life-expectancy.htm
 - 
	05-01-2017, 07:19 PM #8
 Re: Washington Post article: Home Inspectors can go too far.
		InterNACHI in the news again https://therealdeal.com/2017/04/28/h...killer-report/
 - 
	05-01-2017, 07:41 PM #9
 Re: Washington Post article: Home Inspectors can go too far.
		So an inspector will tell a client the age of the HVAC equipment (as an example), and give them your document. Explain to me how that is any different than telling a client that the same equipment is nearing the end of its expected service life?
There is a huge difference between telling someone the average life of XYZ is 7 - 10 years, and this one is 14 years old, and telling someone that this XYZ will die within 6 months.
Please explain InterNACHI's position on inspectors telling clients about equipment nearing the end of its expected service life. Your initial post appears to infer that InterNachi thinks its a bad idea. If that is the case, then why are you providing information on service life for your inspectors to hand out?
A little clarification please?
 - 
	05-01-2017, 08:15 PM #10
 - 
	05-02-2017, 03:02 AM #11
 Re: Washington Post article: Home Inspectors can go too far.
		You guys still hammering away at the largest recognised certifying home inspection association in North America?
Being happy and freely helping others combined with Great Education is highly rewarded.
I thought you astute professionals would have learned by now.
Oh well. Best of luck with all your endeavors.
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
 - 
	05-02-2017, 03:28 AM #12
 Re: Washington Post article: Home Inspectors can go too far.
		Robert,
I'm just asking for clarification on InterNACHI's stand on the topic that Lisa started. Since you are an InterNACHI inspector, maybe you can shed light on the policy of telling clients when something is nearing the end of its expected life?
My SOP state that I must report on things when they are near the end of their expected life. From what I gather from the article Lisa posted, InterNACHI does not require inspectors to tell clients when something is near the end of its service life. In fact, if I read the article correctly, some InterNACHI inspectors feel that home inspectors should not tell clients when something is near the end of its service life.
I have never read InterNACHI's SOP, so I don't really know if its in there or not. Lisa then posted that inspectors should just give out the InterNACHI document about expected service life instead of trying to predict. It seems like a contradiction to me, but possibly I am missing something in the translation.
My question has nothing to do with home inspector association size, certifying capability, or even comparing associations.
Since Lisa has not, or can not, answer my question directly, maybe you can answer the question, since you are an actual practicing home inspector, and an astute professional yourself.
 - 
	05-02-2017, 03:41 AM #13
 Re: Washington Post article: Home Inspectors can go too far.
		Morning Jack. Hope you are in good health and spirits today.
As for the term, "near the end of their service lives." I concur about the importance of service life but will add, in some cases this can be difficult to nail down successfully.
I prefer two narratives, Vintage, Obsolete.
As to, "near the end of their service lives" the term serviceable has crept into soft inspection reports thus confusing the client.
Too bad.
So, Sad.
Were as the narrative vintage or obsolete express a more definitive view of the subject in question.
I concur.
I agree, but even new component can fail catastrophically without warning.
We walk a fine line providing due diligence for our clients Jack.
Let's take HVAC equipment as an example. The company is out of business.
The boiler still has 13 years of service life. Cast iron boiler.
My clients says, almost 80% of it usefull life has completed. I want to negotiate.
My reply, it was operating successfully and can continue doing so until it fails or becomes unserviceable.
Much thanks for your view on the subject,"near the end of their service lives." Always enjoy your posts.
I use CD, Carson Dunlop, life expectancy when required.
Best regards.
Robert
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
 - 
	05-02-2017, 05:42 AM #14
 Re: Washington Post article: Home Inspectors can go too far.
		
....LOL, I see some changes have been made since the last time that was posted. Service life is defined as the following:
(26) Service Life: Service life is the expected lifetime, or the acceptable period of use in service of a particular system or component. It is the time that any manufactured item can be expected to be “serviceable,” providing proper maintenance has taken place over the period concerned. Service life may vary from region to region, and inspection to inspection based on the home being inspected and the professional opinion and findings of the inspector.
Commenting on the "service life" of a system or component is not the same as "predicting future conditions"......not even close. Home inspection standards change from state to state, internachi's are far below our state standards and therefore irrelevant. In other words, teaching inspectors in our state to follow your standards would be a violation of rules for the profession.
If you knew anything about home inspections, you would know this.
 - 
	05-02-2017, 07:18 AM #15
 Re: Washington Post article: Home Inspectors can go too far.
		InterNACHI operates a free issue resolution service for home inspectors: Welcome to InterNACHI's Free Issue Resolution Service - InterNACHIPlease explain InterNACHI's position on inspectors telling clients about equipment nearing the end of its expected service life. Your initial post appears to infer that InterNachi thinks its a bad idea. If that is the case, then why are you providing information on service life for your inspectors to hand out?
A little clarification please?
Because like most humor, the cartoon I posted has some truth to it. Consumers often complain that a system or component didn't last quite as long as the inspector said it would. It's simply impossible to predict the exact day an air conditioner (for example) will fail. So to take the heat (and complaints) off of InterNACHI members, we recommend our members put that liability on InterNACHI instead by providing InterNACHI's Estimated Life Expectancy Chart. InterNACHI, being the world's largest inspection association and publisher of the document siphons off the complaints for our members.
The chart does two things at once: It peels off the liability from our members who would otherwise attempt the impossible, that being to accurately estimate life expectancy, while at the same time subliminally reminding homeowners that everything in their home (like human beings), is falling apart and will one day die.
 - 
	05-02-2017, 10:18 AM #16
 - 
	05-02-2017, 11:43 AM #17
 Re: Washington Post article: Home Inspectors can go too far.
		Tell it to the consumer who calls and says "My inspector said I had three more years left on my water heater and it died after only two years."
InterNACHI does upwards of 20,000 inspections a day, (yes, I said a day), so we hear it all.
 - 
	05-02-2017, 12:34 PM #18
 Re: Washington Post article: Home Inspectors can go too far.
		Lisa,
I'm sure you missed my last post with a question, so Ill post it again.
Thanks
So an inspector will tell a client the age of the HVAC equipment (as an example), and give them your document. Explain to me how that is any different than telling a client that the same equipment is nearing the end of its expected service life?
There is a huge difference between telling someone the average life of XYZ is 7 - 10 years, and this one is 14 years old, and telling someone that this XYZ will die within 6 months.
Please explain InterNACHI's position on inspectors telling clients about equipment nearing the end of its expected service life. Your initial post appears to infer that InterNachi thinks its a bad idea. If that is the case, then why are you providing information on service life for your inspectors to hand out?
A little clarification please?
 - 
	05-02-2017, 12:47 PM #19
 Re: Washington Post article: Home Inspectors can go too far.
		It does not matter how many or how few inspections are done IN A LIFETIME ... NO INSPECTOR IN THEIR RIGHT MIND should say:
Being as EVERYTHING (except a ticking time bomb clock) as a LIFE RANGE (in years, months, days, etc) ... and thus an anticipated life expectancy ... based on that LIFE RANGE ... and from the date of manufacture to the date it is at the time of the inspection, the POTENTIAL REMAINING LIFE can be calculated:
 Originally Posted by Lisa Endza
					
				
LIFE RANGE (in years) 5-10
AGE (in years) 7 years old (based on date of manufacture)
POTENTIAL REMAINING LIFE (in years) 0-5
Formula to calculate POTENTIAL REMAINING LIFE
LIFE RANGE minus AGE equals POTENTIAL REMAINING LIFE
5-10 minus 7 equals 0-5
I certainly hope that NO ONE, not any school, not any association, not any organization, not any business, teaches or advises inspectors to give a concise and drop dead date of remaining life.
Let's see, that was manufactured on 01-01-2010, it has a life of 11 years, 4 months and 3 days, that mean it will stop working on 05-04-2021 ... being as this is 05-02-2017, that item will last another 4 years and 2 days ... really?
Is Lisa/Nick/whomever serious?
Even the ticking clock on the time bomb could fail and not cause the bomb to explode, allowing the ticking clock to either stop ticking or keep on ticking ... with nothing happening either way.
- - - Updated - - -
I wanted to point this out separately ...
Really?
I didn't know that all the inspectors were employees of yours ... I bet the IRS would love to find that out.
 - 
	05-02-2017, 01:02 PM #20
 - 
	05-02-2017, 03:04 PM #21
 Re: Washington Post article: Home Inspectors can go too far.
		For some homebuyers, yes.Can this really be that difficult to understand?
Neither are most homebuyers.Oh yeah, I keep forgetting.....you're not an inspector.
 - 
	05-02-2017, 03:28 PM #22
 Re: Washington Post article: Home Inspectors can go too far.
		Remember - Lisa/Nicky/whoever stops by here frequently and 'goes fishing' ... usually ... one of us takes the bait ... and the struggle begins ... even though they are never able to reel one all the way in, I'm sure they enjoy the struggle.
Occasionally they 'seed the pond' and it looks like they catch one ... when they reel it in ... the rest recognize the plastic fish on the hook.

 - 
	05-03-2017, 09:28 AM #23
 Re: Washington Post article: Home Inspectors can go too far.
		Jerry,
They seem to have teased you with the bait and made you looooook.
The hand out is more than likely just their way to prevent someone with little experience and/or a club inflated ego from making a statement that will back the HI into a corner. They want to leave the buyer making the inference of useful like rather than the HI saying it will last x years. Marketing and protection of HI. When you create a false sense of knowledge and experience you have to provide caveats to keep them from self inflected injury (lawsuits).
And yes I admit I am teased to the surface by the imitation bait. Now I must also admit I will wait to see if someone else takes the bait before me, while hoping that the fishermon will be ignored and just go away. Aaaaaaaah life's little hopes and dreams.
 - 
	05-03-2017, 01:17 PM #24
 Re: Washington Post article: Home Inspectors can go too far.
		Somewhat correct. InterNACHI, which is a third-party to the transaction and which is the largest home inspection association in the world, publishes that chart so that home inspectors aren't backed into a corner by consumers who not only expect that a home inspector has the magic ability to determine how long a system and component will last, but also idiotically relies on those guesstimates and then unconscionably tries to hold the home inspector responsible for systems and components that fail any earlier.
Push that liability off on us. We're good at handling it: Welcome to InterNACHI's Free Issue Resolution Service - InterNACHI
 - 
	05-03-2017, 02:11 PM #25
 Re: Washington Post article: Home Inspectors can go too far.
		Lisa,
I'm still waiting for your response regarding InterNACHI's policy on inspectors telling their clients about something nearing the end of its expected life.
It should not be that hard. You seem to have document after document that you have available for your members. Surely, there should be a position statement regarding this. Or is the InterNACHI inspector quoted in the article acting as the InterNACHI spokesman on this matter?
Thanks for your prompt response.
 - 
	05-03-2017, 03:23 PM #26
 Re: Washington Post article: Home Inspectors can go too far.
		Hey Jerry, did you read through the Florida specific life expectancy chart? This is some good stuff......concrete tile roof coverings are good for 80+ years.
https://www.nachi.org/florida-life-expectancy.htm
This is by far and away the best comment: "Florida inspectors are subject to state requirements for reporting deficiencies based on expected service life"
Lisa, I think we found your issue......lol
 - 
	05-03-2017, 04:38 PM #27
 Re: Washington Post article: Home Inspectors can go too far.
		I like "Boiler 40 (if installed)", what if the boiler is not installed? What is life if not installed?
Then there is the typical question of where did they come up with this chart. What is it based on and by what standards. Again absolutely no siting of any source or qualifications listed. Typical of poor writing and presentation of supposed facts. Just saying something does not make it so, yet they think it does.
 - 
	05-03-2017, 07:24 PM #28
 Re: Washington Post article: Home Inspectors can go too far.
		For many models, the shelf life of the boiler is less than its installed life because the gaskets dry out.I like "Boiler 40 (if installed)", what if the boiler is not installed? What is life if not installed?
 - 
	05-03-2017, 09:52 PM #29
 Re: Washington Post article: Home Inspectors can go too far.
		Jack, what about Carson Dunlop LIFE CYCLES & COST?
As you express to Lesa, and as a home inspector yourself, what do you not understand?
IMO, these two outstanding individual, Alain Carson and Bob Dunlop, known by "The Home Inspection Team", I suspect for SEO marketing juice, defined how to survey/inspect real estate property more than 37 or 38 years ago.
Most others somewhat infringed on copywriters and invented their own report systems doing so.
Are CD's LIFE CYCLES & COST not realistic?
Should CD trained home inspectors, as well as other certified home inspectors using the HORIZON reporting software not post age, life expectancy and costs?
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
 - 
	05-04-2017, 04:28 AM #30
 Re: Washington Post article: Home Inspectors can go too far.
		
 - 
	05-04-2017, 06:30 AM #31
 Re: Washington Post article: Home Inspectors can go too far.
		If they are 37 years old, they probably aren't.Alain Carson and Bob Dunlop, known by "The Home Inspection Team", I suspect for SEO marketing juice, defined how to survey/inspect real estate property more than 37 or 38 years ago.
Most others somewhat infringed on copywriters and invented their own report systems doing so.
Are CD's LIFE CYCLES & COST not realistic?
 - 
	05-04-2017, 08:11 AM #32
 Re: Washington Post article: Home Inspectors can go too far.
		I try to find install or manufacture dates on as many systems as I can and include them in the report, and I do note if they are older, but always as a comment, and if they operated at the time of inspection. Calling for a working hot water tank to be replaced simply because it's more than 10 years old is over the top in my opinion. And I am am just happy some of the houses I inspect have paint on the walls, I could not care less what color it is.
- - - Updated - - -
I try to find install or manufacture dates on as many systems as I can and include them in the report, and I do note if they are older, but always as a comment, and if they operated at the time of inspection. Calling for a working hot water tank to be replaced simply because it's more than 10 years old is over the top in my opinion. And I am am just happy some of the houses I inspect have paint on the walls, I could not care less what color it is.
 - 
	05-04-2017, 08:19 AM #33
 Re: Washington Post article: Home Inspectors can go too far.
		Correct. It would be like declaring a healthy 80-year old man to be dead.Calling for a working hot water tank to be replaced simply because it's more than 10 years old is over the top in my opinion.
 - 
	05-04-2017, 09:21 AM #34
 Re: Washington Post article: Home Inspectors can go too far.
		Bad analogy ... nonetheless, though, even us humans have 'typical life expectancy' times ... which vary greatly based on where the human lives.
A better analogy would be that the 25 year old water heater has a typical life of 10 years, recommend replacement (or be prepared for failure and/or leakage and the resulting damage).
The "healthy" 80 year old man may be near failure and/or "already leaking" ... the difference is that there *is no replacement available* for the 80 year old man ... there is for the water heater.
 - 
	05-04-2017, 09:26 AM #35
 Re: Washington Post article: Home Inspectors can go too far.
		Good post Jerry.
 - 
	05-04-2017, 09:48 AM #36
 - 
	05-04-2017, 11:40 AM #37
 Re: Washington Post article: Home Inspectors can go too far.
		Gaskets dry out when not in use. Note the right column of the chart in the attached PDF which lists the shelf life of rubber gaskets being substantially less then the life expectancy of a boiler in use: http://www.shurjoint.com/Files/Chn/D...0Life-RevB.pdf
 - 
	05-04-2017, 11:57 AM #38
 Re: Washington Post article: Home Inspectors can go too far.
		
 - 
	05-04-2017, 11:58 AM #39
 Re: Washington Post article: Home Inspectors can go too far.
		Our Life Expectancy Chart doesn't distinguish between all the different boiler manufacturers, nor the different models, nor the different materials used in each of them, nor the manufacturers of those materials. It doesn't even list the shelf life of them (it assumes and states "installed" life).
If we did all that for every system and every component, the chart would be 1,000 pages long and not very useful to our members.
https://www.nachi.org/life-expectancy.htm has two very specific purposes: One has to do with reducing liability for our members and the other has to do with helping our members' clients realize that everything in their home will one day need to be repaired or replaced. It serves those two purposes well.
 - 
	05-04-2017, 12:04 PM #40
 - 
	05-04-2017, 12:17 PM #41
 Re: Washington Post article: Home Inspectors can go too far.
		First off, does it matter? They all have shelf lifes that are less then the life expectancy of an installed boiler. You asked why we noted that we were referring to "installed" boilers. That's why. Some installed boilers have an installed life expectancy that is greater than the shelf-life of their own parts.
Second, our chart doesn't provide that info for reasons I explained.
Third, the purpose of our chart is not to provide outrageously-detailed information about materials used in all the various models by all the various manufacturers. It's designed to help InterNACHI members accomplish two things, both have much to do with reducing liability. InterNACHI owns 1/2 of its E&O insurance program and this is one of the ways it keeps claims down. Listing or even knowing "which of the 7 types of rubber gasket" is used in each model of each boiler does not help keep claims down and would likely detract the recipient from grasping the chart's intended underlying theme.
Last edited by Lisa Endza; 05-04-2017 at 12:22 PM.
 - 
	05-04-2017, 12:23 PM #42
 - 
	05-04-2017, 12:30 PM #43
 Re: Washington Post article: Home Inspectors can go too far.
		I don't know. All I can tell you is what is in the chart, the goal of the chart, and whether an addition to the chart would increase or decrease the the intended underlying theme of the chart which is necessary to achieve the chart's goal of helping InterNACHI members.
If you want to know what parts of a boiler have a shelf life that are less than the installed life expectancy of that boiler, I suggest you contact the manufacturer. I can give you some contacts if you need them.
 - 
	05-04-2017, 12:35 PM #44
 Re: Washington Post article: Home Inspectors can go too far.
		
None of them are approved for use with a "boiler" Lisa. A boiler is a steam pressure vessel, the gaskets would need to be rated for upwards of 1200 degrees.
http://www.henniggasket.com/boiler-gaskets-seals
All kidding aside, you need to understand that the people around you may not be as educated as you think. As you have said before, you are not really an association of inspectors.
 - 
	05-04-2017, 01:20 PM #45
 Re: Washington Post article: Home Inspectors can go too far.
		And the gasket manufacturer you linked to makes all the gaskets and rubber parts to all boilers?
 - 
	05-04-2017, 01:23 PM #46
 - 
	05-04-2017, 01:26 PM #47
 Re: Washington Post article: Home Inspectors can go too far.
		So you are 100% certain that the shelf life of every part of every boiler is no less than its service life?
 - 
	05-04-2017, 01:33 PM #48
 Re: Washington Post article: Home Inspectors can go too far.
		
I don't inspect boilers Lisa, haven't seen one in south Florida. I also don't wonder around home Depot inspecting uninstalled boilers. But I do know a thing or two about them, apparently more than you.
The chart you provided doesn't even have materials that are approved for use with a boiler....yet you tried anyway and were caught in a lie.
Have a nice day.......
 - 
	05-04-2017, 01:41 PM #49
 Re: Washington Post article: Home Inspectors can go too far.
		I gathered that much. So you aren't willing to state whether the shelf life of any part of a residential hydronic boiler is less than the boiler's installed life expectancy?I don't inspect boilers Lisa, haven't seen one in south Florida.
 - 
	05-04-2017, 02:00 PM #50
 Re: Washington Post article: Home Inspectors can go too far.
		
 - 
	05-04-2017, 02:06 PM #51
 Re: Washington Post article: Home Inspectors can go too far.
		Not true. Don't try to wiggle out.
There are no variables if you are stating that no part of a boiler has a shelf life less than the installed life expectancy of that boiler.
There are only variables if you believe the reverse, that there could be parts of a boiler that have shelf lifes less than the installed life expectancy of the boiler.
Since you believe there are variables, you must believe the latter, in which case you agree with InterNACHI.
 - 
	05-04-2017, 02:27 PM #52
 - 
	05-04-2017, 02:59 PM #53
 Re: Washington Post article: Home Inspectors can go too far.
		You know, it’s almost like you just can’t accept anything unless it comes from your group. “Service life” varies from region to region and even inspection to inspection based on the home being inspected and the professional opinion and findings of the inspector. All “variables”Lisa.
Case in point, a shingle roof covering installed in north Florida may last 4-6 years longer than the same exact roof covering installed in south Florida. “life expectancy” is not a one-shoe-fits-all process as you have implied. There are “variables”…….I don’t know why this is so hard to understand.
It’s like you create something based on nothing, then try to make the nothing something so you can feel like you accomplished something. Take a step back and consult the experts Lisa, not those who keep telling you they are.
 - 
	05-04-2017, 03:02 PM #54
 Re: Washington Post article: Home Inspectors can go too far.
		For some systems and components. Not for most others.“Service life” varies from region to region
You could actually have a chart for every region, every system/component manufacturer, every installation practice, every level of usage, etc.
But again, that wouldn't affect the intended underlying purpose of the chart. Remember, the chart has two purposes, both have to do with lessening InterNACHI member liability.
It's not a chart to look up exactly how long your water heater will last, because no chart can tell you that about your particular water heater.
 - 
	05-04-2017, 04:28 PM #55
 Re: Washington Post article: Home Inspectors can go too far.
		Lisa, Why is it you will answer/argue post after post, yet not answer a direct question?
I asked a question that you should be able to answer within seconds. InterNACHI, I would hope, has policy and procedures documented.
Could you please share the InterNACHI policy for inspectors telling their clients about the expected life of equipment. On one hand you are handing out a document that has expected life of various components, but in the article, there is an InterNACHI inspector that appears to be claiming that InterNACHI policy is to NOT tell clients about expected life.
Is Walter Fish the Official InterNACI spokesman on SOP and Policy and Procedures? The article certainly makes it look like he is speaking for InterNACHI when he says that inspectors have no business telling clients about expected service life of equipment. Perhaps he is not aware of the document where you are giving out the expected life of various components.
If he is giving misinformation about InterNACHI SOP and P&P's, then you may want to advise him not to speak to the press as a representative of InterNACHI. If he is the Official Spokesman for InterNACHI, then maybe he can come on this forum and answer this question.
Please clarify! It shouldn't be that hard.
Last edited by Jack Feldmann; 05-04-2017 at 04:37 PM.
 - 
	05-04-2017, 07:01 PM #56
 Re: Washington Post article: Home Inspectors can go too far.
		Our SOP does not require members to do it: 2.1 - VIII of Home Inspection Standards of Practice - InterNACHICould you please share the InterNACHI policy for inspectors telling their clients about the expected life of equipment.
The reason InterNACHI members should hand out the chart is to emphasize to their client that they are NOT predicting the life expectancy of one of the PARTICULAR systems or components of the home they inspected, but instead providing a pre-authored, pre-printed chart that is clearly NOT referring to any particular system or component of the home that was inspected.
We've been at this for many years and this is the only way we've found that doesn't cause the consumer to later blame the home inspector, should something fail earlier than expected.
Click on image: InterNACHIcartoon2.gif
Last edited by Lisa Endza; 05-04-2017 at 07:16 PM.
 - 
	05-05-2017, 06:51 AM #57
 Re: Washington Post article: Home Inspectors can go too far.
		Nick told me he hasn't performed a home inspection "in 20 years". I took a screen shot of the statement if you would like to see it.
You are not an inspector of any kind Lisa, you haven't the faintest idea what you are talking about. You are parroting what another person tells you while completely ignoring those who are experts in the profession. You can not be taught or educated in any way in the profession because you have no experience to discern what is and isn't truth.
 - 
	05-05-2017, 07:08 AM #58
 Re: Washington Post article: Home Inspectors can go too far.
		Note my title at InterNACHI. I can take a screenshot from Good people working every day to help your inspection business succeed. - InterNACHI if you would like to see it.
My job is to find the answers to your questions and relay them to you.
As for Nick not doing having performed a home inspection in 20 years, I confirmed you are correct. He only does commercial inspections these days.
 - 
	05-05-2017, 07:24 AM #59
 Re: Washington Post article: Home Inspectors can go too far.
		
LOL........
You are not an inspector of any kind Lisa, you haven't the faintest idea what you are talking about. You are parroting what another person tells you while completely ignoring those who are experts in the profession. You can not be taught or educated in any way in the profession because you have no experience to discern what is and isn't truth.
 - 
	05-05-2017, 07:30 AM #60
 Re: Washington Post article: Home Inspectors can go too far.
		
Your entire association is this way. I constantly supply accurate and verifiable information to your inspectors who can't seem to grasp it. All they do is resist any information that contradicts what they are currently doing. You can't learn....they can't learn....you could tell them and show them, they just continue doing what they were doing.
And what's worse is that you association has zero checks and balances.....a 4 member board that nobody knows what they are doing. Bad inspections are actually rewarded in your association.
What is it with you that you can't process information?
 - 
	05-05-2017, 08:45 AM #61
 Re: Washington Post article: Home Inspectors can go too far.
		I've read some of the responses to your posts on InterNACHI's message board. Why do so many claim you don't know what you are talking about, if you actually do?
 - 
	05-05-2017, 09:58 AM #62
 Re: Washington Post article: Home Inspectors can go too far.
		
"Your entire association is this way. I constantly supply accurate and verifiable information to your inspectors who can't seem to grasp it. All they do is resist any information that contradicts what they are currently doing. You can't learn....they can't learn....you could tell them and show them, they just continue doing what they were doing."
 - 
	05-05-2017, 10:13 AM #63
 Re: Washington Post article: Home Inspectors can go too far.
		And how's that working out for us?
"Your entire association is this way. .... they just continue doing what they were doing."
 - 
	05-05-2017, 10:24 AM #64
 Re: Washington Post article: Home Inspectors can go too far.
		
 - 
	05-05-2017, 01:08 PM #65
 Re: Washington Post article: Home Inspectors can go too far.
		Thanks for posting your response Lisa.
If I read this all correctly, InterNACHI SOP tells inspectors not to comment on expected life, yet provide a document that lists the expected life of components, and encourage your inspectors to give it to their clients.
This appears to me to be a huge contradiction. If I was a client, and received a document that called out an expected life of a gas furnace (as an example), and my house had a gas furnace, and my inspector told me how old it was (most inspectors make a note of equipment age, or include a photo of the label), I could easily do the math an determine something was at the end of its life.
While my inspector may not have directly told me my furnace was near the end of its expected life, he or she certainly gave me all the information needed to make that conclusion.
So, is the inspector violating the InterNACHI SOP's by giving out the document, or in fact telling the client about expected life, without actually telling them? I'm very confused about INterNACHI's policy on this.
Could you elaborate on this policy?
 


						
					
				
				
				
					