Point of attachment for service-drop conductors
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
05-18-2017, 07:27 AM #2
Re: Point of attachment for service-drop conductors
First photo:
- No flashing where mast penetrates roof.
Second photo:
- Neutral (grounded conductor) coming out of mast/weather head to overhead service drop appears smaller than other conductors, looks to be a lot smaller.
- Minimum height of lowest conductor (including drip loop) above the roof is 18"
- Maximum roof crossed is 4'.
- Maximum conductor length crossing roof is 6' (allows for diagonal length increase over the 4 foot roof area being crossed).
- Roof area being crossed is the overhang only (mast is on exterior wall, going up on the outside of the exterior wall).
Those should work for starters in those photos.
-
05-19-2017, 01:48 AM #3
Re: Point of attachment for service-drop conductors
Mast boot flashing is covered.
Modified roof was poorly applied. Amateur mistakes throughout.
Thanks for drip-loop/roof deck height/clearance requirements.
I will review the neutral.
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
07-07-2017, 05:10 PM #4
Re: Point of attachment for service-drop conductors
If that's a service feed ahead of the meter, you would need to check the utility's requirements--the NEC doesn't govern them.
-
07-07-2017, 05:52 PM #5
Re: Point of attachment for service-drop conductors
-
07-08-2017, 01:26 AM #6
Re: Point of attachment for service-drop conductors
Reported.
Second photo:
If you look at the feed and SEC neutral gauge at wire nut, the are the same.
Covered.
<48 inches.
<72"
Thanks Jerry.