Secondary Panel Issue ?
Does the AKA sub-panel secondary panel still require the neutral and grounds be separated even when the panel its mounted up against to main service panel ???
Similar Threads:
-
11-29-2017, 05:20 PM #2
Re: Secondary Panel Issue ?
Yes.
Says I need at least 5 characters ... "Yes." is only four ...
- Charlie Chaplin
- Joe E Brown
- Buster Keaton
- Harold Lloyd
- Groucho Marx
-
11-29-2017, 05:22 PM #3
Re: Secondary Panel Issue ?
[QUOTE=Jerry Peck;276922]Yes.
Says I need at least 5 characters ... "Yes." is only four ...
- Charlie Chaplin
- Joe E Brown
- Buster Keaton
- Harold Lloyd
- Groucho Marx[/Q
I like It, Thank you
-
11-29-2017, 05:26 PM #4
Re: Secondary Panel Issue ?
Wait, you're not going to give him the whole "Service Equipment vs. Panel" lecture.
Ok, fine.
Sam,
There is no "main panel" in the NEC. There is "service equipment". This is where the main disconnect lives and the only place (well, except at the transformer) where grounded (neutral) and equipment grounding conductors are bonded together. Everywhere else, they are required to be isolated.
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
11-29-2017, 05:29 PM #5
-
11-29-2017, 06:23 PM #6
Re: Secondary Panel Issue ?
Actually, I did give you a break.
This is what you said:
Gunnar was simply pointing out what I usually do - that there are only two types of electrical panels:
1) "service equipment" panels
2) 'other than service equipment' panels.
And then Gunnar pointed out that the neutral is only bonded to ground at "service equipment" panels.
My short "Yes." was because you were asking about the electrical panel which was 'next to' the "service equipment" panel ... meaning that the panel in question "was not" THE "service equipment" panel ... but you insisted on calling it by a term you should forget.
If you had forgotten that term, then you would think in terms of "service equipment" and "NOT service equipment" ... and likely would have recognized that the neutral is only bonded to ground in "service equipment" panels ... thereby answering your own question while taking the photos ... "NOT service equipment" means the "neutral is NOT bonded to ground".
-
11-29-2017, 07:33 PM #7
-
11-30-2017, 08:33 AM #8
Re: Secondary Panel Issue ?
I love these discussions!
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
11-30-2017, 08:36 AM #9
Re: Secondary Panel Issue ?
Who's on second!
www.1stproinspection.com
Certified Master Inspector
Like Us On Facebook https://www.facebook.com/1stproinspection/
-
11-30-2017, 12:37 PM #10
Re: Secondary Panel Issue ?
What. ?
Bookmarks