    Default Additional venting for water heater required?

    I moved a gas water heater outside of the house into a newly constructed closet = slab floor, framed, roof, etc. The metal utility door is vented (top to bottom). Am I also required to have an additional vent on the structure or running from the top of the water heater to the outside of the structure? OR is the vented door enough? This is in AZ. Thank you.

    Similar Threads:
    Member Benefits1

  2. #2
    Join Date
    Apr 2013
    Location
    High Springs, Florida
    Posts
    174

    Default Re: Additional venting for water heater required?

    Read this...
    https://codes.iccsafe.org/public/doc...rt-vi-fuel-gas

    Quote Originally Posted by Sonia Carver View Post
    I moved a gas water heater outside of the house into a newly constructed closet = slab floor, framed, roof, etc. The metal utility door is vented (top to bottom). Am I also required to have an additional vent on the structure or running from the top of the water heater to the outside of the structure? OR is the vented door enough? This is in AZ. Thank you.



    www.1stproinspection.com

    Certified Master Inspector
    Like Us On Facebook
    https://www.facebook.com/1stproinspection/

  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Additional venting for water heater required?

    Quote Originally Posted by Sonia Carver View Post
    I moved a gas water heater outside of the house into a newly constructed closet = slab floor, framed, roof, etc. The metal utility door is vented (top to bottom).
    That 'venting' is for "combustion air".

    Am I also required to have an additional vent on the structure or running from the top of the water heater to the outside of the structure? OR is the vented door enough? This is in AZ. Thank you.
    Yes, you need the "vent" from the draft hood, with a minimum 1 foot rise before an elbow to go out a wall, or go vertical through the roof. This vent is for combustion by-products.

    It should all be shown in the manufacturer's installation instructions which came with the water heater ... you did keep the installation instructions, and you are following them, right?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Jan 2018
    Location
    Arizona
    Posts
    2

    Default Re: Additional venting for water heater required?

    Thank you. Very helpful! Water heater was not new* I just had it moved.


    Quote Originally Posted by Jerry Peck View Post
    That 'venting' is for "combustion air".



    Yes, you need the "vent" from the draft hood, with a minimum 1 foot rise before an elbow to go out a wall, or go vertical through the roof. This vent is for combustion by-products.

    It should all be shown in the manufacturer's installation instructions which came with the water heater ... you did keep the installation instructions, and you are following them, right?



  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Additional venting for water heater required?

    Quote Originally Posted by Sonia Carver View Post
    Thank you. Very helpful! Water heater was not new* I just had it moved.
    Search the Internet for the manufacturer and model number, if the water heater is new enough to be moved then you should be able to find the installation instructions.

    Most water heaters I've seen in the last 30 years have a plastic sleeve stuck to the side with the instructions in it, plumbers rarely look at the instructions (which explains why so many are installed incorrectly - plumbers already "know" how to install a water heater).

    Rarely do home owners know the instructions are there, and fewer remove the instructions.