    Default Wiring hanging from joists

    2006 build. I thought you needed a 1X6 to attach wiring to floor joists in this manner. Never seen this type wiring in 20 years of inspecting.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: Wiring hanging from joists

    As is, the installation doesn't pass muster. If, however, a ceiling is installed, the cables fastened to the bottom of the joists might be OK. The exact code wording says that the joists have to be drilled or running boards used in an unfinished basement, and exactly what constitutes a finished basement is open to interpretation.

    Occam's eraser: The philosophical principle that even the simplest solution is bound to have something wrong with it.

  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Wiring hanging from joists

    The CSST bond connection is incorrect too.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    May 2009
    Location
    New Jersey
    Posts
    90

    Default Re: Wiring hanging from joists

    Jerry,
    There is a grounding clamp and wire on the black gas piping where the piping exists the interior foundation wall. I don't know why an additional clamp was installed on the csst piping itself. The joint in the ground wire is soldered.


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Wiring hanging from joists

    Quote Originally Posted by Richard Roshak View Post
    I don't know why an additional clamp was installed on the csst piping itself.
    Richard,

    While it's good that it was "also" properly bonded, but still not good that there is a clamp on the CSST itself. That should be removed.