Results 1 to 6 of 6
Thread: TPR valve pipe termination
-
04-24-2018, 07:17 AM #1
TPR valve pipe termination
Came across this water heater the other day. No drain pan, but I believe it's grandfathered in and not required. But I am confused about how the TPR relief is terminated. Shouldn't there be an air gap of at least 1 1/2 in (3/4 in. cpvc pipe) from the floor? This pipe terminates into the unfinished crawl space under the house. Is this allowed?
Similar Threads:
-
04-24-2018, 07:49 AM #2
Re: TPR valve pipe termination
UPC 608.5 Relief valves located inside a building shall be provided with a drain, not smaller than the relief valve outlet, of galvanized steel, hard drawn copper piping and fittings, CPVC, or listed relief valve drain tube with fittings which will not reduce the internal bore of the pipe or tubing (straight lengths as opposed to coils) and shall extend from the valve to the outside of the building with the end of the pipe not more than two (2) feet (610 mm) nor less than six (6) inches (152 mm) above the ground or the flood level of the area receiving the discharge and pointing downward. Such drains may terminate at other approved locations. No part of such drain pipe shall be trapped or subject to freezing. The terminal end of the drain pipe shall not be threaded.
And.....
504.6 Requirements for discharge piping.
The discharge
piping serving a pressure relief valve, temperature relief valve
or combination thereof shall:
1. Not be directly connected to the drainage system.
2. Discharge through an air gap located in the same room
as the water heater.
3. Not be smaller than the diameter of the outlet of the
valve served and shall discharge full size to the air gap.
4. Serve a single relief device and shall not connect to piping
serving any other relief device or equipment.
5. Discharge to the floor, to an indirect waste receptor or
to the outdoors. Where discharging to the outdoors in
areas subject to freezing, discharge piping shall be first
piped to an indirect waste receptor through an air gap
located in a conditioned area.
6. Discharge in a manner that does not cause personal
injury or structural damage.
7. Discharge to a termination point that is readily observable
by the building occupants.
8. Not be trapped.
9. Be installed so as to flow by gravity.
10. Not terminate more than 6 inches (152 mm) above the
floor or waste receptor.
11. Not have a threaded connection at the end of such piping.
www.1stproinspection.com
Certified Master Inspector
Like Us On Facebook https://www.facebook.com/1stproinspection/
-
04-24-2018, 10:19 AM #3
Re: TPR valve pipe termination
Thanks Roy for posting the code. If I'm reading it right, it's in violation of #7 in that the homeowner can't see the end of the pipe and therefore not even know if the TPR valve has opened. Is that correct as you see it?
-
04-24-2018, 10:24 AM #4
Re: TPR valve pipe termination
Also is the homeowner violating #2 by not having an air gap in the same room; and possibly #5 in not allowing for possibility of freezing?
-
04-24-2018, 08:27 PM #5
Re: TPR valve pipe termination
#2 and #7, in my opinion. Remember we are not code inspectors so be carefull quoting code to your cients or stating something is in violation of code in your report. It can get you in trouble, should you be mistaken.
We do not have the authority to state that any component in the home is in violation of code, only municipal code inspectors are allowed to say something is in violation of code. (Please correct me if I am wrong here)
You may however, use code as back up in order to prove that what you say is correct, if you are challenged by someone who says that you are wrong, or its not a problem, or tells the client that you are just being picky.
I am a brand spanking new inspector so take it with a grain of salt. This is how I understand it to be.
Ok let the beatings begin!! Am I wrong about this?
-
05-04-2018, 04:17 AM #6
Re: TPR valve pipe termination
That code language also says, "such drains may terminate at other approved locations"
So, approved by who? The local AHJ? Perhaps they approved that installation.
Bookmarks