Thread: Electrical panel location
-
09-04-2018, 12:32 PM #1
Electrical panel location
Does this mean the electrical panel is supposed to be located inside ? Please don't call me a dummy.
Similar Threads:
-
09-04-2018, 01:00 PM #2
-
09-04-2018, 02:16 PM #3
Re: Electrical panel location
That panel is not for use outside. It does not have a 3R rating. It also looks too high.
All answers based on unamended National Electrical codes.
-
09-04-2018, 02:47 PM #4
Re: Electrical panel location
Is the label on the cover, on on the panel enclosure itself? I see the photo showing a label on the inside of the cover door, but is that the label in the photo?
If on the cover, maybe the panel enclosure itself may ... may ... may be suitable for use outdoors with the appropriate cover.
Of course, if that label is on the cover ... the panel may be some other brand and that label may not even be applicable to what is behind the cover. Maybe there is another label on the enclosure behind the cover?
Just raising some possibilities.
You got that switch and receptacle, presumably.
-
09-05-2018, 03:15 AM #5
Re: Electrical panel location
The label pictured is on the inside (on the panel door)
-
09-05-2018, 07:22 AM #6
Re: Electrical panel location
Sam,
I suspect you already figured out that the label tells enough of the story to make a recommendation.
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
09-05-2018, 02:57 PM #7
-
09-05-2018, 06:17 PM #8
Re: Electrical panel location
6'7" to the center of the grip of the operating handle.
Occam's eraser: The philosophical principle that even the simplest solution is bound to have something wrong with it.
-
07-28-2019, 12:07 PM #9
Re: Electrical panel location
So this panel is too high??
Last edited by Bob Ozbirn; 07-28-2019 at 12:16 PM.