    Default Double tap at main lug

    This should not be allowed correct ? Is it because of proper contact and or lug size ?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2

    Default Re: Double tap at main lug

    And dis-similar metals.


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Double tap at main lug

    Not allowed, correct.

    Those terminals are rated for one conductor - one only.

    Those terminals are also not rated for copper AND aluminum ... they would be rated for copper OR aluminum.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Dec 2008
    Location
    Erwin, TN
    Posts
    330

    Default Re: Double tap at main lug

    Quote Originally Posted by Jerry Peck View Post
    Not allowed, correct.

    Those terminals are rated for one conductor - one only.

    Those terminals are also not rated for copper AND aluminum ... they would be rated for copper OR aluminum.
    Nice info